We are getting only cold water and if we are lucky, after 5-10min we would get warm water for a little while. I have cleaned the system with vinegar. I am about to replace the check valve. Please help me understand the following:

1. Per the front panel, at times, the temperature of the water going out is colder than the water coming in. Most of the time, the in/out temperatures are about the same. Is that normal?
2. The cold water intake, the pipe into the WH is feels warm and may be a bit hot at times. Would this be a check valve issue?
3. Is the 2-way valve the same part as the check valve?
4. The hot water out is connected to the condensation pipe, is that normal? There is no pipe going into the recirculation inlet as that was is capped.

Thank-you!
 

anh

New Member
Messages
2
Reaction score
0
Points
1
Location
San Diego, CA
Here is what they piping looks like. Thanks again.
20241119_103819.png
 

Attachments

  • 20241119_103827.png
    20241119_103827.png
    573.9 KB · Views: 36

GReynolds929

Active Member
Messages
608
Reaction score
211
Points
43
Location
WA
The 2-way valve is not the check valve. An easy way to isolate the check valve as the issue is to set the 2-way valve to external. If the temperature issue goes away you have a bad check valve. As an aside, you need to remove the condensation drain from your T&P drain line. Condensate from combustion will eat metal if not neutralized and you will have a leak.
 

Bannerman

Well-Known Member
Messages
5,175
Reaction score
925
Points
113
Location
Ontario, Canada
Below, is the flow diagram for the NPE-240A Internal Circulation setting.

If the internal Check-Valve remains stuck open, which is a fairly common issue with that tankless model, some or all incoming cold water flow will bypass the heat exchangers and instead, flow directly to the hot water outlet connection through the 2-way valve. As water flow will bypass the flow and temperature sensors, the water exiting from the unit could potentially be colder than the temperature sensor is reporting.

npe-recirc-flow-internal.jpg

Further to GReynolds comment regarding the combined condensate and pressure relief valve drain lines, they require separate piping runs. Currently, if the pressure relief valve should release, the water being released under pressure will flow back-up into the gas burner's condensate drain pan and possibly also into the exhaust vent piping.
 