Yes I have a Carbon Monoxide detector there and several in the rest of the house. The company who installed it are coming Tuesday.
But to be honest I don't think the problem is the venting. But when they get here I really want them to call Navien and see what they say?
I really hope I didn't make a bad choice going with this Combo boiler? It looks good! But will it stand up to use and will I have major headaches when it breaks down?
Low mass combi boilers are usually WAY sub-optimal for the average house. They're a good fit for houses with much higher than average space heating loads combined with modest to average water heating needs. (Say 2 people living in an uninsulated 5000' house.)
If you think you may end up replacing it there are two bits of napkin-math analysis worth running on your system and heating history:
First, get a good handle on the design heat load
by using wintertime fuel use against heating degree-day data. You'll find that at high fire even the smallest wall hung combi boilers are usually 2x-5x more burner than is needed for heating the place.
Then,
analyze the amount of heat emitter you have on each zone for how much heat it can deliver at and average water temp of 120F, which is what it takes to actually get the mid-90s efficiency out of these things. If the radiation can't emit the full minimum-modulated output of the boiler it will be forced into cycling on/off rather than modulating the firing rate with heat load, which puts a lot of wear & tear on the boiler, and cuts into as-used efficiency.
The minimum fire output of the NCB 210E and 240E is about 17,000 BTU/hr, which would take 75-85 feet of
typical fin tube baseboard per zone to run at 95% efficiency most of the time. If the heat load of the whole house is only 25,000 BTU/hr @ +15F (NYC & L.I. type
99% outside design temps) it's not really going to modulate much even if there is enough radiation to keep it from short-cycling.
As long as it's not short cycling at condensing temperatures it's not an efficiency disaster or particularly "...bad choice...", but for 19 out of 20 houses in NY it's not exactly a
good choice either.
If it turns out yours is short cycling there are several programming parameter tweaks to minimize that and get more useful lifespan out of the thing. To advise intelligently we'd have to run at least the napkin math analyses on the system. If the radiation is high volume cast iron radiators there is a lot of forgiveness built-in, and even if under-radiated short cycling can usually be suppressed. For fin-tube baseboard & cabinet convectors it's more iffy.