Diagnosing problems with NPE 240A recirculation

Users who are viewing this thread

seatan

New Member
Messages
2
Reaction score
0
Points
1
Location
seattle
Hi - first of all thanks for everybody that contributes to these forums, I've learned so much here from the experts willing to help.

My situation:
NPE-240A-NG installed when the home was built (2019)
Dedicated recirculation return line, uses the water heater's internal recirculation pump

For the last few months, we'd been having an issue where filling the bath start hot but eventually spewed cold water. Used this forum to diagnose a possible problem with our recirc check valve. Removing it did in fact show that the o-ring had become dislodged and valve was stuck open. So I ordered a new one and installed that a few days ago.

Since then I've noticed that it takes a long time to get hot water from any faucet, (90 seconds or more to get hot, used to be just a few seconds) and I'm now wondering if our internal recirculation pump might be bad. The pump does turn on when the unit starts up, and does turn on every half hour for a few minutes, but I'm worried its not actually moving water.

I called Navien and they (reluctantly, it seems like they REALLY hate talking to homeowners) gave me some information about some relevant diagnostic readings (hit the wrench button and then +/- to cycle through readings).

A: Flow rate for the whole unit (gpm)
B: Water temperature leaving unit (fahrenheit)
G: Flow rate for the heat exchanger (gpm)
R: Water temp leaving the heat exchanger (fahrenheit)

So when I can hear the recirc pump turn on every half hour or so, I would expect the G reading to be non-zero (since it's sending water through the hot water lines), but it stays at 0.0. When I just turn a hot faucet on however, I see a non-zero G reading (~1 gpm).

I'm also a bit worried that the new check valve might be the problem, since (a) this started happening just after installing it, and (b) if it was failing to allow water through it seems like that would be hard to differentiate from a failing pump.

It looks like these pumps are reasonably easy to replace, but I'm curious to know if there are other things I should check or tests I could perform to prevent unnecessary work/costs. Thanks!
 

Breplum

Licensed plumbing contractor
Messages
2,303
Reaction score
984
Points
113
Location
San Francisco Bay Area
Pull the check valve and see if it is stuck open (the little plunger rod would be stuck out the bottom and not springing back)
a zero reading when pump has power can be a non op pump OR a bad flow sensor, but bad flow sensor won't show flow even if you trip the T&P.
 

Lifespeed

Member
Messages
410
Reaction score
6
Points
18
Location
California
Sure am glad I didn't get the recirc model, Navien appears to have cheaped out on some important internal parts. My external recirc is on 12 years without failure. Cheap to replace or not, the PITA factor of tearing into the water heater is so not worth it.
 

John Gayewski

In the Trades
Messages
4,769
Reaction score
1,531
Points
113
Location
Iowa
Are you sure the recirc line itself has been fully bled out? It can take a surprisingly large amount of water to fully burp the air from the line and if there's a bubble in the pipe it won't circulate.

Hopefully your system is setup to give a good bleed with a garden hose attached and ran to a drain. If it is you should open it fully and see if it started spitting air.
 

Lifespeed

Member
Messages
410
Reaction score
6
Points
18
Location
California
Isn't the recirc line subject to water pressure on the inlet side, and as such not require bleeding? I'll defer to the experts, but my external recirc has been drained several times when plumbing service was required elsewhere in the house. It spits some air out the hot water side of the faucet then functions normally.
 

John Gayewski

In the Trades
Messages
4,769
Reaction score
1,531
Points
113
Location
Iowa
Isn't the recirc line subject to water pressure on the inlet side, and as such not require bleeding? I'll defer to the experts, but my external recirc has been drained several times when plumbing service was required elsewhere in the house. It spits some air out the hot water side of the faucet then functions normally.
No. Water takes the path of least resistance. It's easier for water to travel from the supply to the outlet. There's no reason for it to go around a loop first.
 

Lifespeed

Member
Messages
410
Reaction score
6
Points
18
Location
California
Hmmm, maybe Navien doesn't use a self-priming pump and this is specific to Navien? Specifics matter, if you say they need bleeding I believe you. With the O-ring failures and bleeding requirement, it would appear they could have done better.

Taco pump doesn't need bleeding. No doubt it's 50X the Bill of Materials (BOM) cost of a Navien pump.
 

Attachments

  • pump.jpg
    pump.jpg
    37.3 KB · Views: 103
Last edited:

John Gayewski

In the Trades
Messages
4,769
Reaction score
1,531
Points
113
Location
Iowa
Hmmm, maybe Navien doesn't use a self-priming pump and this is specific to Navien? Specifics matter, if you say they need bleeding I believe you. With the O-ring failures and bleeding requirement, it would appear they could have done better.

Taco pump doesn't need bleeding. No doubt it's 50X the Bill of Materials (BOM) cost of a Navien pump.
All pumps (centrifugal) need water to pump. If there's no water in the line it can't pump. Some system configurations are more apt to need more bleeding than others. But in general and most of the time if a system is drained the recirc line needs refilled with water. Most configurations of piping need valves to facilitate bleeding air.

Not sure why we're talking about a silly thing such as this. It's pretty basic and common. Your not knowing about it doesn't make it special. Navien, taco, grundfos, and any other pump needs water to pump. Some have different ways to bleed air and there are many many different methods with different mechanisms to bleed air from systems but it's basic and required.
 

Lifespeed

Member
Messages
410
Reaction score
6
Points
18
Location
California
It's also pretty basic to place the pump near the high point in the system so it self-bleeds. Problem solved. Can't happen in every case, but is completely practical for many.
 

GReynolds929

Active Member
Messages
569
Reaction score
195
Points
43
Location
WA
High, low, upside down; it doesn't matter if there's nowhere for the air to escape. Pumps don't bleed air out of the system. That's why there are specific devices designed to remove air, or as was stated a drain valve to flush the air out. Glad you are happy with your water heater setup, but unless you have a small buffer tank it's not better than the "A" model with everything you have built in, maybe more if no external buffer tank.
 

Lifespeed

Member
Messages
410
Reaction score
6
Points
18
Location
California
Open the hot faucet, air is lighter than water. Water flow blows it out. There's your bleeder. You've never seen this?

Needing a bleeder means the plumbing was done in a way that traps air. It's usually avoidable, but not always.
 
Last edited:

John Gayewski

In the Trades
Messages
4,769
Reaction score
1,531
Points
113
Location
Iowa
Open the hot faucet, air is lighter than water. Water flow blows it out. There's your bleeder. You've never seen this?

Needing a bleeder means the plumbing was done in a way that traps air. It's usually avoidable, but not always.
The water doesn't move reverse through the system. Your not fully grasping the concept here. Water has to replace the air. It can't move backward through the check valve which leaves a large void where water cannot travel.

The more you comment the more it's obvious you're not grasping here. Sometimes a system can bleed itself but most will not. Most times the water will not push the air out from the return side because it is rushing through the faucet. It's common and basic.
 

Fitter30

Well-Known Member
Messages
4,974
Reaction score
973
Points
113
Location
Peace valley missouri
There is a internal two position valve that has to open when pump runs and has to set for internal. Lower left side. Look at the gpm flow if recir not running.
 

John Gayewski

In the Trades
Messages
4,769
Reaction score
1,531
Points
113
Location
Iowa
There is a internal two position valve that has to open when pump runs and has to set for internal. Lower left side. Look at the gpm flow if recir not running.
He has a dedicated recirc line. The valve needs to be set on external.

The internal setting of that valve is for homes with no recirc line and it only flows through the heater. It for preventing stacking in the heater and getting hot water quicker as the coil and small tank are "always" hot.
 

Lifespeed

Member
Messages
410
Reaction score
6
Points
18
Location
California
The check valve
The water doesn't move reverse through the system. Your not fully grasping the concept here. Water has to replace the air. It can't move backward through the check valve which leaves a large void where water cannot travel.

The more you comment the more it's obvious you're not grasping here. Sometimes a system can bleed itself but most will not. Most times the water will not push the air out from the return side because it is rushing through the faucet. It's common and basic.
"Grasping", are you serious? Bleeding air is the most basic of concepts. Closed hydraulic systems need bleeding, for obvious reasons. An open system (faucet) in many cases does not need to be bled, only needs it if there is a way to trap air in an elevated location where it can't be removed. Which is an indication of a non-ideal installation.

Don't know what Navien did with their check valves, but in my system the check valve is at the cold inlet to the water heater. The recirc pump outlet connects between the check valve and the heater cold inlet. No check valve in series with the pump at all. Why doesn't cold water back flush the recirc line and flow out the faucet? Because, as you said, water takes the path of least resistance through the heater and out the faucet, not backwards through the pump impeller. Self-bleeds every time and works perfectly.

When the pump is at the high point of the system air moves upward through it thanks to gravity. The recirc line refills from water pressure, which, even with an open faucet, is greater than zero.

I have no doubt someone could plumb a house in a way that traps air and needs manual bleeding. But it is trivial to build a recirc setup that self-bleeds.
 

John Gayewski

In the Trades
Messages
4,769
Reaction score
1,531
Points
113
Location
Iowa
The check valve

"Grasping", are you serious? Bleeding air is the most basic of concepts. Closed hydraulic systems need bleeding, for obvious reasons. An open system (faucet) in many cases does not need to be bled, only needs it if there is a way to trap air in an elevated location where it can't be removed. Which is an indication of a non-ideal installation.

Don't know what Navien did with their check valves, but in my system the check valve is at the cold inlet to the water heater. The recirc pump outlet connects between the check valve and the heater cold inlet. No check valve in series with the pump at all. Why doesn't cold water back flush the recirc line and flow out the faucet? Because, as you said, water takes the path of least resistance through the heater and out the faucet, not backwards through the pump impeller. Self-bleeds every time and works perfectly.

When the pump is at the high point of the system air moves upward through it thanks to gravity. The recirc line refills from water pressure, which, even with an open faucet, is greater than zero.

I have no doubt someone could plumb a house in a way that traps air and needs manual bleeding. But it is trivial to build a recirc setup that self-bleeds.
No. Just no. I don't know why your continuing with this. I'm hoping your not a plumber and praying you start looking at some schematics. Your just saying ridiculousness.

If your describing an injection type of recirculation they need two check valves. Your pump probably has one internally as they are most times equipped with them.
 
Last edited:

John Gayewski

In the Trades
Messages
4,769
Reaction score
1,531
Points
113
Location
Iowa
Here's one I installed a while ago (not quite done at the time of the photo). If there were an integral check valve the engineer might have only drawn one check valve. But it definitely needs two. The cold will definitely pass into the recirculation return line and you'll get cold water only. It will go straight through the pump like nothing.
Screenshot_20240508-221538_Gallery.jpg
 

harrydoyle

New Member
Messages
6
Reaction score
1
Points
3
Location
Oklahoma city
Pull the check valve and see if it is stuck open (the little plunger rod would be stuck out the bottom and not springing back)
a zero reading when pump has power can be a non op pump OR a bad flow sensor, but bad flow sensor won't show flow even if you trip the T&P.
Breplum have you found the check valves available now an improvement or just as failure prone pics are from 2017 240a
 

Attachments

  • 20241118_104241.jpg
    20241118_104241.jpg
    63.8 KB · Views: 15
  • 20241118_102849.jpg
    20241118_102849.jpg
    102.2 KB · Views: 12

Breplum

Licensed plumbing contractor
Messages
2,303
Reaction score
984
Points
113
Location
San Francisco Bay Area
The newest check valves are no better. Same o-ring issues persist. They'd need to improve the composition of the o-ring.
 