I've got one of the HRVs that has a safety warning where the blower motor bearings fail and the unit catches on fire. The following explains it.
The manufacturer's band-aid fix was to provide the following inline fuse so that it will blow when the motor fails rather than come good for a terrible motor design.
We the end users are on the hook to replace the motor every few years or take it apart frequently and oil the motor bushings. The unit has fragile components so every time I take it apart to oil the motor I end up breaking some other part. It's to the point I dread having to take it apart yet again. This thing is a real POS and time to replace it.
I asked the original installer to propose a replacement that hopefully has the same or similar layout of the ports. I have two ports on the left side go to the outside and the two ports on the right side go to the living space.
What was offered has some ports on opposite sides.
I also was hoping to be able to reuse the control wiring in the walls but have my doubts that will be possible. I have a four conductor cable going from the HRV to the nearest bathroom where I use two of the conductors connected to a mechanical crank timer. The four conductors then go to the next three rooms where there are also crank timers. The timers are all wired in parallel to the same two conductors.
Fitter30
Peace valley missouri
Have u contacted venmar? Sleeve bearings are in most cases not designed to carry axial thrust loads.
LLigetfa
NW Ontario, Canada
To what end? They contacted me and supplied me with that inline fuse.
I contacted Venmar on March 15th and they confirmed that they sent me the inline fuse and considered the case closed. I requested the case be escalated and they reluctantly took my phone number and said level 2 support would call me back. I am still waiting for the call.
LLigetfa
NW Ontario, Canada
I decided on a VanEE AI Series Model V160H75RS
I could not get a local dealer to sell me one so I ordered it online. It arrived yesterday and I will start the installation tomorrow. The unit does not have the ports on the same side as my old HRV so I will need to route an insulated flex duct 180 degrees. I will probably tape the inside bend with aluminum foil tape to keep the pleats from restricting airflow.
Fitter30
Insulated flex duct without the liner will slide over sheet metal duct pipe. Put liner over pipe and pull insulation over pipe throw liner away.
LLigetfa
NW Ontario, Canada
The building air exhausted to outside could be at or near the dew point and so galvanized metal ducting is not something I really want to use. I realize you only mention sheet metal which could also be aluminum but finding 6 inch aluminum elbows is not easy. Getting a 100% seal on the elbows and joints is also a challenge and if there is any condensation formed, it could soak the insulation. Ideally, I would want the inner liner to fit over the elbows to maintain the moisture barrier but don't think I can do that.
LLigetfa
NW Ontario, Canada
I finished the install of the new HRV but have yet to install the Advanced Touchscreen Control. For now I have the existing crank timers wired in.
LLigetfa
NW Ontario, Canada
I am curious if there is anyone here that is familiar with this VIRTUO AI Series? Purportedly, it senses the pressure on the four duct ports and adjusts the balance automatically to compensate for changing conditions. Below is an excerpt from their brochure.
Thanks to Virtuo Air TechnologyTM, no need to balance the unit manually. Both PMSM motors are controlled by an artificial intelligence
performing 120 readings per minute then processing this information to maintain the requested airflow.
For typical installation, Virtuo will ensure a balanced ventilation at every selected speed regardless of the weather conditions, the type of
connection, the variable speed furnace/AHU, the stack effect, the filter clogging and so on. This results in peace of mind for installers and
users knowing that the unit will always remain balanced and that it will maintain its maximum heat/energy recovery efficiency.
With that in mind, when I first powered up the unit prior to connecting the ductwork, I fully expected the initial test result to show the top rated 160 CFM but it was topping out at 140 CFM. After connecting all four ducts, it topped out at 120 CFM.
LLigetfa
NW Ontario, Canada
It turned into a much bigger job than I had anticipated. I decided to mount the control next to the thermostat for the furnace which is in a central hallway. The kitchen, breakfast, dining, and living room are all open concept except for a short partition wall so that upper cabinets would have a place to hang. I had forgotten that since the wall is load bearing, it had blocking installed. I had to take down a kitchen cabinet (upper) so that I could cut a large enough access in the drywall from where I could drill through the blocking. I then dropped a small chain down through the hole in the blocking and shoved a magnet up through the hole in the base plate and subfloor from the crawlspace since fish-tape was not going to hit the hole.
I had been meaning to take down the upper cabinet anyway to repair it since it was pulling apart from the weight of the china in it.
LLigetfa
NW Ontario, Canada
The explanation that Venmar support gave me was that the unit senses barometric pressure which may have been affected due to "stack effect". My home is fairly well sealed but at the time of installation, the wife likely had an upstairs window open as I felt a strong inrush on the fresh air supply duct, so that lends credence to Venmar's claim. I was going on the assumption that the unit would only sense differential pressure across the four ports.
LLigetfa
NW Ontario, Canada
I have had two instances where the touchscreen control lost communication with the HRV. Fortunately, I have a conveniently located wall switch that controls the outlet the HRV is plugged into so I can power-cycle it to recover from the communication error without having to go down into the crawlspace. I suspect that short intermittent power bumps are the root cause for the communication error.
The crank timers still work when the touchscreen loses communication and they are the only control the wife uses so I don't need to educate her on how to recover from the communication error. When rebooting the HRV, it goes through a POST (power on self test) during which time, the touchscreen is inoperative.
LLigetfa
NW Ontario, Canada
I've had the control throw that E50 communication error many times since installing. At first I thought it might be due to power bumps brought on by storms but the errors persisted through late Fall and Winter. Recently I touched base with the dealer who purported to have a fix for it which involved replacing the touchscreen control and installing a filtration harness (part #1110442). The filtration harness looks to be a MOV connected between the chassis and signal GND. The replacement control has an older revision than what it is replacing.
After replacing the control and installing the harness, I quickly got several E50 errors. I put back the old control and thought I was on the right path, but then it too threw E50 errors albeit less frequently so I had to take the filtration harness off. I am back to square one now.
Not sure if I should keep working with the dealer or with Venmar. For now I'll wait to see what the dealer has so say.
Fitter30
Barometric pressure is air density not building pressure. Building pressure takes outside and inside pressure to see if the envelope is pressurised or in a negative. What is the complete model and serial number of the Venmar?
Fitter30
Wall control model sv66144-09 or the number 41303? From reading the manuals on the control the smart feature read outside temp and indoor rh for speed control nothing was stated about building or barometric pressure. The cable between touch screen and unit is that what came with the control or supplied by you?
LLigetfa
NW Ontario, Canada
Six days passed from when I put it back to the way it was to when I got my first E50 error yesterday. My dealer said he would open a ticket with Venmar and said I should hold on to the the parts for now.