I may not be in correct forum so please advise if not
We have in floor radiant heating. Ours is a closed system with gas water heater recirculating the water in the lines. Pex pipes
Problem is that some areas of the floor seem to be cool this year there are two pumps and both seem to be working correctly so wondering what the problem could be
We did replace both pumps recently as well..
Any ideas of what is going on?
 

Fitter30

Well-Known Member
Messages
5,513
Reaction score
1,112
Points
113
Location
Peace valley missouri
Do u know pipe size and lenghts of loops? Pumps changed like for like? Old pumps bran and model # and new pumps brand and model numbers? Water pressure in system?
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,193
Points
113
Location
New England
It may be that there is an air lock...the water can't flow properly, so it may not be flowing through that loop.

If the pressure is low, with elevation changes, that can impact things, too.
 

John Gayewski

In the Trades
Messages
5,093
Reaction score
1,645
Points
113
Location
Iowa
Sounds like air to me. You need to purge the air from the individual loops that aren't heating. Hopefully it's installed to make this fairly easy.
 