Hybrid Boiler System - Pressure Relief Valve

Users who are viewing this thread

GRC

New Member
Messages
1
Reaction score
0
Points
1
Location
Sioux Falls, SD
Have you ever ran into a scenario where you are adding a boiler to an existing system and the current boiler requires a 30 psi relief valve but the new boiler needs 50 to operate? Is there a way to make this system work or do the valves absolutely have to be the same setting? IE : 30 psi or 50 psi
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
A higher pressure relief valve may be required when you are pumping to a higher elevation so you can maintain pressure at the high point (pressure will drop 0.43#/foot of elevation gain). You need pressure at the high point to prevent the water from potentially boiling or flashing to steam. You'd have to read the specs on the 30# unit...it might support a higher value, but it's only safe when you actually need it, otherwise, if there were a fault, the water temp could get much hotter. A 30# relief valve works for most typical homes, and if not needed, the boiler with the 50# valve could be changed to a 30# one with no loss in function.
 