HRV/FURNACE WIRING

Users who are viewing this thread

Fartsac

New Member
Messages
3
Reaction score
0
Points
1
Location
Martintown, Ontario
Hello,
I would like my furnace fan to activate when I choose MAX on the the wall control board or when I activate the ligh touch push button switch in the bathroom.
My equipment:
Venmar Constructo #43110
Lennox EL296UHE
My set up:
Relay Wiring.png
 

Fitter30

Well-Known Member
Messages
5,521
Reaction score
1,114
Points
113
Location
Peace valley missouri
1&3 coil
4Common
2 no
5nc
Don't know what a wall control is but would need two relay one for each devise light & wall control. PROBLEM
if furnace has a multi speed blower heat runs at a lower speed than ac to make this work without frying the blower motor both heat and ac have to run on the same high speed and might have a cold draft in heat if heat is satisfied and fan is running.
Relay looks correct wire both relays in parallel.If
Correct voltage relay coils.
Why not put the hrv on a timer or indoor air quality control.
 