How to run vent when drain pipe runs under bathtub?

Users who are viewing this thread

Whatnot

Member
Messages
57
Reaction score
0
Points
6
Location
Wisconsin
I am installing a new bathtub and the drain has to run under the tub to the opposite end. I have not been able to find anything on how to run the vent with this configuration. I could run it up either end wall.

I only have 2x8 joists and am hoping to keep everything above the bottom if possible.
 

wwhitney

In the Trades
Messages
6,898
Reaction score
1,952
Points
113
Location
Berkeley, CA
Do you want to run the drain down the joist bay to the opposite end and keep going horizontal with the drain past that wall above?

If so, per the Wisconsin plumbing code, you can use a 1-1/2" trap, run the trap arm at exactly 1/4" per foot, and have the vent connection up to 6' away when you use an upright horizontal combo for the vent takeoff. Or if you need more than 6', you could can use a 2" trap (upsize from 1-1/2" on the inlet side of the trap) and go up to 8'. The 1/4" per foot is critical here, as that is the minimum pitch, but the total fall is limited to one pipe diameter (hence 6' for 1-1/2" and 8' for 2").

If your drain turns downward where the vent comes off, then the Wisconsin plumbing code has lower limits on how long the trap arm can be, see Table Table 382.31−1 "Maximum Developed Length Between Vent and Trap."

Cheers, Wayne
 

Jeff H Young

In the Trades
Messages
9,792
Reaction score
2,473
Points
113
Location
92346
2x2x1 1/2 combi on back 2x1 1/2 bushing on end with 1 1/2" p trap? pretty easy run pipe high in joist bay so trap dosent hang below joist in cieling below
 

Jeff H Young

In the Trades
Messages
9,792
Reaction score
2,473
Points
113
Location
92346
btw you can come up on either end of a 5 ft tub with this method you can have the vent on the dran end or on the far side
 

Whatnot

Member
Messages
57
Reaction score
0
Points
6
Location
Wisconsin
The pipe it needs to tie into is a 2" running perpendicular to the joists. It is below the joists and running along the basement block wall so stepped in a ways from the above exterior wall. If I run the vent straight up, it will come through the floor under the tub. I do have the wall furred out so it might be possible to do but not easy.
 

Whatnot

Member
Messages
57
Reaction score
0
Points
6
Location
Wisconsin
Do you happen to have any diagrams of the combi on back? I am trying to picture that but can't see how there would be space for it.
 

Jeff H Young

In the Trades
Messages
9,792
Reaction score
2,473
Points
113
Location
92346
The pipe it needs to tie into is a 2" running perpendicular to the joists. It is below the joists and running along the basement block wall so stepped in a ways from the above exterior wall. If I run the vent straight up, it will come through the floor under the tub. I do have the wall furred out so it might be possible to do but not easy.
Do you happen to have any diagrams of the combi on back? I am trying to picture that but can't see how there would be space for it.
well a little info helps. maybe notch down into the sill plate with a long sweep on top of that a 2 x 1 1/2x 1 1/2" spigot santee for the tub santee shouldnt be to high



 

John Gayewski

In the Trades
Messages
4,727
Reaction score
1,517
Points
113
Location
Iowa
You need a diagram to illustrate your problem. With the pipe running perpendicular to the joists you should be able to vent between the joists and route a pipe through the back wall of the tub. Without some kind of spatial knowledge about what your dealing with the problem seems very simple to solve, but we'd need to know all of the variables.
 