Gas Line Size

Users who are viewing this thread

Plumber69

In the Trades
Messages
2,380
Reaction score
214
Points
63
Location
Prince Rupert, British Columbia
Looked at a job today, there is a 35' long gas line, 1 inch. This will supply 200,000 btu on demand, two 75,000 btu furnaces, 16,000 btu dryer, 35,000 btu range. Im thinking 1" is too small
 

wwhitney

In the Trades
Messages
6,567
Reaction score
1,847
Points
113
Location
Berkeley, CA
Looked at a job today, there is a 35' long gas line, 1 inch. This will supply 200,000 btu on demand, two 75,000 btu furnaces, 16,000 btu dryer, 35,000 btu range. Im thinking 1" is too small
If it's a 1/4 psi system (7" w.c.) with 0.5" w.c. allowable pressure drop, and 1" iron pipe, then you are right. Per the 2015 IFGC Table 402.4(2), allowable flow on a 35' 1" iron pipe is about 350 kBTUs/hr.

https://up.codes/viewer/washington/ifgc-2015/chapter/4/gas-piping-installations#402

Cheers, Wayne
 

Plumber69

In the Trades
Messages
2,380
Reaction score
214
Points
63
Location
Prince Rupert, British Columbia

wwhitney

In the Trades
Messages
6,567
Reaction score
1,847
Points
113
Location
Berkeley, CA
Think being short 50,000 would be a big deal
I don't really know--but from the tables I infer that the allowable length is 28', so you'd be 25% over length, before any allowance for the additional segments from the end of the 1" pipe to each appliance. Is it feasible to run a separate 1" line from the meter to the tankless water heater?

Cheers, Wayne
 