interalian
Member
We have a 2-storey 2600' house with an unfinished 1500' basement. There are two furnaces: one for top floor (70,000BTU with 3ton AC) for ~1100'. The other for main floor/basement (120,000BTU, no AC), ~3000' combined. All supply lines 5". I'll explain the ducting layout and issues by floor and room - doors usually left closed on top floor.
Top floor:
-Master/ensuite/WIC: Five supply registers and one 8x16" return grille. Two exterior walls. Thermostat for upstairs furance is in this room and this room is always comfortable.
-Bedroom 2: One supply register and one 8x16" return*. Two exterior walls. This room is cold in winter.
-Bedroom 3: One supply register and one 8x16" return. One exterior wall. This room is warm to hot in winter so we keep the register mostly closed.
-Bonus room/nook. Three supply registers and one 8x16" return. Three exterior walls. This room is open to the main hallway and is cool in winter.
-Bathroom: One supply register, no return. This room is warm in winter.
As far as I can tell, three of the returns share a single 12x16" joist cavity and a 3.5x16" wall space duct to run down to the furnace in the basement. Bedroom 2 has its own wall duct to the basement.
Main floor:
-Front hall: One supply register, no return. Three exterior walls (one is garage). This area is cool in winter.
-Front room: One supply register and one 8x16" return. Two exterior walls and a cantilever bump-out. This room is cold in winter.
-Half bath: One supply register, no return. One exterior wall (garage). This room is hot in winter. There's a damper in the supply duct that's in the closed position. We keep the register mostly closed as well.
-Laundry room: No supply register, no return. No exterior walls. We have a standup freezer as well as the laundry pair, so this room is always warm/hot in winter.
-Back hall/walk-through pantry: Two supply registers, no return. One exterior wall. This room is warm in winter. One supply register is blocked off, the other has a damper that's in the closed position. We also keep the register mostly closed.
-Kitchen/dining/living room (open area): **EDIT** Four (yes, only four) registers for the entire space. One 8x16" return (yes one) for the entire space. Living room ceiling is 20' and adjoins two-flight stairs to upstairs. Three exterior walls and cantilever off dining room.
Basement:
-One open area, three registers. One return air grill in ceiling that appears to be connected to BOTH furnaces cold trunk. 2x4 framed and R10 insulated concrete walls, concrete floor.
This area will be finished and have one bedroom and a family area plus a full bath.
Based on the above, what would need to change to help balance the system? I have access to the main floor ducts now, and will be looking at the required supply/return for the finished basement.
I really don't think one return for almost all the space on the main floor is anywhere large enough. It would be easy enough to add another return in the kitchen/dining open area by installing in the kitchen island which divides the space. I could also add a supply duct/register under the kitchen cabinets.
Any/all thoughts welcome. I can provide photos if they'd help. The house is a drafty nightmare.
Top floor:
-Master/ensuite/WIC: Five supply registers and one 8x16" return grille. Two exterior walls. Thermostat for upstairs furance is in this room and this room is always comfortable.
-Bedroom 2: One supply register and one 8x16" return*. Two exterior walls. This room is cold in winter.
-Bedroom 3: One supply register and one 8x16" return. One exterior wall. This room is warm to hot in winter so we keep the register mostly closed.
-Bonus room/nook. Three supply registers and one 8x16" return. Three exterior walls. This room is open to the main hallway and is cool in winter.
-Bathroom: One supply register, no return. This room is warm in winter.
As far as I can tell, three of the returns share a single 12x16" joist cavity and a 3.5x16" wall space duct to run down to the furnace in the basement. Bedroom 2 has its own wall duct to the basement.
Main floor:
-Front hall: One supply register, no return. Three exterior walls (one is garage). This area is cool in winter.
-Front room: One supply register and one 8x16" return. Two exterior walls and a cantilever bump-out. This room is cold in winter.
-Half bath: One supply register, no return. One exterior wall (garage). This room is hot in winter. There's a damper in the supply duct that's in the closed position. We keep the register mostly closed as well.
-Laundry room: No supply register, no return. No exterior walls. We have a standup freezer as well as the laundry pair, so this room is always warm/hot in winter.
-Back hall/walk-through pantry: Two supply registers, no return. One exterior wall. This room is warm in winter. One supply register is blocked off, the other has a damper that's in the closed position. We also keep the register mostly closed.
-Kitchen/dining/living room (open area): **EDIT** Four (yes, only four) registers for the entire space. One 8x16" return (yes one) for the entire space. Living room ceiling is 20' and adjoins two-flight stairs to upstairs. Three exterior walls and cantilever off dining room.
Basement:
-One open area, three registers. One return air grill in ceiling that appears to be connected to BOTH furnaces cold trunk. 2x4 framed and R10 insulated concrete walls, concrete floor.
This area will be finished and have one bedroom and a family area plus a full bath.
Based on the above, what would need to change to help balance the system? I have access to the main floor ducts now, and will be looking at the required supply/return for the finished basement.
I really don't think one return for almost all the space on the main floor is anywhere large enough. It would be easy enough to add another return in the kitchen/dining open area by installing in the kitchen island which divides the space. I could also add a supply duct/register under the kitchen cabinets.
Any/all thoughts welcome. I can provide photos if they'd help. The house is a drafty nightmare.