Code interpretation - Change of direction

Users who are viewing this thread

Stereo

Member
Messages
61
Reaction score
1
Points
6
Location
Colorado
The 2018 IPC Section 708.1.4 states, in part, that when a 2" horizontal drainage pipe has a change of direction greater than 45 degrees, a cleanout is required. If I make a 90-degree turn using two 45's, do I still need a cleanout? The distance between the 45-degree fittings would only be about 6". Each change of direction is 45 degrees but the overall change of direction is 90 degrees. I'm not sure this configuration would reduce resistance any more than a long sweep 90 so I'm worried it won't pass muster.

Due to obstructions, I can't reduce the overall angle that the drain enters the stack. The pipe is running through a crawl space in which I can't meet the requirement of 24" vertical access to a cleanout.

Thanks in advance for your feedback.

Change of direction.jpg
 

Reach4

Well-Known Member
Messages
38,902
Reaction score
4,436
Points
113
Location
IL
Can you put a cleanout in within 40 ft upstream?
708.1.4 Changes of direction.

Where a horizontal drainage pipe, a building drain or a building sewer has a change of horizontal direction greater than 45 degrees (0.79 rad), a cleanout shall be installed at the change of direction. Where more than one change of horizontal direction greater than 45 degrees (0.79 rad) occurs within 40 feet (12 192 mm) of developed length of piping, the cleanout installed for the first change of direction shall serve as the cleanout for all changes in direction within that 40 feet (12 192 mm) of developed length of piping.
 

Stereo

Member
Messages
61
Reaction score
1
Points
6
Location
Colorado
Can you put a cleanout in within 40 ft upstream?
708.1.4 Changes of direction.

Where a horizontal drainage pipe, a building drain or a building sewer has a change of horizontal direction greater than 45 degrees (0.79 rad), a cleanout shall be installed at the change of direction. Where more than one change of horizontal direction greater than 45 degrees (0.79 rad) occurs within 40 feet (12 192 mm) of developed length of piping, the cleanout installed for the first change of direction shall serve as the cleanout for all changes in direction within that 40 feet (12 192 mm) of developed length of piping.
 

Stereo

Member
Messages
61
Reaction score
1
Points
6
Location
Colorado
I came up with a different approach that avoids this situation, but I’m still curious to know the answer for when a cleanout cannot be installed - even within 40’ - due to access limitations.
 

GReynolds929

Active Member
Messages
354
Reaction score
115
Points
43
Location
WA
I came up with a different approach that avoids this situation, but I’m still curious to know the answer for when a cleanout cannot be installed - even within 40’ - due to access limitations.
In your diagram a cleanout is easily added by using a wye instead of an 1/8th bend.
 

Stereo

Member
Messages
61
Reaction score
1
Points
6
Location
Colorado
In your diagram a cleanout is easily added by using a wye instead of an 1/8th bend.
Not enough headroom, per code. I’m still hoping someone will answer me about whether using two 45s takes away the need for a clean out.
 