I'm not very familiar with circuit venting, although I've done a bit of reading and have gone over the IPC code section (914). https://up.codes/viewer/colorado/ipc-2018/chapter/9/vents#914
I have a question about the interplay of 914.2 "The circuit vent connection shall be located between the two most upstream fixture drains" and 914.5 "Fixtures, other than the circuit-vented fixtures, are permitted to discharge to the horizontal branch drain."
I understand 914.5 to mean that the horizontal branch drain with the circuit vented fixtures can have other separately vented fixtures discharging into it, at any place, including upstream of all the circuit vented fixtures. So in that situation, what is the proper interpretation of "two most upstream fixture drains" in 914.2?
It could mean the "two most upstream circuit vented fixture drains," which would be clear. But it doesn't say that. It could mean the "two most upstream fixture drains of any venting type," although that would be weird if there are two or more separately vented fixture drains upstream of the circuit vented drains.
Function wise, it seems like the reason for 914.2, when there are no upstream separately vented fixture drains, is to put the vent connection at the upstream end while ensuring that the horizontal vent just downstream of the vent connection is washed by a fixture. That avoids a horizontal drain vent that could foul.
So from that point of view, "between the two most upstream fixture drains" should mean "downstream of at least one fixture drain (of any venting type), and downstream of at most one circuit vented fixture drain". Is that a reasonable interpretation?
Any thought would be appreciated.
Cheers, Wayne
I'm not very familiar with circuit venting, although I've done a bit of reading and have gone over the IPC code section (914). https://up.codes/viewer/colorado/ipc-2018/chapter/9/vents#914
I have a question about the interplay of 914.2 "The circuit vent connection shall be located between the two most upstream fixture drains" and 914.5 "Fixtures, other than the circuit-vented fixtures, are permitted to discharge to the horizontal branch drain."
I understand 914.5 to mean that the horizontal branch drain with the circuit vented fixtures can have other separately vented fixtures discharging into it, at any place, including upstream of all the circuit vented fixtures. So in that situation, what is the proper interpretation of "two most upstream fixture drains" in 914.2?
It could mean the "two most upstream circuit vented fixture drains," which would be clear. But it doesn't say that. It could mean the "two most upstream fixture drains of any venting type," although that would be weird if there are two or more separately vented fixture drains upstream of the circuit vented drains.
Function wise, it seems like the reason for 914.2, when there are no upstream separately vented fixture drains, is to put the vent connection at the upstream end while ensuring that the horizontal vent just downstream of the vent connection is washed by a fixture. That avoids a horizontal drain vent that could foul.
So from that point of view, "between the two most upstream fixture drains" should mean "downstream of at least one fixture drain (of any venting type), and downstream of at most one circuit vented fixture drain". Is that a reasonable interpretation?
Any thought would be appreciated.
Cheers, Wayne