Can I run 1” pex-b re-circulation loop with 1/2” branches to each fixture if within 10’ of 1”? Or should I run 3/4” branches to each fixture?

Users who are viewing this thread

Messages
40
Reaction score
1
Points
8
Location
Pa
I’m running a 1 inch recirculating loop to 3.5 bathrooms,. Should I run a 1/2” branches off that 1 inch line to each fixture, as they are all within 10 feet of the 1 inch line? Or, should I run 3/4” inch branches to each fixture and step down to 1/2” at the connection?
 
Last edited:

wwhitney

In the Trades
Messages
6,567
Reaction score
1,847
Points
113
Location
Berkeley, CA
The former will waste less water and time. Maybe if you have an uber large tub it would be worth 3/4" just for the tub filler.

Cheers, Wayne
 
Messages
40
Reaction score
1
Points
8
Location
Pa
The former will waste less water and time. Maybe if you have an uber large tub it would be worth 3/4" just for the tub filler.

Cheers, Wayne
Would there be any noticeable difference in pressure with the direct 1/2” option?
 

John Gayewski

In the Trades
Messages
4,364
Reaction score
1,349
Points
113
Location
Iowa
The pressure loss in 10' of 1/2" pipe vs 3/4" pipe isnt going to be much. If you already have low pressure and your valve causes a lot of pressure drop it could be noticeable, but in most circumstances you won't notice it.
 