Boiler btuh output ratings.

Discussion in 'Boiler Forum' started by toebone51, Aug 6, 2011.

  1. toebone51

    toebone51 New Member

    Joined:
    Apr 3, 2011
    Occupation:
    Boiler operator and plumber.
    Location:
    LA
    I have 2 heating water boilers rated at 7,300,000 btuh. The relief valve on each unit is rated at 6,235,000 btuh @125 psi. I had an inspection yesterday from my insurance company and he red flagged them. They told me I had to have a relief valve that was equal to or above the boiler rating. The state inspector approved the boilers upon commissioning in 2009. I had an inspection from the same insurance company in 2010 with a different inspector and they were approved. I thought you sized the relief valve to go off at 80% of the boilers maximum capacity. I know the psi factor. Not the btu factor. Is there a different formula for btu? Thanks for your response.
     