I need to finish my second floor and I'm not quite sure the best way to go about doing the insulation.

I will need to add attic baffles to let the air move under my roof. The ceiling in the room will be at letter C. Do I run the baffles from A to C or B to C so that whole cold zone has room to breathe.
 

Attachments

  • Screenshot_20180831-153526_Drive.jpg
    Screenshot_20180831-153526_Drive.jpg
    61.7 KB · Views: 892

Dana

In the trades
Messages
7,889
Reaction score
509
Points
113
Location
01609
You don't have sufficient rafter depth to come anywhere near a code-min R49 for roof insulation even without giving up the code mandated 1" minimum vent channel in the cathedralized ceiling for a soffit-to-ridge venting scheme. Are those 2x8s?

Are there pre-existing soffit & ridge vents, or is this attic currently gable vented?

The 2x4 kneewalls are nearly impossible to air seal adequately, and would need to be at least R13 cavity + R5 continuous insulation on the exterior side to meet IRC code min for DOE climate zone 4 & 5 parts of upstate NY (in yellow or green), R13 + R10c.i. for zone 6 portions of upstate NY (in blue).

new_york.png


How you deal with the roof-R issue most cost-effectively depends on your climate zone. Which color county are you in?
 

BIGBREW

Member
Messages
67
Reaction score
3
Points
8
Location
Upstate New York
I am in blue

Was planning on building all the rafters out to make room for R38 and run a ridge vent under that.
 

Dana

In the trades
Messages
7,889
Reaction score
509
Points
113
Location
01609
Ridge venting without soffit venting of equal or larger free area doesn't do much. Does it already have soffit vents?

IRC code minimum is R49, not R38.

To hit R38 with the code-mandated 1" vent gap for a vented roof would take a total depth of 11.25" even using high density fiberglass, which is 4" of headroom gone from your room (and a lot of work). To hit R38 with low-density batts takes 12.5" of depth, stealing 6.5" of headroom on the sloped ceilings.

HFO-blown closed cell polyurethane foams run about R7/inch. With a 2x8 rafter you have 7.25" of space, which is enough to hit ~R49 unvented without adding any depth to the rafter bays. It's moisture safe for the roof deck, but it's expensive (about $1.25-$1.50 per square foot per inch of depth in my area- that's $9-10 per square foot for R49.) If you stopped at 5.5" it would hit your sub-code R38 goal, but it would still be pretty expensive.

In zone 6 to go unvented you need at least half the total R to be air-impermeable insulation. With just 3" of HFO blown foam ($4-5 per square foot) you'd be at about R20-R21, and would have 4.25" left over in a 2x8 rafter bay for fiber insulation, which is enough to hit your goal in a moisture safe manner:

A high density "cathedral ceiling" fiberglass batt designed for 2x6 would perform at about R18 when compressed to 4.25" and you'd hit your R38 goal without extending the rafters.

An R23 rock wool batt designed for 2x6 cavities would perform at about R19 when compressed to 4.25", for modestly better thermal performance (but far better fire resistance, and low/no risk of airborne fiber particles reaching your indoor air.)

With either rock wool or HD fiberglass and 3" of HFO-blown closed cell foam you'd still have more than half the total R exterior to the foam/fiber interface, so no interior side vapor retarder (other than standard latex ceiling paint) would be necessary to avoid moisture accumulation in the fiber over the winter.

owens-corning-compressed-fiberglass-insulation-r-value-chart.png


It's easier to get the necessary air tightness if you move ALL of the insulation up to the roof deck when going with a cathedralized ceiling in an attic room, whether vented or unvented. This adds quite a bit to the expense. To do it with insulation on the floor of your mini side-attics behind the kneewalls requires making meticulous air dams in each floor joist where it crosses under the kneewall, on each end. Otherwise the ventilation air in one mini-attic can and will cross under the floor to the other mini-attic whenever the wind blows, taking heat out of the room's floor when it does. Simply stuffing it full of low-density cellulose isn't good enough as an air barrier.

The kneewalls themselves would also need 1.5"- 2" of fire-rated foil faced polyiso on the attic side of the kneewall to meet current IRC code minimum performance. It would need at least R7.5 just for moisture control in the kneewall assembly, but that would be R2.5 shy of the thermal performance called out in the code.

When it's all said and done, given the large PITA factor for sealing up the mini-attics behind the kneewalls it's better and often cheaper to do it all at the roof assembly.

It's your call as to whether extending the rafters to do a vented assembly with fiberglass R38 is really worth it. If you went with an unvented foam/fiber hybrid in 2x8 rafter bays, when it comes time to re-roof adding 1.5" of reclaimed roofing polyiso (or a 2" polyiso nailbase panel) above the structural roof deck would meet or beat current IRC minimum performance.

A primer on the topic of insulating at the roof assembly lives here, hitting most of the main points and options. Note that in the blog piece they point out the IRC prescriptive minimum of R25 for the foam in a hybrid approach in climate zone 6. That's true- it's written in the code that way, but the presumption behind that prescriptive is a total of R49, the code minimum. The key determinant of condensation risk is the ratio. R25/R49= 51%. For an R38 assembly you'd only have to meet or beat 0.51 x R38= R19 for the foam layer to have the same ratio.

With 3" of HFO blown foam you're there, but not with 3" of cheaper (but more environmentally damaging) HFC blown closed cell foam, so you'd have to go to 4", (at about the same cost as 3" of HFO blown) and it would have to be installed in two 2" lift with a cooling off period between them, whereas HFO blown foam can be installed at 3-4" in a single pass without quality problems or fire risk during curing.
 

Dana

In the trades
Messages
7,889
Reaction score
509
Points
113
Location
01609
Good information thank you. Yes there are soffit vents already.

If going vented with rafter extensions, rather than adding full dimension full depth lumber to add the extra depth, use 2x2s or 2x3s and 1/2" OSB side gussets every couple of feet as the make a rail at the right depth truss-style, and cut 1.5" deep foam board to fill in between the 2x2 rail and the rafter edge. A high density R38C fiberglass is 10.25" deep, so make the gussets 11.50" deep and 6" wide to guarantee the 1" vent gap + chute depth.

With a 2x3 rail (2.5" deep) and a 2x8 rafter (7.25") that means the 1.5" thick cut foam layer would be 1.75" wide. Cutting 1.5" foil faced polyiso into strips is dead-easy using a 4-5" steel wallboard taping knife sharpened on it's edges, as seen in this short video. Pre-build the trusses/extensions screwing or nailing the gussetts to the rail, and using small blobs of foam board construction adhesive to the gussets, then taping the foam board to the rail on the side opposite the gussets. That way the whole extender assembly can get side-nailed to the rafters with ease.

The foam board being the same nominal thickness as the rail & rafter ensures a reasonable width-fit for batts. When installing the batts, use a batt knife to make shallow 3/4-1" deep slits in the side of the batts where the edges of the gussets are so that the batt will compress at the side there without forming a gap in the insulation.

With full dimension 11.5" deep solid wood the R-value of the rafter would be about R13.8 or a bit less (depends on the species). Reducing the solid-wood to 9.75" (rail + rafter) the wood's R-value is about R11.7, but the 1.75" of polyiso is good for at least R10.5, for a total of R22.2. R22.2 is still far more conductive than the R38 fluff between the rafters, but still a ~35% reduction in heat transfer through R14 rafters.

If using 2x2 rails and 2.75" of foam the rafters will be about R27, which is even better. For long runs the flatness of the ceiling would be a bit off with 2x2s, but in your case it the cathedralized ceiling portion of the finitshed room looks like it would be reasonably short.

It's a PITA to do it this way, though not as bad as you might think at first. The assembly still won't be at a code-min R49, but it'll be measurably better than R38 between solid rafters, and closer to code-min on a U-factor basis. (With R38 rafters and an inch of vent it would just barely make it to code-min thermal performance using U-factor calculations.)
 