I have this now:

p.jpeg


I'd like to add a utility sink on the right side, like this:

p.png


Is that proper/legal or does the sink's p-trap need to be tied into the vent separately as well? I'm guessing no.

Update - I found this. Would it be ok?

index.php
 
Last edited:

Terry

The Plumbing Wizard
Staff member
Messages
29,942
Reaction score
3,461
Points
113
Location
Bothell, Washington
Website
terrylove.com
Each trap will need it's own venting. Especially for a washer and laundry tray.

washer_rough_b.jpg


804.1 All plumbing fixtures or other receptors
receiving the discharge of indirect waste pipes shall be
approved for the use proposed and shall be of such
shape and capacity as to prevent splashing or flooding
and shall be located where they are readily accessible
for inspection and cleaning. No standpipe receptor for
any clothes washer shall extend more than thirty (30)
inches (762 mm), nor less than eighteen (18) inches
(457 mm) above its trap. No trap for any clothes
washer standpipe receptor shall be installed below the
floor, but shall be roughed in not less than six (6)
inches (152 mm) and not more than eighteen (18)
inches (457 mm) above the floor.
 
Last edited:

Reach4

Well-Known Member
Messages
38,964
Reaction score
4,463
Points
113
Location
IL
Thanks for the reply. Does this count as dedicated venting for each?
You can put a cleanout above the santee, rather than low like you have it now. That frees up space for the laundry drain.
 