Is there a better way to vent this

Users who are viewing this thread

JohnDill

New Member
Messages
14
Reaction score
5
Points
3
Location
Colorado
addition plan.jpg
 

wwhitney

In the Trades
Messages
6,579
Reaction score
1,852
Points
113
Location
Berkeley, CA
Yes. If the lower left fixture is a shower, then you can eliminate all the VTRs except for the lav. As long as your trap arms are all horizontal and basically in the same (2% sloped) plane, and within the length limits (no more than one internal pipe diameter fall from the trap to the first wye, but 1/4" per foot slope), then your lav wet vents tub, the shower, and the WC.

Cheers, Wayne
 

JohnDill

New Member
Messages
14
Reaction score
5
Points
3
Location
Colorado
Yes. If the lower left fixture is a shower, then you can eliminate all the VTRs except for the lav. As long as your trap arms are all horizontal and basically in the same (2% sloped) plane, and within the length limits (no more than one internal pipe diameter fall from the trap to the first wye, but 1/4" per foot slope), then your lav wet vents tub, the shower, and the WC.

Cheers, Wayne
Thanks Yes the first fixture is the shower. That will be easier then a dry vent on each one.
 