Thermostat set a temp push hold that will take it out of time schedule. Just to the right of the expansion tank 16" there are two pipes going into the boiler, top of pipes are tees to the right is return piping left of the tees are supply.
Thoses pipes should be very hot 130*- 107* with boiler running
 

Thekid1

Member
Messages
76
Reaction score
2
Points
8
Location
Long Island, NY
Thermostat set a temp push hold that will take it out of time schedule. Just to the right of the expansion tank 16" there are two pipes going into the boiler, top of pipes are tees to the right is return piping left of the tees are supply.
Thoses pipes should be very hot 130*- 107* with boiler running

Ok I'll check. I dont have thermometers at those pipes, or are you asking me to feel them? Doesnt the screen that I showed on the boiler show those supply and return temps? I'm not sure exactly what your asking, I'm sorry.
 

Fitter30

Well-Known Member
Messages
4,388
Reaction score
805
Points
113
Location
Peace valley missouri
Boiler temp isn't system temp. The 136*- 123* pic heat is going out to the system. Other pics where temp difference is 1*-3*heat isn't going out to the system either the taco pump has stopped because its going bad or its not getting power. See your outside temp is 50* outdoor reset if default settings weren't changed 130* boiler water temp. You can touch the piping just be smart about it.
 

Thekid1

Member
Messages
76
Reaction score
2
Points
8
Location
Long Island, NY
Boiler temp isn't system temp. The 136*- 123* pic heat is going out to the system. Other pics where temp difference is 1*-3*heat isn't going out to the system either the taco pump has stopped because its going bad or its not getting power. See your outside temp is 50* outdoor reset if default settings weren't changed 130* boiler water temp. You can touch the piping just be smart about it.

Ok, what exactly are you asking me to do so I can be more help to diagnose this problem?
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
If the house got warmer, the pump had to be running. Now, it may not be running properly, or there's an air lock somewhere. It takes more heat to raise the house temperature than to maintain it, so 130-degree water may not be enough. The chart I linked earlier shows quite a bit of difference in heat per foot of fin-tube based on the temperature. Ideally, it runs as low as possible and the boiler runs longer so there are fewer cycles, putting out just enough heat to overcome that lost to the outside. That produces the most even, comfortable heat, but low water temp prevents the radiators from generating a lot of heat needed to raise the temperature.
 

Fitter30

Well-Known Member
Messages
4,388
Reaction score
805
Points
113
Location
Peace valley missouri
The manual link posted previous page 3rd from the bottom tell how to get into the program and u can raise the minimum temp up and write down the rest of the setting. System piping hot left of the tees from boiler? Have down loaded the thermostat link looked at cycle rate?
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
WIth a properly dialed in outside reset, keeping temperature shouldn't be an issue, and the boiler temp will rise or fall to compensate. But, assuming I understand how it works (not 100%), it won't turn the supply temperature up to speed up from what amounts to a setback, and with it being 50-degrees outside, it would likely be on a really low fire mode.
 

DIYorBust

Active Member
Messages
753
Reaction score
94
Points
28
Location
Long Island, New York
WIth a properly dialed in outside reset, keeping temperature shouldn't be an issue, and the boiler temp will rise or fall to compensate. But, assuming I understand how it works (not 100%), it won't turn the supply temperature up to speed up from what amounts to a setback, and with it being 50-degrees outside, it would likely be on a really low fire mode.
I think some boilers do have an automatic boost where they will up the water temp if the t-stat calls for heat for some amount of time.
 