I agree completely with this, except i would wet vent both the toilet and tub through the lav by using a 3x2 double y, you can bush down the tub side and run 1 1/2 inch pipe.

that works fine but, now your toilet is not vented properly.

connect the lav/tub line to the toilet arm and you got it.

you can eliminate the relief vent before the lav if you want. its not required.

If you want to tie in the tub, seperately to the blue pipe, then you vent it seperately. which is more work then its worth, just tie the lav and tub to the toilet arm and your done.


Thanks to Krows drawing ( page 1) - your input now makes perfect sense - i will update the image ( on page 1 ) and let you all see it to check it out - im in canada so if anyone from canada could set me straight on the vent size that would be cool.

thanks again Novice piper
 

Krow

Plumber
Messages
903
Reaction score
3
Points
16
Location
Ontario, Canada
- im in canada so if anyone from canada could set me straight on the vent size that would be cool.
I'm in Ontario Canada. 1 1/2" venting for your layout is fine across Canada


BTW, in Canada, you cannot use a double wye on a horizontal run/drain (Just thought I would mention it)
 

NovicePiper

Not a Master Plumber
Messages
97
Reaction score
0
Points
0
Location
CAN Toronto GTA
I am by no means any kind of artist as you are, but here is a simple layout that may help. Check your local codes for sizing of your vents. In my area we can vent an entire bathroom with 1 1/2" pipe

The Drawing below shows the wash basin drain and the tub drain wet venting the toilet

Is this ok?

Thanks for the sketch Krow muchos appreciated - is the 3" to the 3rd floor tied in to the 4" stack correctly/position below the kitchen sink? & in turn is the kitchen sink tied in correctly to the 4" stack?

Thanks Krow :)

novicepiper
 

Attachments

  • basement_r_4.jpg
    basement_r_4.jpg
    93.7 KB · Views: 806
Last edited:

Bombjay

New Member
Messages
62
Reaction score
1
Points
0
Run your toilet back to the wall then vent it kind of like this...Hope you can see this.The toilet vent can be 2" If your waste is 4" that is fine.You had no sizing on your waste and vents.1 1/2 for your tub and lav (Uhhh sink.)waste, 1 1/4 for your tub and sink vents until they connect with the toilet vent.Could you post a pic. of the room and maybe the space below?



scaled.php
 
Last edited:

NovicePiper

Not a Master Plumber
Messages
97
Reaction score
0
Points
0
Location
CAN Toronto GTA
Run your toilet back to the wall then vent it kind of like this...Hope you can see this.The toilet vent can be 2" If your waste is 4" that is fine.You had no sizing on your waste and vents.1 1/2 for your tub and lav (Uhhh sink.)waste, 1 1/4 for your tub and sink vents until they connect with the toilet vent.Could you post a pic. of the room and maybe the space below?



scaled.php

could you send a larger pic if poss - i cant read your dims. I thought i had listed every pipe dim in the room via the left top coloured dots (4", 3" 2", 1.5"). I thought the layout was complete! as is re last image posting ------ please bare in mind, this is all done at the computer at the mo. the only pipe in that room at the mo is the main blue stack running vertical and then offset underground exactly as on image:)

Thanks for your input - really appreciated Bombjay.

PS The image is to scale in everyway I will update the image and include all measurements


ROOM DIMENSIONS = 118" (9' 8") X 63" (5' 2") and 18" depth below ground level.
 
Last edited:

Mikey

Aspiring Old Fart, EE, computer & networking geek
Messages
3,024
Reaction score
17
Points
38
Location
Hansville, Washington
What software do you use for those gorgeous drawings? If it could transform back and forth from 3D to the standard plumbing drawing format (like Krow did -- it's got a name but I forget what it is), that would be great.

Are you a novice piper as in plumbing, or as in piping?

http://www.youtube.com/watch?v=C-D6iI_3LHE

(This gets good about 1:20 into the clip. Who ever would have thought of harmonizing guitar and bagpipe?).

Mikey

Also a novice piper... (that's not me in the clip)
 

NovicePiper

Not a Master Plumber
Messages
97
Reaction score
0
Points
0
Location
CAN Toronto GTA
What software do you use for those gorgeous drawings? If it could transform back and forth from 3D to the standard plumbing drawing format (like Krow did -- it's got a name but I forget what it is), that would be great.

Are you a novice piper as in plumbing, or as in piping?

http://www.youtube.com/watch?v=C-D6iI_3LHE

(This gets good about 1:20 into the clip. Who ever would have thought of harmonizing guitar and bagpipe?).

Mikey

Also a novice piper... (that's not me in the clip)

Thanks for the vid - im neither a bag pipe player or plumber i just can sweat pipes and glue abs pipes together... that certainly does not qualify me for either as i dont know the theory behind venting, is it supposed to suck air in or act as a release for frontal air force and push air out of the way of on coming waste - i thought it was both - but I am probably sort of incorrect maybe.

i do like the bag pipes and the guitar though - so thats acdc then - thats a first for me:eek:

software 3d max - no idea what the software your talking about re schematics & 3d in one - if you find out let me know please:)

thanks novicepiper
 
Last edited:

Mikey

Aspiring Old Fart, EE, computer & networking geek
Messages
3,024
Reaction score
17
Points
38
Location
Hansville, Washington
The main reason for venting (combined with fixture traps) is to prevent the infiltration of sewer gas (it's as bad as it sounds) into the living space.

Imagine a fixture like a sink with a straight pipe going into a sewer. With no water in the drain pipe, the gases generated in the sewer have a clear path into the house. This would be bad :(. If you've ever used an outhouse or port-a-potty on a hot day, you have only a slight inkling of how bad it can be -- like fatal :eek:.

So, the sink (and all other fixtures as well) have those "trap" thingies in their drains to keep (trap) a small puddle of water in them, sealing the pipe from the sewer. Toilets have a trap built in to the bowl -- a large part of the water used in the flush goes to refill the trap with nice clean water after all the poop has been washed downstream.

However, if an upstream neighbor or fixture let go a large discharge, that frontal air pressure you mentioned might push the trapped water aside and burble sewer gas up into the sink. Bad :(. Or, when you drain the sink, or when any large slug of water going goes down the drain downstream from the sink, a low-pressure situation could be created and siphon the trap, draining enough water to destroy the seal. Bad :(.

The vent system allows all the traps to remain in a pressure-neutral state, and not be siphoned, maintaining the seal. Good (big-grin smiley intended here, but prohibited by the system, which I just found out is limited to 4 images per message).
 
Last edited:

NovicePiper

Not a Master Plumber
Messages
97
Reaction score
0
Points
0
Location
CAN Toronto GTA
The main reason for venting (combined with fixture traps) is to prevent the infiltration of sewer gas (it's as bad as it sounds) into the living space.

Imagine a fixture like a sink with a straight pipe going into a sewer. With no water in the drain pipe, the gases generated in the sewer have a clear path into the house. This would be bad :(. If you've ever used an outhouse or port-a-potty on a hot day, you have only a slight inkling of how bad it can be -- like fatal :eek:.

So, the sink (and all other fixtures as well) have those "trap" thingies in their drains to keep (trap) a small puddle of water in them, sealing the pipe from the sewer. Toilets have a trap built in to the bowl -- a large part of the water used in the flush goes to refill the trap with nice clean water after all the poop has been washed downstream.

However, if an upstream neighbor or fixture let go a large discharge, that frontal air pressure you mentioned might push the trapped water aside and burble sewer gas up into the sink. Bad :(. Or, when you drain the sink, or when any large slug of water going goes down the drain downstream from the sink, a low-pressure situation could be created and siphon the trap, draining enough water to destroy the seal. Bad :(.

The vent system allows all the traps to remain in a pressure-neutral state, and not be siphoned, maintaining the seal. Good (big-grin smiley intended here, but prohibited by the system, which I just found out is limited to 4 images per message).

Thanks Mikey that was a good explanation - i knew about the p trap water keeping poopie smells out etc - just not sure about the venting issue - but now i do have a clearer understanding... do you happen to know the meaning of life...and starbucks, whats that all about!
 
Last edited:

NovicePiper

Not a Master Plumber
Messages
97
Reaction score
0
Points
0
Location
CAN Toronto GTA
venting - mikey

So as i understand: and please correct me if im wrong

1) large discharge of water from above could create positive pressure and push air through a p trap below - resulting in bubbles and poopy smells?

2) large discharge of water from below could create negative pressure (vacuum) and suck air from a p trap above - resulting in siphoning and poopy smells?

please see my little diagram-

Q1) whats stops A and B from having positive and negative pressure on the kitchen sink?

Q2) Will C affect any of the above floors?



thanks novicepiper
 

Attachments

  • diargam.jpg
    diargam.jpg
    86.5 KB · Views: 1,034

Krow

Plumber
Messages
903
Reaction score
3
Points
16
Location
Ontario, Canada
If you do this, you will be in the good books with any Canadian inspector and or Canadian juresdiction. Your sizing of venting and dranage is ok. We generally do not use any 1 1/4" pipe and fittings any more because they are double and triple the money than the 1 1/2". (just a cost factor)

You are allowed to use 1 1/2" for your bathtub drain. 2" is optional. The waste and overflow assembly kit for the bathtub will be 1 1/2" anyway
 

Attachments

  • basement_r_4.jpg
    basement_r_4.jpg
    20.1 KB · Views: 804
Last edited:

NovicePiper

Not a Master Plumber
Messages
97
Reaction score
0
Points
0
Location
CAN Toronto GTA
If you do this, you will be in the good books with any Canadian inspector and or Canadian juresdiction. Your sizing of venting and dranage is ok. We generally do not use any 1 1/4" pipe and fittings any more because they are double and triple the money than the 1 1/2". (just a cost factor)

You are allowed to use 1 1/2" for your bathtub drain. 2" is optional. The waste and overflow assembly kit for the bathtub will be 1 1/2" anyway

Cool - thanks Krow - the red pipe in the revision you posted... can that go up straight up, or does it have to be exactly as in your drawing?

- ill start preping everything now and leave that one section until i hear back from you - thanks again

novicepiper
 

Redwood

Master Plumber
Messages
7,335
Reaction score
13
Points
0
Location
Connecticut
The sketch Krow made is in line with what I was suggesting. I would however, break out some more slab and run the lav drain more direct with fewer elbows and shorter horizontal runs. Both have effects on reliability. 2" is a minimum Dia. under the slab.

As with anything there are a few different ways of doing it. Below is a sketch of what I was saying. I did not show connection details you seem to have a handle on that. Please excuse my rudimentary drawing... What did your program cost? Where is it available?

novicepiper.jpg
 
Last edited:

Krow

Plumber
Messages
903
Reaction score
3
Points
16
Location
Ontario, Canada
can that go up straight up, or does it have to be exactly as in your drawing?
If you can go straight, then do it. It will save you on fittings. The best path from location A to location B, is in a straight line.

Redwood suggested a couple of alternative routes to take, which are just as good. There are many ways to skin a cat lol
 

Krow

Plumber
Messages
903
Reaction score
3
Points
16
Location
Ontario, Canada
If you want to stick with the pic I provided, maybe these slight amendments might suit you better
 

Attachments

  • basement_r_4.jpg
    basement_r_4.jpg
    20.5 KB · Views: 671

NovicePiper

Not a Master Plumber
Messages
97
Reaction score
0
Points
0
Location
CAN Toronto GTA
The sketch Krow made is in line with what I was suggesting. I would however, break out some more slab and run the lav drain more direct with fewer elbows and shorter horizontal runs. Both have effects on reliability. 2" is a minimum Dia. under the slab.

As with anything there are a few different ways of doing it. Below is a sketch of what I was saying. I did not show connection details you seem to have a handle on that. Please excuse my rudimentary drawing... What did your program cost? Where is it available?

novicepiper.jpg


Thanks for all your input Redwood - I believe I referenced you to krow in one of Krows postings you have both been v helpful/useful and patient with my lack of knowledge - so thanks again :D

------------------------------------------------------------------------
SOFTWARE TITLE: 3ds max
COMPANY: Autodesk
Price: 3K+ tax depends on what version you buy.

You can download a free trial but if you've not done any 3d before, it prob going to be more work than results - that said i picked it up ok so im sure anyone else can too:)

Im up for doing visuals if you need any (which i doubt) but the offers there - just let me know.

I don't have the software but I could do you some visuals if you needed!?

thanks

novicepiper
 
Last edited:

NovicePiper

Not a Master Plumber
Messages
97
Reaction score
0
Points
0
Location
CAN Toronto GTA
thanks

At this juncture, I believe the last image to be complete and final - thanks mainly to Redwood, Krow, Mikey & Jimbo + everyone else too.

If anyone has any questions let me know - once again, a big thanks to you all.

novicepiper
 

Redwood

Master Plumber
Messages
7,335
Reaction score
13
Points
0
Location
Connecticut
$3K Gulp!:eek:

I guess I'll keep the rough ones I'm using...

That last sketch should do well for you!
It certainly looks a lot simplier than the one you started with huh?:cool:
 

Mikey

Aspiring Old Fart, EE, computer & networking geek
Messages
3,024
Reaction score
17
Points
38
Location
Hansville, Washington
So as i understand: and please correct me if im wrong

1) large discharge of water from above could create positive pressure and push air through a p trap below - resulting in bubbles and poopy smells?

2) large discharge of water from below could create negative pressure (vacuum) and suck air from a p trap above - resulting in siphoning and poopy smells?

please see my little diagram-

Q1) whats stops A and B from having positive and negative pressure on the kitchen sink?

Q2) Will C affect any of the above floors?



thanks novicepiper
a1) proper venting of the kitchen sink
a2) yes, if the upper floors aren't vented properly.

Here's a simple test I just made up, which a real pro can correct and my feelings won't be hurt: for any fixture, its trap must be vented, and that vent path to open air cannot be affected by anything that can suck or blow. There are special cases (e.g., stack venting) that aren't obvious.
 
Last edited:
Top
Hey, wait a minute.

This is awkward, but...

It looks like you're using an ad blocker. We get it, but (1) terrylove.com can't live without ads, and (2) ad blockers can cause issues with videos and comments. If you'd like to support the site, please allow ads.

If any particular ad is your REASON for blocking ads, please let us know. We might be able to do something about it. Thanks.
I've Disabled AdBlock    No Thanks