In my area about 300 bucks.
we still need to talk, sorry.
In my area about 300 bucks.
Should I have a well company do the video or can I have a plumbing company do it?
My well guy quoted me $800 for video inspection.
Seems expensive for a 160 ft deep well.
Not to complicate matters, butThe 45 gpm req'ts for the fire sprinkler system will not need to go through the water treatment components but I am sizing my pump to be able to supply that flow if it was ever needed and of course to satisfy the County authorities, etc.
Cary, since the integrity of the casing looked good we're not planning to video again after brushing/bailing.
I had an official fire sprinkler plan created and the max flow calculated was 36.1 gpm at minimum 20 psi. I still believe the Gould 60GS75 will be the best bet, and as valveman said it won't produce more backpressure than the CSV3B2T can handle for my application.
A CSV and the 5 HP 55GS50 pump should cost half what you were quoted for the 10 HP and VFD. And I know it will work much better and last longer.