Gotcha lol. I have tried to research how that would make things work correctly but haven't found much. I'll wait for an expert opinion!LL header theory is above my pay grade here
One of the pros will have to address that...
gotcha. I found a local plumber who seems to know his stuff when it comes to mod cons and he seems to like HTP and says his main supply house carries them and the local support is great in NH. I'll update when I have a quote but I'm expecting $1700-1900 for the boiler and another $2,000 in labor and materials. My gas company still has a $1500 rebate which should put this around $2300-2600 out of pocket. At least I hope that's a pretty accurate idea of cost.BTUs in has to equal BTUs out to keep it from cycling. Without significant thermal mass to work with the cycles will be short, thus, the only way a low loss header can address short cycling is if it has a lot of water mass, say a 20+ gallon hydraulic separator, not Navien's pre-built closely spaced tees:
(The tall tank next to the boiler with the vent on top)
vs.
(The fatter pipe with the connections to the boiler, which is Navien's pre-made low loss header.)
The napkin math:
It takes 1 BTU to raise 1 lb of water 1 degree F.
The typical high/low differential on a condensing boiler is between 5F and 10F.
At 110F average water temp typical fin-tube puts out about 200 BTU/hr per foot. A 14 foot zone delivers thes 2800 BTU/hr.
The output of the NCB-240 at that temp is about 95% of the 18,000 BTU/hr minimum input, or about 17,000 BTU/hr.
So the excess heat going in is about 14,000 BTU/hr.
With a low-mass low-loss header, 50 feet of distribution plumbing the 14' of fin tube and the internal volume of the boiler adds up to about 2 gallons of water, x 8.34 lbs/gallon is about 17 lbs.
With 14,000 BTU/hr going into 17lbs of water it's temperature is rising 14,000BTU/hr /17lbs= 824F p/hour, or (/60=) 13.7 F per minute.
So, with a high/low differential of 5F the burn cycles would be about 5/13.7= 0.365 minutes, or about 22 seconds long.
In that 22 seconds the amount of heat buffered in the thermal mass of the system is about 86 BTU. With the fin-tube emitting at 2800BTU/hr, or 46.7 BTU/minute, it cools off the 5F in less than 2 minutes before re-firing, so a complete firing-cooling-refiring cycle takes less than three minutes, and you would get more than 20 burn cycles per hour.
With a differential of even 10F you're looking at burns less than 45 seconds long, and more than 10 cycles per hour. This is short cycling.
You can't cheat the thermal physics with magical plumbing.
But,say, you have massive hydraulic separator with 18 gallons of water, plus the and 2 gallons of distribution plumbing fin-tube, boiler, etc you're looking at 20 gallons or about 167 lbs to work with, and a 5F swing would take about 220 seconds, more than 3 minutes, and a 10 F swing would take more than 7 minutes of burn time. At a 5F differential the buffered BTUs is 5F x 167lbs= 835 BTU, and with the fin tube emitting 2800 BTU/hr the cooling time takes 835/2800= ~0.3 hours or 18 minutes, so even with a 5F swing you're at only a couple of burns per hours, and at 10F swing it will be barely more than one burn per hour.
But an 18 gallon low loss header like a Boiler Buddy BB-18 is a pricey piece of hardware (about a grand, with shipping at internet pricing), which is quite a bit more expensive than another 40' of fin-tube to bring it up to 54'. At an AWT of 120F and 200 BTU/hr per foot, a 54' stick of fin tube emits 11,000 BTU/hr and there is now "only" ~5,000 BTU/hr of excess, not 14,000, and you've picked up another ~7lbs of water, tripling the burn times, shortening the off times, but still bringing it to under 10 burns per hour with a 10F swing.
But with average heat loads a slow as implied by the total amount of baseboard band-aiding an oversized minimum-burn rate with a massive low loss header is still the "wrong" solution. Massive low loss headers really only make sense for micro-zoned houses, and it's still counterproductive to size the boiler to where it cycles rather than modulates with the whole-house load.
I'd be surprised if you can get out of it for under $5K (before rebates are applied), but maybe. If it's replacing cast iron there will be the additional costs of the plastic venting & combustion air supply, and the exhaust condensate management stuff, etc.
The UFT-80W (and most other fire-tube boilers) usually doesn't need hydraulic separation/low-loss headers to function well, so as a drop-in replacement it should be pretty easy to plumb-in, could even be simpler than what the prior boiler needed.
In 19 out of 20 systems there would be no need to pipe the UFT-080W primary/secondary. That is true of most fire-tube boilers, due to the low pumping head and tolerance of high temperature differences on the heat exchanger.
Replacing zone valves with pumps costs over $100 per zone in just hardware, and you's also be into it for the primary pump too, and the extra plumbing, etc., plus the additional labor involved. Maybe that adds up to $3K, maybe it doesn't, but it is not likely to be necessary.
If you stick with zone valves you should probably swap out the circulator with an ECM drive smart pump (a ~$150-200 cost adder on the hardware front) to be able to tweak the flow under various conditions, but there is no reason you can't go that route. Setting it up a smart pump for a constant 20F temperature difference would usually be super-kind to the boiler, but you may want to set it up for constant backpressure instead, depending on the particulars of the system. If it were a different type of heat exchanger the primary/secondary might make sense in some cases, but in most residential systems it's possible to specify a flow & pump that would work fine without primary/secondary anyway.
Spending another $3K to be nicer to a $1700 boiler that is also a design tolerant of a wide range of flows & temperature differences doesn't make much sense to me. If the contractor quoting the $5K seems competent and stands behind the work (get references), go with it. Find out what they intend to use for a pump, and if its a standard 1-speed, discuss the ECM drive smart pump concept. With a dialed-in right-sized mod-con the pump will be running pretty much 24/7, and if you go with a low efficiency sub-optimal 1-speed it will end up using more than 5x the electricity of a smart pump.
December 2015 is a lousy month to use, since it had several days toward the end of the month that had a cooling load instead of heating. (I recall skiing in 70F weather the afternoon of 24 December!) With super-mild weather the error from solar gains and other gas appliances is greater, compared to months with a consistent and deeper heat load.
That said...
I downloaded a daily HDD for the past year rom station KMTH, and truncated it to the period from 12/10/2015 and 1/12/2016. You don't know what time of day the meter was read, but you have to throw out either the first day's or last day's HDD to be valid, since they didn't read the meter at 12:01 AM on December 10th, then 11:59 PM on January 12th.
Adding it up from 12/10 through 1/11 it comes up with 930.2 HDD, and adding up from 12/11 through 1/12 it's 910.2 HDD, so spitting the difference it's likely that the fuel use covered about 920 HDD.
90 therms is 9,000,000 BTU. Burned at 80% efficiency it put at most (0.8 x 9,000,000=)7,200,000 BTU of heat into the heating system.
That's 7,200,000/920= 7826 BTU per HDD, or (/24=) 326 BTU per degree-hour.
A design temp of -3F is 68F cooler than the presumptive 65F heating/cooling balance point base, so the implied load is:
68F x 326 BTU per degree-hour= 22,168 BTU/hour.
As a sanity check, for 1420' of conditioned space that works out to 22,168/1420= 15.6 BTU/hr per square foot of conditioned space. That's a credible number, but a bit on the high side for a tight 2x6 framed house. But if the existing boiler was 130,000 BTU/hr (in or out), the thing is really more than 4x oversized for the design load, and probably delivering 70-75% efficiency (best case.) So the real load is probably closer to 22,168 x 70/80= 19,397 BTU/hr with a load/area ratio of about 13.7 BTU per square foot, which is also a credible number.
If you have 100 feet of baseboard, that's 222 BTU/hr per foot needed when it's -3F outside, which can be delivered at an average water temp somewhere between 120F- 125F. That's definitely in the condensing zone, even at design condition, which means you can probably set it up the reset curve to run with 110F-115F output & 94-95% efficiency most of the season, only dropping to the low-90s during the coldest weather.
The plumber who says you're limited to 87-88% either can't or didn't do even the most rudimentary math on it!
A ~$5K quote for a relatively simple swap-out seems fair, and about what it costs to drop in a 2-3 plate cast-iron beastie that only hits' mid-80s efficiency. The ECM pump will pay for itself in fairly short years on the electricity savings alone, and allows you to optimize the system a bit better.
Pumping the system at ~2 gpm (~1000 lbs /hour) and a delta-T of 20F will deliver 20,000 BTU/hr, which is your approximate heat load. So setting the low end of the curve initially to something like 125F @ 0F and the pump at 2gpm constant flow will probably work just fine. When both zone valves are open both zones will be getting ~1 gpm, which is sufficiently turbulent for good heat transfer, and when only one is open and taking the full flow it's still a reasonable flow. That's neither a stress on the boiler or the plumbing. The delta-T will be smaller when the water temps are lower, since the fin-tube is emitting less, but that's fine.
At 326 BTU per degree-hour the ~7600 BTU/hr min-fire output balances at 7600/326 = 23F cooler than the 65F presumptive balance point, or ~42F. For 100' of fin-tube to balance it would only need to emit 76 BTU/ft to balance which would be fairly low water temp something like an average water temp 100F. At 2 gpm that would be a delta-T of 7.6F, so setting the minimum supply temp to something around 105F would be about right, then play around a bit with the maximum outdoor temperature. If you set the maximum outdoor temp to 40F it would probably keep up when it's 40F or lower, but if it won't fire at all at warmer temps than that you'll be pretty chilly during the shoulder seasons. Odds are pretty good that your true heating/cooling balance point is about 60F, so you might start there, or even lower. There's plenty of room to play around with it, but the goal is very long, near constant burns, at a reasonably low flow. Taking the flow under 1 gpm may have paradoxical results, since it may not be turbulent enough for good heat transfer due to laminar flows insulating the walls of the fin-tube pipe from the warmer flow in the center.
This is awkward, but...