I just wanted to know if this drain would be adequate for proper draining? I added the 90 to go into the stud to the p-trap. New home owner and trying to learn as I go.

upload_2017-3-8_10-30-1.png


Thanks so much for your help.
 
Last edited:

Terry

The Plumbing Wizard
Staff member
Messages
29,942
Reaction score
3,459
Points
113
Location
Bothell, Washington
Website
terrylove.com
Is that 1.5" pipe? The washer should be run with 2".

I have never run a washer using two 90's above the p-trap. Interesting. I have done it with 45's.
The 90 on the left looks to be a vent 90 instead of a medium 90.
The 90 on the right should have been a long turn 90.
It would have been nice if you had drilled through the stud and located the p-trap in the same stud space, perhaps using the far right hole for the drain, and installing the water to the left.
 