I know that vents need to be 6" above flood level rim before they can be horizontal but what is the flood level rim of a toilet since the P-trap is in the toilet? Sorry if it is a dumb question.
 

Terry

The Plumbing Wizard
Staff member
Messages
29,942
Reaction score
3,461
Points
113
Location
Bothell, Washington
Website
terrylove.com
Flood level is the top of the bowl. However, inspectors look at all the plumbing nearby and often want it six inches above the highest fixture, not the lowest fixture. For that reason, plumbers will run their horizontal vents at 42" which is six inches higher than a 36" counter.

dwv_b2.jpg
 
Last edited:

hj

Master Plumber
Messages
33,608
Reaction score
1,047
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
42", OR 6" aboe the flood/overflow level WHICHEVER IS HIGHER, is the code "standard" in most cases to cover the possibility that a 36" kitchen sink would be connected to the line.
 