Hey guys, I'm attempting my first DIY plumbing project.
I found this site, and have learned quite a bit, thanks so much to everyone who gives their time & advice here.
I'm going to put a utility sink in the garage next to the laundry.
Here's what I got;
pipes.jpg
I've seen the example picture on a few of the threads, I guess I just want a little confirmation, is this all I need to do;
pipes2.jpg
 

Cacher_Chick

Test, Don't Guess!
Messages
5,458
Reaction score
213
Points
63
Location
Land of Cheese
What you have drawn in is fine as long as you install a sanitary tee above the existing one for the drain. If you are going to revent the washer, the vent take-off should be a wye and 45. The drain should be 2" and vent 1-1/2".

You need to make sure that the sink is high enough so that when the trap is installed this will allow proper pitch to the drain.
 
Last edited:

Terry

The Plumbing Wizard
Staff member
Messages
29,942
Reaction score
3,461
Points
113
Location
Bothell, Washington
Website
terrylove.com
washer_rough_b.jpg


Some codes allow the sink to wet vent over the washer, if the piping is 2"
Or you can vent both and it passes anywhere.
If you have the washer over the sink, then for sure they both need venting.
 

Cacher_Chick

Test, Don't Guess!
Messages
5,458
Reaction score
213
Points
63
Location
Land of Cheese
DudeJoe, the problem is that there is more to it than what you think.

Because the washer drains a high volume of water quickly, the tee for the sink should be above the tee for the washer.

Putting the sink tee over the washer makes it necessary to install a re-vent on the washer drain to meet code in many areas.

An additional challenge is that the sink drain and the washer drain need to be 2" Because the existing tee for the washer is only 1-1/2 inch at the top, it that existing tee will need to be replaced with one that is 2" at all 3 ports.

You are going to need to cut out the existing tee and laundry drain and start fresh.

Don't cut off too much or you wont have anything to connect to, and/or the washer trap will be on the floor.

IMG_20130217_205333.jpg
 
Last edited:

TheDudeJoe

New Member
Messages
3
Reaction score
0
Points
0
Location
Las Vegas
Thanks again for all the help everyone.
Here is what I've ended up with before glueing and and going through the studs.
image.jpg
The washer drain is going to be higher, I haven't figured out where I'm putting the outlet box yet, other that that, how am I looking.
 

MTcummins

In the Trades
Messages
389
Reaction score
1
Points
18
Location
Pittsburgh PA
Funny how towns ravaged by natural disaster, with massive amounts of total rehabilitation, and permits/inspections to go with it, tend to lax up a bit on code enforcement. Seems they have better things to do than insist that the letter of code be enforced, such as get millions of people back in their homes.

I'm no code-nazi. You could probably look up many posts on here where that's apparent. But in this case, there was no reason to not do it right, the access wasn't that difficult, the wall is open, etc.

I'll let the real pros like Terry answer for sure, but what you have there looks all right to me. Make sure you get your full standpipe height on that washer drain, but you already mentioned that you know you need to do that.
 

Terry

The Plumbing Wizard
Staff member
Messages
29,942
Reaction score
3,461
Points
113
Location
Bothell, Washington
Website
terrylove.com
What you have there now will work, as long as the standpipe on the washer is taller. Change that and you can go ahead and glue it up.

Max trap arm length before vent
1.5" = 42"
2.0" = 60"

You can pretty much use a medium 90 anywhere except on waste going from vertical to horizontal.
or horizontal to horizontal. Horizontal to horizontal needs a long turn. (edit)
The long sweep on the vent is fine though.
I quit stocking "vent" 90's with my fittings. Medium 90's can be used more places and they cost less.
 
Last edited:

MTcummins

In the Trades
Messages
389
Reaction score
1
Points
18
Location
Pittsburgh PA
Isn't a horizontal to horizontal 90 generally a long sweep situation as well? I could be remembering wrong as far as code, but I'd always do a long sweep or 2 45s in that situation if possible. I know a medium 90 is usually used for a trap arm turning out of the wall (such as in this setup), but I never use a medium 90 on its side anywhere else in the drainage system.

I find that vent els can be handy in a few select situations, but yes, generally unnecessary extra parts.
 

MTcummins

In the Trades
Messages
389
Reaction score
1
Points
18
Location
Pittsburgh PA
Like the cleanout in your setup too, btw. Often skipped, but a nice thing to put in while you're working. Just be sure to leave some way of getting at it through the drywall, so you can find it when you need it :)
 

Cacher_Chick

Test, Don't Guess!
Messages
5,458
Reaction score
213
Points
63
Location
Land of Cheese
Looking good. :cool:

A minor detail but the horizontal section on the re-vent should be at least 6" higher than the top of the standpipe when you glue it up.
 
Top