3.25 x 10 duct installation

Users who are viewing this thread

TJanak

Member
Messages
240
Reaction score
8
Points
18
Location
South TX
I need to install 3.25 x 10" duct for the new downdraft cooktop. Do I screw the joints together, or is there some other way the sections join? I read something online about some kind of clips but that sounds kinda flimsy.

Should I tape or use some sealer/mastic?

This will go up an exterior wall. Should I try and use fiberglass batts between the sheathing and duct? Obviously I'll have 1/4" of space to work with.

What about condensation? This will run under the cabinet for a couple of foot and then up the wall and out the roof. There is no where for condensate to drain. Should I just insulate well and hope for the best?

Anything else a ductwork/HVAC newbie needs to know?

Thanks
 

MTcummins

In the Trades
Messages
389
Reaction score
1
Points
18
Location
Pittsburgh PA
I am certainly no HVAC pro, so take my advice with a grain of salt...

Generally rectangular ducts have a sort of clip together attachment built into them. This should hold fairly well, but if it feels a bit loose, you can add some sheet metal screws (however, it should be noted that you should NEVER use sheet metal screws in a dryer vent, as the screws inside the pipe will catch all kinds of lint and clog up your vent over time). I tape all seams with either duct tape or foil tape.

Can you not vent this to the side wall that you're going up, rather than going all the way up to a roof? Seems easier and more efficient for heating/cooling purposes.

Cramming fiberglass into a 1/4" space will give you basically the same insulation value as just leaving the space empty. Compressing it like that drastically reduces its insulating value - you want it loose and fluffy in the bay. You could use a thin rigid insulation board or a duct wrap or something, but with that little space, you won't get much benefit. You're better off ducting to the side wall if possible so that you avoid this problem. There are restrictions on how/where you can sidewall vent (distance from windows etc) on a water tank or furnace... I'm not sure if these apply to a cooktop vent... hopefully someone else can chime in on that.
 

hj

Master Plumber
Messages
33,599
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
"S" cleats on the long sides, and "drive cleats" on the short ones, the same as if it were for a heating system. It would take a "lot" of pop rivets to make it even somewhat air tight.
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,771
Reaction score
1,191
Points
113
Location
New England
Because the fumes coming off the stove may have grease in it, you don't want the seams to leak. There are some mastics designed to seal flues, but I don't know if they are approved for this application. I know your fan probably has a grease filter, but over the years, some will likely get by and into the duct. This can be a fire hazard, but is more common in commercial kitchens. I'd call the manufacturer of the vent and ask them their thoughts.
 

TJanak

Member
Messages
240
Reaction score
8
Points
18
Location
South TX
Didn't know about the "S" and drive cleats, after looking them up that sounds like a good, secure connection. Looks like I will use foil tape and/or mastic over the joints. Just have to get a good approved mastic.

Thanks
 

Ballvalve

General Engineering Contractor
Messages
3,581
Reaction score
45
Points
48
Location
northfork, california
I bent a million s's and drives in my youth. Now its all about tape and laps. A good aluminum tape really is incredible stuff.

s's and drives give an internal lip like a rivet or much worse a screw, and do not do the corners. So no good solution. Be sure to insulate well to try and keep the grease in suspension.

Built a community center in Alaska. Sub forgot to insulate the duct from the hood though the attic... plans actually didnt show it. Condensation filled the hood and burned the place down a year later.
 
Last edited:

Ballvalve

General Engineering Contractor
Messages
3,581
Reaction score
45
Points
48
Location
northfork, california
That was the story. No details. It wasnt my contract luckily , I was just the gunner, doing the detail mechanicals and keeping the drunken indians working. But the electricals in a big hood can short out and arc and start a fire.

Actually I had installed a phone dialer and detectors, so the place stayed up. Fire burns slower when its -45 outside. Try hanging steel siding at that temperature. Great fun. lived in a motley mobile where the diesel furnace NEVER shut off. Couldnt put a drink on a windowsill, would freeze in a few minutes. Odd to see all the cars in a market lot parked with motors running.
 

Dana

In the trades
Messages
7,889
Reaction score
509
Points
113
Location
01609
Condensation is anything that enters the draft hood in vapor or gas form, and liquifies or solidifies when the wall of the duct is below the temperature at which that material is in gas form. In a whiskey still a lot of that condensate is ethanol, in an oil-fired heating appliance flue it has all SORTs of goodies.

But in range hood vents the flammable culprit is usually fats/oils caking into a thick film of grease on the cold duct walls, then dripping a flammable stream of liquid oil into the range top flames at some point when it's warmer, going off like a flame-thrower. Grease fires are less likely in a downdraft cook top, (it can't drip up against gravity) but it's still better to keep the grease from building up in the duct by insulating it in cold climates.
 

TJanak

Member
Messages
240
Reaction score
8
Points
18
Location
South TX
Dana,

How would I insulate the 1/4" gap between the duct and exterior sheathing in the wall? There is brick outside of sheathing. Also, what would be ideal to use in the attic space?

I have ideas but often times my ideas are unconventional.
 

Dana

In the trades
Messages
7,889
Reaction score
509
Points
113
Location
01609
I'm not sure if there are any code restrictions on what can come in contact with a range hood duct. A flexible low expansion foam designed for windows & door framing (eg. Dow "Great Stuff Window & Door" ) would probably make the nicest air seal for your 1/4" gap in the exterior sheathing. Fiberglass is barely more than an air-filter in that type of application, and most caulks would likely fail (and quickly.)

R8 batts (designed for 2x3 framing) wrapped and taped around the ducts would be enough. Alternatively kraft faced R11 or R13 batts would be fine (but overkill.) If you use unfaced batts you'd have to give it an air-barrier wrap of Tyvek or something for the insulation to perform, on the other hand it's not a very high-performance application- it just has to have sufficient R to let the walls of the duct to come up to temp quickly when the blower is running.
 

DonL

Jack of all trades Master of one
Messages
5,205
Reaction score
72
Points
48
Location
Houston, TX
must have been firewater:p

Sounds like Dana was on the right track.


We have that Firewater here in Texas, Because of Fracking.

I wonder how much a bottle would be worth.

Who knows it may become the fuel of the future...
 

BobL43

DIY Senior Member
Messages
1,802
Reaction score
8
Points
38
Location
Long Island, NY
Sounds like Dana was on the right track.


We have that Firewater here in Texas, Because of Fracking.

I wonder how much a bottle would be worth.

Who knows it may become the fuel of the future...
At what cost to the environment or safety? Take a drink of water, light up your Marlboro, and POOF the majik dragin
 

DonL

Jack of all trades Master of one
Messages
5,205
Reaction score
72
Points
48
Location
Houston, TX
At what cost to the environment or safety? Take a drink of water, light up your Marlboro, and POOF the majik dragin

lol


The Gov allows Fracking®, Marlboro©™ smoking, So its got to be good.

As long as you pay your Sin Taxes and Fees it must be safe for you and your environment.


I like Dragons...
 

Ballvalve

General Engineering Contractor
Messages
3,581
Reaction score
45
Points
48
Location
northfork, california
Shopping at harbor fright? RATED duct tape lasts, under or over RATED aluminum tape. Not the crap from home depression and Asia. Short pop rivets are gems too. Seems like no one uses them much anymore.

those million miles of flex ducts are held together only with duct and aluminum tape. Maybe some mastic for the few honest and careful installers.

tape for real men: http://www.grainger.com/Grainger/NASHUA-Duct-Tape-6A061?Pid=search

http://www.grainger.com/Grainger/SHURTAPE-HVAC-Tape-10A411?Pid=search

And a 300 degree tape:

http://www.grainger.com/Grainger/NA...cm_sp=IO-_-IDP-_-RR_VTV70300505&cm_vc=IDPRRZ1
 
Last edited:

Dlarrivee

New Member
Messages
1,150
Reaction score
0
Points
0
Location
Canada
I use foil tape, and a LEED compliant mastic, 1/4" screws... I've never heard of using rivets on small stuff like this...

I have used a pin welder to insulate larger duct.

I have never used 2 different tapes...
 