Toilet vent question

Users who are viewing this thread

TronPlayer

New Member
Messages
11
Reaction score
2
Points
3
Location
Tennessee, USA
Under the IPC, are these venting options allowed under a slab for toilet venting? I've seen mixed messaging , especially on the sanitary tee option. Thanks
 

Attachments

  • 3Capture.PNG
    3Capture.PNG
    254.9 KB · Views: 108
  • 1Capture.PNG
    1Capture.PNG
    799 KB · Views: 107

wwhitney

In the Trades
Messages
7,259
Reaction score
2,072
Points
113
Location
Berkeley, CA
No, neither is allowed anymore. Dry vents can't be horizontal unless at least 6" above the fixture flood rim.

Cheers, Wayne
 
Top