Second floor too hot in summer
PP_
Nashville, TN
Had a 1850 sq ft two story 3 bed 2.5 bath. Beds all 2 fl in st.louis. One 3.5 ton unit. Installed a 2 ton air hander in attic return in the hall ceiling single grill in two bed and 2 bathrooms and 2 in the master. Didn't need heat upstairs just cooling for 6* difference. First month electric bill dropped $50 in 1988. Run the 3.5 during the day, night the 2 ton. Upstairs was oversized but 40 years ago that was the smallest split. 5.5 ton was great for entertaining 90*+ twenty five people no problem.
Thought I will air seal, as it is one of the important steps. My AC unit is about 8 years old and do not want to add another AC for the second floor right now. Would do it if I am not able to address the issues after adding the return ducts. Please note my difference is temp between lower floor and second is about 15* + on a 90* day.
Dana
In the trades
Air sealing both the attic floor and the ducts are VERY important for controlling both moisture and heat flows in the house. Insulation without air sealing can lead all sorts of moisture problems in the attic.
Before adding any insulation caulk the seams between the sheet rock & top plates of the partition walls, and all electrical & plumbing penetrations with polyurethane caulk (or can foam for any gaps over 1/2" in width). Be sure to seal over any electrical boxes or lighting fixtures too. Recessed lights can a be a huge heat & moisture leak, but taping the seams of a cardboard box that has 3" of clearance from the fixture on all sides and caulking it to the sheet rock allows you to heap over the tops. (Replace any incandescent bulbs with LEDs to keep the heat down inside boxed-in light fixtures.)
The gaps to any flues & chimneys need to be air sealed with non-combustible materials such as sheet metal and fireproof caulk. With cellulose insulation it's important to install a wrap of R15 rock wool around flues & chimneys tied in place with wire.
Leaky ducts and air handlers create pressures that drive air infiltration between the attic and conditioned space whenever the system is running, and will often leak copious air even when off. (That problem can be an order of magnitude worse if there aren't adequate return path sizing, particularly from doored off rooms with supply registers. ) Seal the seams of all ducts and duct boots (even if they don't look leaky untreated seams do leak under pressure when the air handler is running), and caulk the boots to the ceiling gypsum with polyurethane caulk. Sometimes it's easier/better to pull the grille or register and seal the boots from the inside, and use mesh tape + duct mastic to seal the duct boot to the ceiling. Seal the seams of any air handlers in the attic with a UL 181 rated metal duct tape (eg Nashua 324A, found in most box stores.)
With air sealing and R40+ attic insulation that difference will likely shrink. But solar gains from upper floor windows usually suffer from a lousier shading factor, and convection forces even within a hermetically sealed house would make the warmer air rise to the top, so attic insulation won't fix it completely. Short of a second ducted system, a single 3/4 ton ductless mini-split can do a WORLD of good for cooling the upper floors.
I live in an antique 1.5 story bungalow with inadequately insulated 6" raftered half-story ceiling. The oversized ducted central air doesn't run long enough to adequately serve the guest quarters, and with no supply register in the loft it's effectively not served at all. My home office is essentially a wide ~10' x 10' landing at the top of the open stairwell with an open rail overlooking the kitchen, and a door to the guest-quarters. (The guest quarters is comprised of ~300' of head-banger sloped ceiling bedroom + a 75 square foot bathroom in a dormer off the north side of the bedroom.) With the door to the bedroom open to the office an 8000 BTU/hr window shaker is enough to keep the whole upstairs cool, albeit with ~5-7F difference in temp between the loft-office and the bedroom when it's 90F+ outside. Earlier this summer when shopping for a quieter window AC the 8000 BTU/hr U-shaped Midea that lets the top sash slide down between the compressor side outside, and the evaporator coil inside) looked like it was just the ticket, but sold out almost everywhere, and being price gouged by most vendors. I ended up buying the 12000 BTU/hr unit and crossed my fingers that it's modulation levels would make it not ridiculously oversized for such a small space, and it EXCEEDED expectations on modulation range, noise levels, and capacity. It has no problems keeping up, and setting it a few degrees cooler than the main system's thermostat it cools most of the first floor too.
It is essentially a "1-ton mini-split in a can". Nerd that I have it on a monitor tracking it's power draw. When the cooling load is very low and the compressor & blowers are all running at their lowest speeds it's only drawing about 100 watts, and "library quiet". On hot sunny afternoons when the sun hits the west facing windows in the loft it will sometimes crank to 900-1100 watts, still nowhere near tripping the breaker. Best of all (which may be of interest to you), even when the outdoor dew points are north of 70F it keeps the indoor RH <60% @ 75F. On muggy 70F+ dew point but not so hot days with less of a sensible cooling and would otherwise run at too low a modulation level to dehumidify, like most mini-splits it has a "DRY" mode that is sufficient to bring the whole house down to <50% over the course of a few hours. Like many mini-splits, when in DRY mode it ignores the temperature setting, and can over-cool the place if left on overnight, so I only run it in that mode when the RH is heading north of 55%.
For a window-shaker it's pretty good, but it's still not as quiet as a mini-split. And while there is a "HEAT" mode indicated on the hand held remote, it doesn't have a reversing valve and doesn't respond to that mode.
  • Like
Reactions: PP_
Dana
In the trades
Hi Dana,
It has been a while, got busy during the last few years.
I got started with fixing the air leaks at the lower floor ceiling.
Started sealing off with duct mastic where there are connections, plumbing lines,
electric fixtures and so on. The way I did is to get cellulose insulation scooped out,
did vacuum to clean up and apply mastic. Once complete, I put back the cellulose
insulation back in place. Cellulose has been compacted (?) to some extend due to
age/gravity(?).
For electric fans and fixtures, do you recommend metal enclosures, or could I do
a plywood box with a 1-2 inch room on all sides of the fixture? My other question
is when it is wood or plywood, does mastic tape adheres to them well? Or do you
recommend any other sealants when it comes to wood/plywood?
Much if this is an edit of my reply to your PM.
Settling in cellulose is mostly a function of mechanical creepage due to seasonal moisture cycling into and out of the material. In a vented attic in the southeastern US it will settle more than more temperate zones like California, but at some density the settling does stop.
Nashville TN is in IECC climate zone 4. The generic version of IRC 2018 calls out R49 for zone 4, but TN requires only R38 under the revised local version of the IRC based on IRC 2018. But if you can fit it, more is better. R38 takes more than 10" of cellulose, which means only fits between 2x12 or larger joists. With smaller joists such as 2x6 the better approach would be to install a second set of joists perpendicular to the existing joists and fill it up to the top, with or without a storage deck up top.
A pair of 2x6s is 11", and with 1.5lbs per cubic foot cellulose would deliver ~R40-R41. If you have the headroom to go with 2x8s that would be 12.75", or R47 pretty close to the standard IRC 2018 prescriptive for zone 4, but still well shy of the IRC 2021's prescriptive R60 (which you probably don't have headroom for near the eaves.)
^^The evolution of IRC prescriptive R values ^^
Be sure to install a barrier that maintains a minimum of 1" of air between the insulation and roof deck slopes to the eaves.
The biggest moisture transfer issues are due to air leakage. Before adding insulation caulk the seams between the sheet rock & top plates of the partition walls, and all electrical & plumbing penetrations with polyurethane caulk (or can foam for any gaps over 1/2" in width). Be sure to seal over any electrical boxes or lighting fixtures too. Recessed lights can a be a huge heat & moisture leak, but taping the seams of a cardboard box that has (the code required) 3" of clearance from the fixture on all sides and caulking it to the sheet rock allows you to heap cellulose over the top. (Replacing any incandescent bulbs with LEDs to keep the temperatures down inside boxed-in light fixtures, further reducing fire risk as well as heat & moisture degradation.)
Leaky ducts and air handlers drive air infiltration whenever the system is running, and will often leak copious air even when off. Seal the seams of all ducts and duct boots (even if they don't look leaky untreated seams do leak under pressure when the air handler is running), and caulk the boots to the ceiling gypsum with polyurethane caulk. Sometimes it's easier/better to pull the grille or register and seal the boots from the inside, and use mesh tape + duct mastic to seal the duct boot to the ceiling. Seal the seams of any air handlers in the attic with a UL 181 rated metal duct tape (eg Nashua 324A, found in most box stores.)