I am interested in replacing my aging boiler with one of the HTP UFT boilers. Based on two years of heating data run through Dana's formulas I have calculated a load of about 45k. I sanity checked this with a heat loss which came in at around 50k. Adding the ASHRAE 1.4x multiplier it gets me up to around 75k so the UFT-80W seems perfect. That said, at present I have an unfinished basement that I imagine in about 5 years or so will be at least partly finished. With this in mind, would it be prudent to get the UFT-100W instead so I have a little more headroom and will definitely be able to support heating the new space. I would usually not considering upsizing but because the UFT has a 10:1 turn down ration, the difference between the on the low end is just 2k (8k vs 10k). So while I will be taking a efficiency hit in the shoulder season over the next few years, it seems like a better option than having to buy a new boiler in five years if the 80w cannot keep up with the extra load.
Or, does the ASHRAE multiplier provide me with enough headroom that I should stick with the 80W?
I understand that this is not a simple question because of all of the heat load variables involved in the current basement, vs the finished space. To that end, at present the space is not technically heated, but does contain a cast iron boiler and the over sized pipes of an old gravity conversion. These provide quite a bit of heat to the space so I would say that in the winter the basement is currently 10 degrees colder than the thermostat upstairs. In the eventual remodel, these pipes would be replaced, and the new boiler will have much lower jacket loss, but since that is not the case now, and my heat load calculations have included the heat that has been leaking into the basement, the 10 degree difference at the 45k load value is valid, correct?
Anyway, the simple question is, since the UFT boilers have such a large turndown ratio which makes the difference between the 80k and 100k only 2k on the low end, does that make them a more valid candidate to oversize?
Thanks in advance for any comments. This is a wonderfully useful community.
Or, does the ASHRAE multiplier provide me with enough headroom that I should stick with the 80W?
I understand that this is not a simple question because of all of the heat load variables involved in the current basement, vs the finished space. To that end, at present the space is not technically heated, but does contain a cast iron boiler and the over sized pipes of an old gravity conversion. These provide quite a bit of heat to the space so I would say that in the winter the basement is currently 10 degrees colder than the thermostat upstairs. In the eventual remodel, these pipes would be replaced, and the new boiler will have much lower jacket loss, but since that is not the case now, and my heat load calculations have included the heat that has been leaking into the basement, the 10 degree difference at the 45k load value is valid, correct?
Anyway, the simple question is, since the UFT boilers have such a large turndown ratio which makes the difference between the 80k and 100k only 2k on the low end, does that make them a more valid candidate to oversize?