New Basement Floor Drain, No Vent

Discussion in 'Canadian Plumbing Code Questions' started by MiloCraft, Nov 1, 2020.

  1. MiloCraft

    MiloCraft New Member

    Joined:
    Nov 1, 2020
    Location:
    Ontario
    Hi everyone,

    I am installing a new basement floor drain, without a vent. Per the local plumbing code:

    A trap that serves a floor drain or hub drain need not be protected by a vent pipe separately where,
    (a) the size of the trap is not less than 3 in.,
    (b) the length of the fixture drain is not less than 450 mm,
    (c) the fall on the fixture drain does not exceed its size, and
    (d) the trap is connected to a horizontal drainage pipe that terminates at its upstream end in a 3 in. stack.​

    I am able to satisfy (a) - (c), but with the basement being finished I am unable to verify (d). I plan on accessing the main 4" sanitary line 1-2 ft. upstream of the backwater valve. The house was built 5 years ago. Is there any situation in which condition (d) would not be satisfied in my case?

    Thank you
     
  2. wwhitney

    wwhitney Well-Known Member

    Joined:
    Mar 17, 2019
    Location:
    Berkeley, CA
    Best course of action would be to verify condition (d) via either opening up drywall or sending a camera upstream from the backwater valve.

    Cheers, Wayne
     
  3. Sponsor

    Sponsor Paid Advertisement

     
Similar Threads: Basement Floor
Forum Title Date
Canadian Plumbing Code Questions White capped pipe (4.5 inches) in a basement floor, what it is for ? May 1, 2017
Canadian Plumbing Code Questions main floor washer basement washroom venting Sep 7, 2014
Canadian Plumbing Code Questions Vent requirement for basement floor drain (Canada) Mar 3, 2012
Canadian Plumbing Code Questions Would this work as a wet vent for a basement 3 piece May 9, 2020
Canadian Plumbing Code Questions BASEMENT BATHROOM Oct 10, 2019

Share This Page