So this is the only place on the internet that might appreciate this story, and I wanna tell someone. My CH-180 was installed 7 years ago and it's been nothing but trouble. Lots of ignition problems, never been able to heat the apartment properly when it's below freezing out, and now the repairman says it's just undersized. I don't agree, and I finally decided to read the manual myself.
The supply temp won't go over 160 no matter how I set the controller. Also there's no outdoor sensor installed, so OK, I bought one on Ebay and installed it. This doesn't seem to help: it's 20 degrees out and no matter where I set the K-curve the house is not warm.
I looked over the dip switches 50 times. Then I looked one more time at the set of 6 dips that are supposed to be set at the factory and never changed, and I saw it: the model number switches were set to CH-240! I flipped one to make it CH-180. Now the supply temp is still 156, but it's 19 degrees out and 70 in here.
I don't know exactly what happened here, but I think I fixed it.
The supply temp won't go over 160 no matter how I set the controller. Also there's no outdoor sensor installed, so OK, I bought one on Ebay and installed it. This doesn't seem to help: it's 20 degrees out and no matter where I set the K-curve the house is not warm.
I looked over the dip switches 50 times. Then I looked one more time at the set of 6 dips that are supposed to be set at the factory and never changed, and I saw it: the model number switches were set to CH-240! I flipped one to make it CH-180. Now the supply temp is still 156, but it's 19 degrees out and 70 in here.