    What would happen if you never put a primary loop in. System has 2 zones each with a dedicated pump
     
  2. fitter30

    fitter30 Well-Known Member

    Joined:
    Feb 2, 2020
    Occupation:
    Retired service tech
    Location:
    Peace valley missouri
  3. Sponsor

    Sponsor Paid Advertisement

     
  4. automaton

    automaton I just like reading manuals

    Joined:
    Mar 7, 2021
    Location:
    New England
    No hydraulic separation from the internal circulator, so possibly lots of stress on the internal pump and exchanger if the flows don't match (what your zones require and what the boiler can do). Additionally, the two zones may not get the same temperature water.
     
  5. Dana

    Dana In the trades

    Joined:
    Jan 14, 2009
    Location:
    01609
    Low mass water tube boilers only have some much range between the minimum flow needed to avoid flash-boil and the maximum at which the flow will erode and wear the heat exchanger from the inside out. It may be possible to design the system and spec a pump that would meet both the radiation's flow requirements and the boilers under all operating conditions, but it might not be. A hacker design that pumps either too little or too much flow through the boiler would likely void the warranty.
     
Similar Threads: Navien boiler
Forum Title Date
Tankless Water Heater Forum Navien Combi Boiler sizing May 25, 2019
Tankless Water Heater Forum Thoughts On Navien Vs AO Smith Small Tankless Propane Boiler Mar 12, 2014
Tankless Water Heater Forum Navien 180 ASME GAS COMBO Boiler/Hotwater heater Jun 25, 2013
Tankless Water Heater Forum Navien NPE 240A NG, Not getting as hot May 1, 2021
Tankless Water Heater Forum Navien NPE 240A Apr 23, 2021

Share This Page