Lochinvar Indirect tank wiring with Tekmar Zone Controller - New Build

Discussion in 'Boiler Forum' started by JMichigan, Sep 27, 2020.

  1. JMichigan

    JMichigan New Member

    Joined:
    Sep 27, 2020
    Location:
    SW Michigan
    I am a DIY.

    We have a new construction 4 zone radiant in slab heat system and a Lochinvar Squire indirect tank for DHW. I am utilizing 5 Grundfos UP-ZV zone valves with one system pump (Alpha 1). I have a Tekmar 306V Controller. The boiler is a Lochinvar Knight WHB110n with an external Grundfos UPML Pump.

    My question is how would you wire this up? I want to utilize the zone priority feature of the Tekmar but I want to utilize the tank sensor instead of an aquatstat.

    The Knight can utilize the tank sensor data but how do I get a signal back to Tekmar to tell it zone 1 needs to open etc?
     
  2. fitter30

    fitter30 Well-Known Member

    Joined:
    Feb 2, 2020
    Occupation:
    Retired service tech
    Location:
    Peace valley missouri
  3. Sponsor

    Sponsor Paid Advertisement

     
  4. JMichigan

    JMichigan New Member

    Joined:
    Sep 27, 2020
    Location:
    SW Michigan
    I have been studying those manuals but I still not sure how to handle it.

    The zones 2-5 thermostats I have tied into the top of the Tekmar controller and the have the actual zone valves tied into the bottom of the Tekmar controller motor/end switch. I am just not sure how to handle the zone 1 (DHW) as its a tank sensor and not an open/close tstat. The Lochinvar can handle the tank sensor but then how do I signal the Zone 1 tstat terminal on the Tekmar? Do I run a parallel signal wire to both components at once? Would I be farther ahead to scrap the Tekmar and just rely on the Knight boiler for everything?
     
  5. fitter30

    fitter30 Well-Known Member

    Joined:
    Feb 2, 2020
    Occupation:
    Retired service tech
    Location:
    Peace valley missouri
    Look at page 60 dhw type in lockinvar manual. Use a relay to signal tekmar zone1 thermostat contacts from lockinvar dhw pump contacts.
     
Similar Threads: Lochinvar Indirect
Forum Title Date
Boiler Forum Lochinvar "Peformance Loop" direction of flow ? Nov 28, 2021
Boiler Forum Lochinvar Noble Messages Aug 16, 2021
Boiler Forum Lochinvar Boiler is Not Throttling Back Like Usual Dec 8, 2020
Boiler Forum Lochinvar KBN211 lockout outlet ARHL Oct 26, 2020
Boiler Forum Lochinvar Knight MRHL/ ARHL issues Dec 3, 2019

Share This Page