I've decided to run a couple new propane branches to add a dryer and a range to my home.
I would appreciate input on a couple of questions:
1. In the process of evaluating the gas distribution system, I noticed the first stage from the tank is only 1/2" copper tubing, approximately 190 feet in length. As far as I can tell, the capacity of that length of tubing at 10 psi is only 209 MBH. Currently, the total maximum appliance load is 296,000 BTUs (110, 88, and 60 from furnaces and 38 from a water heater). Ought I to install a 15 psi first stage regulator to improve this situation?
2. I noticed the first several feet of pipe beyond the second stage regulator is 1/2" black pipe. I'll be adding at least 99,000 BTUs of appliances to the 296. Should I use a close nipple and a reducer to step up the pipe size to 1-1/4?
I would appreciate input on a couple of questions:
1. In the process of evaluating the gas distribution system, I noticed the first stage from the tank is only 1/2" copper tubing, approximately 190 feet in length. As far as I can tell, the capacity of that length of tubing at 10 psi is only 209 MBH. Currently, the total maximum appliance load is 296,000 BTUs (110, 88, and 60 from furnaces and 38 from a water heater). Ought I to install a 15 psi first stage regulator to improve this situation?
2. I noticed the first several feet of pipe beyond the second stage regulator is 1/2" black pipe. I'll be adding at least 99,000 BTUs of appliances to the 296. Should I use a close nipple and a reducer to step up the pipe size to 1-1/4?