Freeze protection for hydronic pole barn heating

Discussion in 'HVAC Heating & Cooling' started by Conde, Feb 13, 2021.

  1. Conde

    Conde New Member

    Joined:
    May 8, 2016
    Location:
    Minnesota
    My father built a pole barn with in-floor hydronic heating. We are just now getting around to adding the heat source (7kw Electro industries Off-peak boiler).

    He is located in Minneapolis MN so the 99% design temperature is -9.4°F.

    We are looking to use a Cryo-tek 100 anti-freeze mixture.
    upload_2021-2-13_8-25-5.png upload_2021-2-13_8-25-5.png
    upload_2021-2-13_8-25-5.png
    In relation to the design temperature, which protection rating should we be targeting? Both category and temperature?

    Thanks
     
  2. fitter30

    fitter30 Well-Known Member

    Joined:
    Feb 2, 2020
    Occupation:
    Retired service tech
    Location:
    Peace valley missouri
    • Propylene glycol needs to be a minimum of 30% for the inhibitors to protect the system. Go with 100% pump, boiler and piping is above ground. Just for some information jan 31 2019 air temp was -31* f 2" in the ground 22*f
    • https://sroc.cfans.umn.edu/weather?page=114
     