Being in a northern climate with cold winters, I am interested in exploring creative approaches to raising the incomming cold water temperature before the plumbing supplies it to the tankless water heaters.

One idea I have is to run it into a non-insulated tank placed in the boiler room where it is excessively warm all the time. This way water coming in on those coldest winter days will stand in a tank indoors in an above room temperature space for a good while to let it take the chill off before heading into the tankless heater.

Earlier today I was reading about people using thermostatic mixing valves to enable increasing the temperature of their tank water heater while delivering a lower temperature to the faucets by mixing in cold water as needed to regulate the temperature. It was mentioned that the aim would be to prevent bacterial growth by increasing the temperature of the water in the tank. Hmm...

That got me to thinking... Would having the incoming cold water sit indoors in a non insulated tank for a while before flowing onward to tankless heaters lead to a problem of bacterial growth in that cold water storage tank?

We have a large filtration, softener, and clorination injection system on our cold water supply plumbing currently, with the clorination system curiously set to its maximum level. So we would be putting highly clorinated water into the tank, unless for some reason that were undesired.

What methods would one take to combat bacterial growth in a cold water storage tank, or what alternate ideas might anyone have for taking the chill off the incomming cold water before feeding it into a tankless water heater?


Thanks,
Jeff
 

Bannerman

Well-Known Member
Messages
4,847
Reaction score
792
Points
113
Location
Ontario, Canada
Is your water source a private well or municipal. Municipal water will the chlorinated to prevent bacteria growth.

with the clorination system curiously set to its maximum level.
Why was the chlorination system installed? We won't know what 'maximum level' represents. Do you test to determine the amount of chlorine in the water after the chlorinator? Does the chlorinator use a pump and if so, does it use a flow meter to activate the pump only while water is flowing?

You mentioned a filtration system, but listed it first and the chlorinator last. Is that the order of treatment?

Consumption of Chlorine and disinfection byproducts is not exactly healthy, and chlorine will be adsorbed through skin and breathed in while bathing.

Does the filtration system contain carbon and does it utilize a large tank and backwashing valve, similar to a water softener?
 

Dana

In the trades
Messages
7,889
Reaction score
509
Points
113
Location
01609
Being in a northern climate with cold winters, I am interested in exploring creative approaches to raising the incomming cold water temperature before the plumbing supplies it to the tankless water heaters.

One idea I have is to run it into a non-insulated tank placed in the boiler room where it is excessively warm all the time.

That sounds like an oversized boiler in a (possibly un-insulated) basement room problem, or too high a boiler temp problem. Assuming it's in a basement, are the basement walls insulated?

A right sized boiler wouldn't be throwing off excess jacket heat. That's an efficiency problem bigger than the water heating efficiency problem. To get a handle on your actual oversize factor, run this math. Depending on the boiler (and some other factors, such as your zone radiation) there are several ways to improve that short of outright replacement.

Rather than an uninsulated tempering tank ahead of the tankless, if you really wanted to harvest significant heat from the a hot boiler room a heat pump water heater would be a better bet. That knocks the temp in the boiler room down degree or two (more, if it's a small-ish room), lowering the amount of heat lost to the outdoors, putting a fraction of that excess heat into the tank instead.

But a heat pump water heater also helps dehumidify the basement. In the July/August time frame even in da Yoop outdoor dew points are above 60F about 25% of the time or more, well above normal basement temps in that area and WAY above your incoming water temps. An uninsulated tempering tank would need something for dealing with summertime condensation on the outside of the tank, since the incoming water temps are well below the summertime outdoor dew point temp. If your basement ever experiences "musty basement" odors or needs a dehumidifier to keep the mold under control, a heat pump water heater does double-duty, handling some of that dehumidification load. A room dehumidifier turns that latent heat of vaporization of the water condensed out of the air into warmer air in the basement, something you don't really want in summer. A heat pump water heater stores that latent heat inside the insulated tank as hot water.

The smallest 40 gallon Rheem ProTerra runs about a grand at box store pricing, and can probably heat water for less money than your tankless. If you want to use it to pre-heat water into a gas fired tankless , setting it to 120F (to limit legionella risk) then mixing it down to something closer to room temp at the input of the tankless might be needed to keep the tankless from flaming out at low flow, since it can only turn down by so much. Or you could just bypass the tankless altogether, and size the heat pump water heater for the biggest tub you need to fill. A 50 gallon heat pump water heater runs about $1500, and is plenty for most 4-5 person families. If it's running short in the dead of winter it can be run in "hybrid" mode for faster recovery (comparable to a standard electric tank water heater.)
 

Fitter30

Well-Known Member
Messages
4,367
Reaction score
800
Points
113
Location
Peace valley missouri
Any heat that the water would pick up in a tank you paid for it. Remember hot goes to cold. Boiler room in a basement either radiates out or up into the house. Gas or oil boilers and or water heaters that have no outside air for combustion is getting by infiltration.
 

Jeff Phillips

New Member
Messages
6
Reaction score
0
Points
1
Location
Upper Peninsula, Michigan
Is your water source a private well or municipal. Municipal water will the chlorinated to prevent bacteria growth.

The property has a well that used to work just fine but i understand several years back the township ran its municipal water pipes down the road and made it illegal for us to continue using our own pump and well, and forced us to buy their water. There is a 100,000 gallon per month billing minimum they enacted which means we pay around $550 per month to "buy" 100,000 gallons of water that we actually only use around 15,000 gallons, sometimes less sometimes maybe up to 20,000 gallons. So at least 80,000 gallons a month that we pay for is water that never got pumped out of the ground and remains in the water table beneath the land.

80% of $550/month is $440 per month that we are paying as nothing more than a tax on 80,000 gallons of water that is sitting under the ground in the water table and remains never pumped out or used at all. The remaining $110 of what we pay per month reflects our actual usage of water we purchase and consume in a month. But we still have to pay $550 per month anyway.

And no, this township does not clorinate the water in their municipal water system. They do nothing to treat it at all. All they have is a large well and large pump and 1800 feet of pipe to bring it down the street to us where they extort $550 a month out of us by prohibiting us from using the well and pump we own that works just fine and would pump the water out of the ground just as well as theirs does on the other end of 1800 feet of pipe. It is a complete scam and nothing more than a $6,600 per year tax on water that isnt even prepared for use and requires us to pay some other company that has its equpment in our basement to then treat the untreated water from the township system to make it safe to drink, or so they tell me. Even though they won't tell me what was unsafe about it. So aggravating!!!

Nothing but bullies. I see zero reason why we must pay them $550 per month for untreated water when we have our own well and pump but are told the government no longer allows it to be used. I wish someone would save us from these tyrants!
 

Jeff Phillips

New Member
Messages
6
Reaction score
0
Points
1
Location
Upper Peninsula, Michigan
Any heat that the water would pick up in a tank you paid for it. Remember hot goes to cold. Boiler room in a basement either radiates out or up into the house. Gas or oil boilers and or water heaters that have no outside air for combustion is getting by infiltration.

Yes I know, but the tenants upstairs have seperate furnaces on their own utility bills so any heat that escapes from the basement to the upper floors is seen as a loss to us and an unintended windfall blessing to the people who live upstairs.

But we are going to keep the common areas and basement heated with the boiler anyway regardless of its issues. I am interested in minimizing the excessive heat build up it creates in the boiler room but as long as it is warm in there i see little reason to not make effective use of the heat that is in there.
 

Jeff Phillips

New Member
Messages
6
Reaction score
0
Points
1
Location
Upper Peninsula, Michigan
That sounds like an oversized boiler in a (possibly un-insulated) basement room problem, or too high a boiler temp problem. Assuming it's in a basement, are the basement walls insulated?

A right sized boiler wouldn't be throwing off excess jacket heat. That's an efficiency problem bigger than the water heating efficiency problem. To get a handle on your actual oversize factor, run this math. Depending on the boiler (and some other factors, such as your zone radiation) there are several ways to improve that short of outright replacement.

Rather than an uninsulated tempering tank ahead of the tankless, if you really wanted to harvest significant heat from the a hot boiler room a heat pump water heater would be a better bet. That knocks the temp in the boiler room down degree or two (more, if it's a small-ish room), lowering the amount of heat lost to the outdoors, putting a fraction of that excess heat into the tank instead.

But a heat pump water heater also helps dehumidify the basement. In the July/August time frame even in da Yoop outdoor dew points are above 60F about 25% of the time or more, well above normal basement temps in that area and WAY above your incoming water temps. An uninsulated tempering tank would need something for dealing with summertime condensation on the outside of the tank, since the incoming water temps are well below the summertime outdoor dew point temp. If your basement ever experiences "musty basement" odors or needs a dehumidifier to keep the mold under control, a heat pump water heater does double-duty, handling some of that dehumidification load. A room dehumidifier turns that latent heat of vaporization of the water condensed out of the air into warmer air in the basement, something you don't really want in summer. A heat pump water heater stores that latent heat inside the insulated tank as hot water.

The smallest 40 gallon Rheem ProTerra runs about a grand at box store pricing, and can probably heat water for less money than your tankless. If you want to use it to pre-heat water into a gas fired tankless , setting it to 120F (to limit legionella risk) then mixing it down to something closer to room temp at the input of the tankless might be needed to keep the tankless from flaming out at low flow, since it can only turn down by so much. Or you could just bypass the tankless altogether, and size the heat pump water heater for the biggest tub you need to fill. A 50 gallon heat pump water heater runs about $1500, and is plenty for most 4-5 person families. If it's running short in the dead of winter it can be run in "hybrid" mode for faster recovery (comparable to a standard electric tank water heater.)


I thought the same thing about the excessive heat around the boiler room suggesting its oversized, but i also have a 4 places I want to add new zone loops to heat from that boiler so if it is over sized, it won't be once I'm done giving it more work to do.

I am curious, for people who have their own well and pump to get cold water, they pump it into a pressure tank. What prevents bacterial growth like legionella in cold water tanks? Obviously those don't get heated to 120 degrees yet millions of people use a well with a pump and tank for cold water. Hmm.

I am definatley intrigued by the idea of the hybrid heat pump water heater acting also as a dehumidifier. There is one corner of the basement that i do have a dampness and mold issue. We plan to do some serious excavating work outside the basement wall there and make some changes to improve drainage but i do occasionally run a dehumidifier in that area currently as needed. It would make lots of sense to swap out the conventional electric tank water heater for the apartment directly above that corner with one of of those hybrids and install it in the basement right underneath the one they were using. Even if we go tankless for the other 9 units, that one in that corner I think your idea would be perfect for instead.
 

Dana

In the trades
Messages
7,889
Reaction score
509
Points
113
Location
01609
I thought the same thing about the excessive heat around the boiler room suggesting its oversized, but i also have a 4 places I want to add new zone loops to heat from that boiler so if it is over sized, it won't be once I'm done giving it more work to do.

In my area the average oversize factor I see for cast iron boilers is ~3x, some have been north of 5x.

If your boiler is currently 3x oversized for the load you'll only have a problem if the 4 new zone loops will more than triple the heat load (roughly proportional to the square feet of conditioned space, with large margins of error.)

About how many square feet of conditioned space is currently served by the boiler, and how much would the 4 new loops add?

Seriously, run the fuel use load calculation math (which also includes the distribution & standby losses that won't change much with added loops), and figure out the oversize factor. Run a room-by-room/zone-by-zone Manual-J(ish) load calculation on the new space that would be added using LoadCalc or CoolCalc (with aggressive rather than conservative assumptions on air tightness, etc.). This would be a necessary first step in figuring out what radiation to hang on those loops anyway. Then run a block load (the whole space, not room by room) Manual-J on the space currently heated by the boiler, and compare that to the fuel-use based load number. Nine times out of ten the load number will be ~25% lower than a cheap freebie Manual-J, in which case you should scale back the Manual-J proportionally, eg: The fuel use calculation says 47,000 BTU/hr the block load Manual-J comes in at 59,000 BTU/hr, so whatever the calculated room loads were for the added new zones would be whatever the tool came up with times 47/59. Since the standby losses weren't separable from the fuel use calculated load, even the scaled numbers are going to be bigger than reality.

Only with a reasonably accurate set of load numbers and the boiler's DOE output numbers would it be possible to make rational decisions on how to optimize system efficiency. (A tempering tank isn't going to do very much.)

I am curious, for people who have their own well and pump to get cold water, they pump it into a pressure tank. What prevents bacterial growth like legionella in cold water tanks? Obviously those don't get heated to 120 degrees yet millions of people use a well with a pump and tank for cold water. Hmm.

The sweet spot for legionella growth is between 85F and 115F, with the most active zone between 100-105F. (Hot tubs are terrible for this.) Most basements in your area would be under 70F in summer, and in most cases it would not much more than that in winter even with the jacket losses of an oversized cast iron boiler heating the boiler room.

If it's north of 85F in the boiler room in winter the efficiency problem has to be REALLY bad! Most cast iron boilers are cranked much hotter than they need to be in the first place, and if the distribution plumbing isn't insulated the pipes behave like a weirdly shaped convecting radiator. Cranking back the boiler's high temp to something more reasonable and insulating the pipes are cheap mitigation. Retrofitting a heat purging economizer control is pretty cheap too, and quite cost effective at 3x+ oversize factors. (Many/most new cast iron boilers come fitted with smarter heat purging controls as standard equipment, which reduces the efficiency hit from ridiculous oversizing.)

If the foundation walls in the basement are not air sealed and insulated the jacket losses are truly lost- more than 10x what they would be if the basement insulation was brought up to current IRC code minimums (= R15 continuous insulation in your climate zone.)

I am definatley intrigued by the idea of the hybrid heat pump water heater acting also as a dehumidifier. There is one corner of the basement that i do have a dampness and mold issue. We plan to do some serious excavating work outside the basement wall there and make some changes to improve drainage but i do occasionally run a dehumidifier in that area currently as needed. It would make lots of sense to swap out the conventional electric tank water heater for the apartment directly above that corner with one of of those hybrids and install it in the basement right underneath the one they were using. Even if we go tankless for the other 9 units, that one in that corner I think your idea would be perfect for instead.

If it's just one corner of the basement it's clearly a ground water or bulk water leakage issue. Surface grading to slope away from the building and exterior "French drain" surface drains are the first steps, followed by water sealing the foundation on the interior side (a whole other subject). Once the foundation walls are known-dry, insulating it with 2" (~R14) of HFO blown closed cell spray polyurethane) provides further waterproofing as well as air sealing and insulation.

How big is the basement? The absolute minimum amount of available volume to support a 50 gallon heat pump water heater (HPWH) is ~700 cubic feet (say a 9x9 room with 9' to the subfloor above with open joist ceiling). Twice or even three times that is better to avoid over-cooling the space during the shoulder seasons. If the basement is larger than 1000 square feet (probably is) multiple HPWHs may be be needed to have a significant dehumidification effect. Taking a WAG at it (without doing the math) with an uninsulated basement figure 500-700 square feet per HPWH to avoid over-cooling the basement in winter (assuming the boiler's losses get fixed). If the foundation gets air sealed and insulated that can probably drop to 400 square feet, 300 of you don't mind it occasionally hitting 45F or lower down there.

Nine gas tankless water heaters suitable for a cold-water location would be north of 1.5 million BTU/hr, which requires a HUGE gas service into the building- that needs to be checked!
 