Hello,
I know that electric space heaters are sometimes the cause of electrical problems (breakers/fuses tripping, parts of the circuit overheating, heater overheating because of poor design/materials, etc). However, I am trying to select heaters to use while we wait for service in the event that the primary heat source goes out.

1. How should I size the heater to be sure that it won't overheat the circuit or trip breakers?

2. Are there any brands that are know to be good or bad?

Thanks in advance!
 

Glennsparky

New Member
Messages
22
Reaction score
0
Points
0
Location
Oviedo, FL near Orlando
1. How should I size the heater to be sure that it won't overheat the circuit or trip breakers?
For 120V circuits, 1440 Watts will max out a 15A breaker. 1920 Watts will max out a 20A breaker.

You have to add up the heater watts and the watts of anything else plugged into that circuit.
 

Speedy Petey

Licensed Electrical Contractor
Messages
1,108
Reaction score
9
Points
38
Location
NY State, USA
For 120V circuits, 1440 Watts will max out a 15A breaker. 1920 Watts will max out a 20A breaker.
This is not true at all. Why do folks insist on perpetuating this MYTH???

1800 for 15A. 2400 for 20A.
Continuous loads follow certain rules for circuit loading. A portable space heater is not considered a continuous load.

I am no fan of space heaters. They cause more problems and fires than I care to know, but come on, facts are facts.
 
Last edited:

DonL

Jack of all trades Master of one
Messages
5,205
Reaction score
72
Points
48
Location
Houston, TX
I like the cheap Walmart Lakewood.

They are small and have a 750W and a 1500W setting.

I have a few in use and always use the 750 Watt setting.

1500 Watts is not safe for long periods.


Have Fun.
 

BobL43

DIY Senior Member
Messages
1,802
Reaction score
8
Points
38
Location
Long Island, NY
I like the cheap Walmart Lakewood.

They are small and have a 750W and a 1500W setting.

I have a few in use and always use the 750 Watt setting.

1500 Watts is not safe for long periods.


Have Fun.
Long periods are not safe, and never fun. Sorry Don, had to say that.
 

Dana

In the trades
Messages
7,889
Reaction score
509
Points
113
Location
01609
The little oil filled finned radiator types (DeLongi, and others) are quieter and safer from a fire-hazard point of than anything with a blower or radiant-reflector. Many/most come with dual elements a 600W and a 900W separately swichable, so you can have it pulling only 600W OR 900W if you don't think the circuit can handle 1500W), and an adjustable on-board thermostat to limit the surface temp of the unit. Shop around, and can usually find a pretty good one for under $50.

oil-filled-radiators.jpg
 
Last edited by a moderator:

Reach4

Well-Known Member
Messages
38,893
Reaction score
4,436
Points
113
Location
IL
While they are not space heaters, infrared heaters can make you more comfortable for fewer watts. The infrared produced turns to heat when it hits your skin or clothes (or anything else). So if it points to your sitting position, you can be comfortable with a lower air temperature. They will still heat the room as as well as a regular heater for a given power, but the infrared will make you feel warmer for the same watts.
 

Wet_Boots

Sprinkler Guy
Messages
799
Reaction score
2
Points
16
Location
Metro NYC
the Pelonis Disc Heaters were always touted for their safety, being that their thermistor heating elements never got fire-starting hot
 

DonL

Jack of all trades Master of one
Messages
5,205
Reaction score
72
Points
48
Location
Houston, TX
This is not true at all. Why do folks insist on perpetuating this MYTH???

1800 for 15A. 2400 for 20A.
Continuous loads follow certain rules for circuit loading. A portable space heater is not considered a continuous load.

I am no fan of space heaters. They cause more problems and fires than I care to know, but come on, facts are facts.



Why do you need to confuse things with the facts ?


People do operate them at 100% load when they get cold.
 

Wet_Boots

Sprinkler Guy
Messages
799
Reaction score
2
Points
16
Location
Metro NYC
It is kinda interesting/significant that these things seem to max out at 1500 watts, which is just a hair away from 80 percent of a 15 amp load.
 

DonL

Jack of all trades Master of one
Messages
5,205
Reaction score
72
Points
48
Location
Houston, TX
What's confusing?
And what does "100% load" have to do with it?


Nothing really.

You are correct for the circuit being able to handle the load. The Line cord and plug won't last long.

My 100% was about how people Put the heater on High, Blow and Go 100 percent of the time.

Just because a Microwave Oven has 100% Power does not mean that you need to use it. Popcorn requires 100%.


900 Watts is a good Max for what may be operating at 100 percent duty cycle and most likely is unsupervised.


Just make sure to install a Smoke Detector near the heater and have 911 in quick dial to operate the 1500 Watt mode.
 

Glennsparky

New Member
Messages
22
Reaction score
0
Points
0
Location
Oviedo, FL near Orlando
Please tell me where I can find this in the NEC. Thanks.
Since the OP said "emergency" and "primary heat" failure, I could only imagine that the space heaters would be on the highest setting all night. Then I thought about how many back stabs the circuit might have gone through. As such, I only felt comfortable with numbers that reflected all loads being continuous.

I admit to cowardice and cutting corners on my answer and I throw myself on the mercy of the court.

But I still side with DonL's posts.
 
Last edited:

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
Please tell me where I can find this in the NEC. Thanks.
For 120V circuits, 1440 Watts will max out a 15A breaker. 1920 Watts will max out a 20A breaker.

You have to add up the heater watts and the watts of anything else plugged into that circuit.
It is not the breaker that has a limit to the amount of amperage that can be plugged in but the receptacle has a limit that can be found here
Table 210.21(B)(2) Maximum Cord-and-Plug-Connected
Load to Receptacle

For a 15 amp receptacle be it on a 15 or 20 amp circuit the max load is 1440 watts
 

Speedy Petey

Licensed Electrical Contractor
Messages
1,108
Reaction score
9
Points
38
Location
NY State, USA
It is not the breaker that has a limit to the amount of amperage that can be plugged in but the receptacle has a limit that can be found here
Table 210.21(B)(2) Maximum Cord-and-Plug-Connected
Load to Receptacle

For a 15 amp receptacle be it on a 15 or 20 amp circuit the max load is 1440 watts
My point exactly.
I think people confuse this section for cord and plug connected equipment with total permissible circuit load, which is found in 210.24.
210.23 Permissible Loads.
(A)
(1) Cord-and-Plug-Connected Equipment Not Fastened in Place.
The rating of any one cord-and-plug-connected utilization equipment not fastened in place shall not exceed 80 percent of the branch-circuit ampere rating.

IMO if a plug fits the receptacle the load is OK. For instance, how can a 1500 watt heater, or an 1875 watt hair dryer legally come with a 15A plug since 210.23(A)(1) deems it illegal? The wattage ratings are either skewed, or they have some sort of "by" with regard to the code.
 

DonL

Jack of all trades Master of one
Messages
5,205
Reaction score
72
Points
48
Location
Houston, TX
I have a Heater that has 1300 or 1500 W and it will heat the internal thermostat so that it cycles on and off even if room temperature is cold.

That helps to save the outlet, but if it wasn't for the High Temperature Line cord then you could have problems, It does get Hot.

When the plug gets dirty, a little resistance makes a lot of heat when powering a 1500 Watt load.


Some of the Low Wattage heater models are good to run off of a portable generator.

Wood may be better for emergency heat. Or a Fat Lady, but food is expensive.


Have fun.
 

Wet_Boots

Sprinkler Guy
Messages
799
Reaction score
2
Points
16
Location
Metro NYC
speaking of high-temperature line cords, is it no longer possible to get some heater line cord (HPN) cut to length at a hardware store - I haven't seen any offered that way for years and years
 