I can only assume this would work.
The tub did not come with one? Usually they come with the panel with the GFI breakers already installed.
 

Speedy Petey

Licensed Electrical Contractor
Messages
1,108
Reaction score
9
Points
38
Location
NY State, USA
I was asked a question via PM from another member. With permission I'm re-posting it here:

Why can't you use more than 6' of the liquidtite? I got about 12' to go from the GFCI to the tub and was planning on using flex all the way (4x #6, ground included).
The answer is simply it is a code restriction.
NEC reference 680.42(A)(1)
 

Alectrician

DIY Senior Member
Messages
688
Reaction score
0
Points
0
I found this inexpensive Rainproof 2-4 circuit nonmetallic(plastic) 125amp box for $18. Any advice on this?



WTH? I have never seen a plastic panel.

As long as it's an outdoor panel and has your gfci breakers in it you are good.
 

frenchelectrican

Electrician
Messages
46
Reaction score
0
Points
0
Location
NE Wis / Paris France { In France now }
WTH? I have never seen a plastic panel.

As long as it's an outdoor panel and has your gfci breakers in it you are good.

yeah i did see few of them but myself i am not a strong fan with plastic box.

BTW Nailbender., with that box you got there one thing you have to watch out is the room to bend the wire with #6's it might get pretty tight in few spots.

If i know what that box brand name i can able tell ya the fastest and safest route to land the wires.

and if you going to run the GFCI on the plastic box make sure you bring out netural wire but ground wire have to be insluated green wire [ once it get outside of building ].

Merci, Marc
 

RickD7

New Member
Messages
2
Reaction score
0
Points
0
I was asked a question via PM from another member. With permission I'm re-posting it here:

The answer is simply it is a code restriction.
NEC reference 680.42(A)(1)

Thanks Speedy Petey,

So solid plastic pipe buried all the way (18 in., right?). Will a 1" pipe be ok for four #6 wires in regards to heat dissipation?
 

Bob NH

In the Trades
Messages
3,310
Reaction score
9
Points
0
Location
New Hampshire
You can't run the NM wires outside in conduit of any kind. You will have to use THWN or some other kind of wire that is rated for wet locations. You will usually find that wire rated for THHN also rated as THWN.

The wire you need is #6 for the hot conductors (#8 will actually handle 50 Amps), and #8 for the white and ground. Those will fit in a 3/4" rigid or flex conduit. You may need the 1" if they are all #6.

The load calculations would let you run smaller wires (THWN) but the inspector on a recent project that I did required the larger wires.

Rigid PVC is easy to run and it is easy to pull if you use lubricant. You can connect flex to the end using a adapters and pull the wire through both at once.
 

Alectrician

DIY Senior Member
Messages
688
Reaction score
0
Points
0
I found this inexpensive Rainproof 2-4 circuit nonmetallic(plastic) 125amp box for $18. Any advice on this?

Are the 2/30 and 2/20 GE GFCI breakers you need available? How much??
 

Nail Bender

New Member
Messages
14
Reaction score
0
Points
0
Location
Houston, TX
You can't run the NM wires outside in conduit of any kind. You will have to use THWN or some other kind of wire that is rated for wet locations. You will usually find that wire rated for THHN also rated as THWN.

The wire you need is #6 for the hot conductors (#8 will actually handle 50 Amps), and #8 for the white and ground. Those will fit in a 3/4" rigid or flex conduit. You may need the 1" if they are all #6.

The load calculations would let you run smaller wires (THWN) but the inspector on a recent project that I did required the larger wires.

Rigid PVC is easy to run and it is easy to pull if you use lubricant. You can connect flex to the end using a adapters and pull the wire through both at once.


Bob, If I run nm thru the attic and out the soffit down 5 feet to a sub panel, Do I still need to run THWN wire for the exterior 5 feet pre-sub portion?
If so where will I splice down to Thwn?
I know post sub panel I will have to run THWN to the circuit board.
 

Nail Bender

New Member
Messages
14
Reaction score
0
Points
0
Location
Houston, TX
Are the 2/30 and 2/20 GE GFCI breakers you need available? How much??

I just assumed they would be available but never checked on that yet, not to mention the price. I usually never have trouble locating things here in the city . I'll let you know tommorow.
 

Bob NH

In the Trades
Messages
3,310
Reaction score
9
Points
0
Location
New Hampshire
Bob, If I run nm thru the attic and out the soffit down 5 feet to a sub panel, Do I still need to run THWN wire for the exterior 5 feet pre-sub portion?
If so where will I splice down to Thwn?
I know post sub panel I will have to run THWN to the circuit board.

I was remarking relative to the comment by RickD7 about burying the conduit 18", without noticing that it wasn't you.

My comment about not using NM is related to the requirement that NM can't be used in any location that is classified as "wet" by the code.

If you have to change wire types you would have to splice it in a box somewhere. I don't believe that a conduit fitting has enough volume to meet the code requirements for a junction box.
 

Nail Bender

New Member
Messages
14
Reaction score
0
Points
0
Location
Houston, TX
I was remarking relative to the comment by RickD7 about burying the conduit 18", without noticing that it wasn't you.

My comment about not using NM is related to the requirement that NM can't be used in any location that is classified as "wet" by the code.

If you have to change wire types you would have to splice it in a box somewhere. I don't believe that a conduit fitting has enough volume to meet the code requirements for a junction box.

Oh ok ,I was just planning on taking nm out of structure and run it the 5' in conduit to panel.
 

Alectrician

DIY Senior Member
Messages
688
Reaction score
0
Points
0
I was just planning on taking nm out of structure and run it the 5' in conduit to panel

You can sleeve that portion of the NM. It is an exception somewhere in the code (anybody???). It is basically the same thing they do for rooftop AC units.
 

KD

New Member
Messages
207
Reaction score
0
Points
0
3/4 sealtight or PVC 40 will take 4 #6 THHN wires. You could strip the sheathing and run the 6-3wG in 3/4 conduit.
 

Nail Bender

New Member
Messages
14
Reaction score
0
Points
0
Location
Houston, TX
Ok
I like you guys to look at this and give me your expert opinions.
The diagram shows the neutral and ground on different bars. If you look at the sub I have here, there is only one bar. I bought a spare bar to install but I would like to consult with you all first. Let me know what you all think.

Spa-diagram-image2.jpg
 

Attachments

  • Spa diagram image2.bmp
    62.5 KB · Views: 3,724
Last edited by a moderator:

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
Oh ok ,I was just planning on taking nm out of structure and run it the 5' in conduit to panel.
This is a code violation
3/4 sealtight or PVC 40 will take 4 #6 THHN wires. You could strip the sheathing and run the 6-3wG in 3/4 conduit.
This is a worse code violation.
310.8(C) Wet Locations. Insulated conductors and cables used in wet locations shall be
(1) Moisture-impervious metal-sheathed;
(2) Types MTW, RHW, RHW-2, TW, THW, THW-2, THHW, THHW-2, THWN, THWN-2, XHHW, XHHW-2, ZW; or
(3) Of a type listed for use in wet locations.


The flex in the PVC is a code violation
 
Last edited by a moderator:

Alectrician

DIY Senior Member
Messages
688
Reaction score
0
Points
0
Can you cite the violation?

I am SURE you are allowed to sleeve NM. It is done every day on roof top AC units and to protect short pieces go to eave lights etc.



Tell me you didn't run that pvc down and loop it into the bottom? That SCREAMS homo(wner) !!:eek: It works and everything but it is u g l y.

If you don't have a hole saw at LEAST use an LB/chase nipple into the side.

I don't know if I WANT to see it exiting from the gable/eave:mad:
 

Nail Bender

New Member
Messages
14
Reaction score
0
Points
0
Location
Houston, TX
Can you cite the violation?

I am SURE you are allowed to sleeve NM. It is done every day on roof top AC units and to protect short pieces go to eave lights etc.



Tell me you didn't run that pvc down and loop it into the bottom? That SCREAMS homo(wner) !!:eek: It works and everything but it is u g l y.

If you don't have a hole saw at LEAST use an LB/chase nipple into the side.

I don't know if I WANT to see it exiting from the gable/eave:mad:

Yea I don't have a hole saw .What is a LB/Chase nipple and what does it look like?

As far as the pvc/flex joint. What is a better way of getting it under the sub or is there an adpter to fit it in the main on top that is appx. 2 1/2" wide?
Yea I wouldn't want the work to be obvious that a "homo(wner)" did it himself. : )
by the way the pvc goes thru the eave where it meets the wall.
 