    I have a 3/4 hp sub. pump with two tanks, 62 & 20 gallon furnishing two homes. Lately I have noticed the pump running ever so often, maybe ever 15 to 20 minutes. I turned the water off where it leaves the pump house and it still leaks down. I figure I either have a hole in the line in the well or could it be a check valve leaking, or is there something else that would cause this? The line in the well is the black plastic 160psi but it has been there for probably 25 years. I appreciate any advice you can give me.
     
  2. valveman

    valveman Moderator Staff Member

    Joined:
    Mar 15, 2006
    Occupation:
    Pump Controls Technician
    Location:
    Lubbock, Texas
    You are on the right track. I am guessing the check valve on the pump.
     
  3. Sponsor

    Sponsor Paid Advertisement

     
  4. wondering

    wondering Member

    Joined:
    Dec 10, 2006
    Got this leak fixed. The line had a split where it connected to the pump. Now I have a question:

    I have always used a 40/60 and even at one time a 40/70 pressure setting. When the leak was getting bad I had changed it to 30/50 thinking it might not leak down as fast ,using it this way until I could get the guy out to check it. Now I wouldn't mind turning it back up, so that is my question, Do you think if I set it up again it might split my line again? I have had this line connected to this pump for 11 years and this is the first trouble I have ever had. The line is about 25 years old though because it was used with another pump. The guy that fixed it said it was just from the pump starts/stops and the line twisting that causes them to split. He also replaced the check valve while he had it out of the well. Appreciate any advice/thoughts you have on changing my pressure setting.
     
  5. WellWaterProducts

    WellWaterProducts In the trades

    Joined:
    Feb 23, 2011
    Location:
    Northwood NH
    If it gives you trouble again change the pipe. A few more pounds of pressure might make weak pipe break sooner.
     
  6. Texas Wellman

    Texas Wellman In the Trades

    Joined:
    Feb 9, 2010
    Occupation:
    Owner of a Water Well and Pump Repair Business
    Location:
    SE Texas-Coastal
    Another poly pipe pump bites the dust!!


    Sorry, I just couldn't help myself. ;)
     
  7. valveman

    valveman Moderator Staff Member

    Joined:
    Mar 15, 2006
    Occupation:
    Pump Controls Technician
    Location:
    Lubbock, Texas
    He didn't say but, I figure that old it is probably only 100# poly. So I thought that was pretty good for 25 years of cycling on and off. Cause I really don't think an extra 10 PSI is as hard on the pipe as when that check valve slams shut for every cycle.
     
  8. wondering

    wondering Member

    Joined:
    Dec 10, 2006
    It is 160 psi pipe. The first years(15) it was used on a 2 line jet pump. When I had to replace the pump, the guy installing the new submersible pump said he was going to use my existing pipe because "it was better than what he had". I figured what he had on the truck wasn't 160 psi so I said that would be fine. When he pulled the pump the other day to fix the leak, he ask then if I wanted to replace the whole line, that he had 160 psi pipe on the truck. He said since the split was right at the pump, if it were his he would just cut that off and continue using the current pipe so that is what I did. It may split again in no time or it could last several more years(I hope). It has been on the submersible for 11 years this March. I may set it back to 40/60. There are 2 houses--sometimes 3--on my well. When the 3rd house has pump trouble they can switch over and use my water, plus there are 25-30 cows that drink from my well. I have read here that nowdays pumps may only last an avg. 7 years so since mine is 11 years old it seems to be holding up well. I just hope it continues to.

    Thanks for your input. Any ideas how to get many years out of a pump or is that just a wait and see thing?
     
Similar Threads: Water Leak--Am
Forum Title Date
Pumps and Tanks Well Forum & Blog Thermal Expansion Tank, CSV, Well water system... Thursday at 4:27 AM
Pumps and Tanks Well Forum & Blog Disconnect roof drain pipe or pipe the water into the sewer before backflow preventer? Jan 19, 2015
Pumps and Tanks Well Forum & Blog Tiny house gravity fed water system.....low pressure Jan 17, 2015
Pumps and Tanks Well Forum & Blog New Water Storage System Jan 10, 2015
Pumps and Tanks Well Forum & Blog adding a pump to city water Jan 5, 2015

Share This Page