Water Heater - Incomplete recirculate loop

Discussion in 'Water Heater Forum, Tanks' started by monty, Jul 30, 2013.

  1. monty

    monty New Member

    Messages:
    41
    Location:
    San Francisco
    I am responsible for replacing a failing water heater at my work location - that is a pretty easy solution...take out the old State water heater and put in a new one. Simple & Done.

    However, I was looking at the installation and there is a Grundfos pump (Model UP 15-18 SU) connected to an insulated pipe that "T's" into the cold water inlet. This is a hot water return line and comes from the ceiling above our 2 bathrooms that are about 20ft from the hot water heater. The pump is not wired up at all (never has been) - so it has never been used in 15 years...There is no expansion tank (the original building plans called for one), or a temp sensor in the pipe.

    I have 1 Kitchen Sink and dishwasher that is 3 feet from the existing hot water heater location. This is a business location - Mon-Fri hours - so a timer or motion sensor in the bathrooms to trigger a recirculate pump would be the a nice thing. I don't want to spend a bunch of money updating this system, but want to see how I could get it running.

    Any help would be appreciated! - Thanks

    IMAG0251.jpg

    Attached Files:

  2. Terry

    Terry Administrator Staff Member

    Messages:
    14,776
    Location:
    Bothell, Washington
    [​IMG]

    I have done the recirc both into the bottom of the water heater, removing the existing drain and installing a tee for the recirc,
    And I have used the incoming cold for the recirc. Normally for the incoming cold, I would have a check valve to prevent the recirc from going upstream, and add an expansion tank.

    Regardless, I use a spring check on the recirc line.

    The Aqua Stat is a nice touch on the recirc. It shuts the pump off when the heated water has completeted the loop.
Similar Threads: Water Heater
Forum Title Date
Water Heater Forum, Tanks Noob question about hot water heater Jul 13, 2014
Water Heater Forum, Tanks Water heater size with and without tempering valve Jul 12, 2014
Water Heater Forum, Tanks Venting options for gas water heater Jul 6, 2014
Water Heater Forum, Tanks Water Heater drain valve failure Jun 26, 2014
Water Heater Forum, Tanks water heater over temp (T & P ) valve piping question Jun 25, 2014

Share This Page