Discussion in 'Plumbing Forum, Professional & DIY Advice' started by pghsebring, Oct 7, 2011.

  1. pghsebring

    pghsebring DIY Member

    Joined:
    Oct 23, 2008
    Location:
    Ohio
    Never had to combine vents in attic before. Always went straight out roof with one stack. Now i have 3 vents going up 3 walls i need to combine in attic. Any tricks to this? Is it as straight forward as it seems? Flip a sanitee over, make sure there's 1/4" pitch on the horizontal? Since i have 2 lines that need to come to the third one that goes out roof, how high above the joists would you put the first horizontal? A couple inches or a foot? I've never seen this done in person, just in books, that's why i'm asking. Anything i need to watch out for?

    Thanks in advance.
     
  2. Terry

    Terry Administrator Staff Member

    Joined:
    Aug 17, 2004
    Occupation:
    Plumber
    Location:
    Bothell, Washington
    The vents can rest on the framing.
     
  3. Sponsor

    Sponsor Paid Advertisement

     
  4. Tom Sawyer

    Tom Sawyer In the Trades

    Joined:
    Nov 29, 2010
    Location:
    Maine
    Yea, they need to pitch back towards the drain(s) but not necessarily a quarter inch per foot. Just enough to make them drain. Most guys use upside down plastic J hangers. I like to use strips of 3/4 plywood with holes drilled in them.
     
  5. Gary in NJ

    Gary in NJ New Member

    Joined:
    Apr 11, 2010
    Location:
    NJ
    Also, the three vents do not need to connect at the same location.
     
  6. LLigetfa

    LLigetfa DIYer, not in the trades

    Joined:
    Feb 6, 2011
    Occupation:
    Information Technology
    Location:
    NW Ontario, Canada
    Use lots of supports as the pipe can sag from the heat. I watched an episode of "Ask This Old House" recently where Richard had to redo a horizontal vent in an attic that had a sag which completely filled with water.
     
  7. hj

    hj Moderator & Master Plumber Staff Member

    Joined:
    Aug 31, 2004
    Occupation:
    Plumber
    Location:
    Cave Creek, Arizona
    It is pretty much, "do it however it works best for you". There are few "regulations" regarding vents as long as they do NOT turn downward before connection together.
     
Similar Threads: Tips/tricks vents
Forum Title Date
Plumbing Forum, Professional & DIY Advice Any tips/tricks on tightening flange bolts? Mar 2, 2014
Plumbing Forum, Professional & DIY Advice Using Studor vents part 2 Jul 22, 2015
Plumbing Forum, Professional & DIY Advice Using studor vents Jul 14, 2015
Plumbing Forum, Professional & DIY Advice Basement bathroom reno, no vents Jun 24, 2015
Plumbing Forum, Professional & DIY Advice Roof vents too short? Apr 17, 2015

Share This Page