Shortening baseboard radiator

Users who are viewing this thread

Pete C

Member
Messages
87
Reaction score
0
Points
6
Location
Connecticut
Just put in new kitchen cabinets. I have a low pullout draw which can not be fully opened due to a baseboard radiator. I could just lop a foot or so off the radiator, but this side of the house is already a bit cooler thanks to earlier project where a few sections of baseboard went away so I really want to avoid losing more.

I have an idea to kill two birds with one stone.

I would like to build a combination rad. cover/bench that would be about 4 ft long. The current rad. is 6 ft. Can I just run another section of radiator right in front of the existing one for a total of 8 ft? How will this perform compared to the existing 6 ft?
 

Reach4

Well-Known Member
Messages
38,749
Reaction score
4,400
Points
113
Location
IL
Probably too late to consider, but there are kickspace heaters/radiators for hydronic that have a thermostatically controlled low power electric fan.
 

Dana

In the trades
Messages
7,889
Reaction score
509
Points
113
Location
01609
With crummy fin-tube baseboard you get maybe 550-600 BTU/hr per running foot at an AWT of 180F, so an 8-footer is only good for about (optimistically ) 4800 BTU/hr, but more realistically closer to 4000 BTU/hr.

A 5"deep x 20" tall Arco Sunrad or Burnahm Radiant radiator puts out 170 BTU/hr per inch of running length @ 180F AWT, so even a 30-incher would put out slightly more heat than your 8' baseboard. Since you want a bit more heat into that room something between 32-40" wide is probably about right. You can build a bench over it if you like- it's about the right height. They're designed to be recessed into kneewalls or under windows, or free-standing. (They put out slightly more heat if it's free-standing than when tucked into recess, of course.)

Brand new they're pretty pricey, but these come up regularly on places like Craigslist for cheap, since they were very popular in post-WW-II houses in the late 1940s & 50s. They clean up nicely if you want to take the trouble to sand-blast & refinish- I've seen some done with gloss automotive paints that look like a million bucks, but I usually lightly sand them by hand & use acrylic latex interior paints. (For steam heating systems use a high-temp paint.)

Several years ago I picked up a 40" and a 56" SunRad in Lyme CT ($100 for the pair- well worth the drive from Worcester MA!) for use in my own home when micro-zoning the heating system. The direct radiation aspects of them are far more comfortable than baseboard, and would make more sense than baseboard for a warming bench. The thermal mass would keep the bench from cycling hot/cold too. One of the 27" Arco SunRads this guy is selling would be about right as a direct upgrade from your 8' baseboard at the same output, but if you want more heat hold out for a slightly longer one. They're out there, and they show up all the time in CT/MA. Like all cast iron rads they're pretty heavy- handle with care. (Moving them from the basement where I painted them all the up to the 2nd floor by myself took some clever belayed rigging and a come-along.)
 