'Nuther S-Trap Dilemma

Users who are viewing this thread

Triumph TT

New Member
Messages
4
Reaction score
0
Points
1
Location
Quebec
I just finished dry fitting our his/her sink plumbing in the master bath. A friend "apprentice" plumber chimed in to say it is no good. I know S-Traps are no-no's but properly vented may pass inspection??? The vent also picks up the shower and tub under the floor.

Am I good to glue or not? Thanks in advance for the expertise.
 
Last edited:

Terry

The Plumbing Wizard
Staff member
Messages
29,946
Reaction score
3,460
Points
113
Location
Bothell, Washington
Website
terrylove.com
That is totally wrong.

The vent for the lavs will come off above the trap arm, not below.
The revent is at 42" above the floor. You can't run a dry vent below the flood level of the fixtures being served.
The trap goes into a vertical santee, with the vent out the top, reventing at 42" above the floor.

Now I need to rest my eyes. It hurt looking at that. :)
 

hj

Master Plumber
Messages
33,599
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
quote; S-Traps are no-no's but properly vented may pass inspection??

There is NO WAY to 'properly vent" an "S" trap, which is why they are forbidden.
 