New water softener system awaiting installation, few questions.

Users who are viewing this thread

Tom Sawyer

In the Trades
Messages
3,625
Reaction score
34
Points
48
Location
Maine
Well, he can always use copper clad bell hangers which are a whole lot less expensive than unistrut and require little skill or effort to install. Strapping it directly to concrete is always a bad idea because the lime in the concrete will eat through the copper eventually. Or he could just do the trailer on wheels thing and run garden hose across the ground LOL
 

ditttohead

Water systems designer, R&D
Messages
6,088
Reaction score
455
Points
83
Location
Ontario California
Well, he can always use copper clad bell hangers which are a whole lot less expensive than unistrut and require little skill or effort to install. Strapping it directly to concrete is always a bad idea because the lime in the concrete will eat through the copper eventually. Or he could just do the trailer on wheels thing and run garden hose across the ground LOL

hahahahah :)

Also, I have not seen a powder coated vibration dampening unistrut clamp yet. Please show me one, that would be an interesting, and bad design.

I have seen the green painted (possibly powder coated) unistrut channel, but once you cut it, you should touch up the paint to prevent rust. I just use the stainless 304, it is fairly inexpensive and you never have to worry about customers calling for rust issues in the future.

Repair work, and simple installs, the 304 stainless is just fine. For major construction jobs, the use of less expensive materials would make sense.

And how to mount to stucco? Not sure why you couldnt answer that yourself. A simple wall anchor, toggle bolt, find a stud, ... do I need to add how to mount stuff to walls to my training seminars?

toggle.jpg
 

Marcelo73

New Member
Messages
24
Reaction score
0
Points
0
Location
Los Angeles
Hello gentlemen, im back after being in hiding for a few weeks. Well as I had initially thought 5-6 hours labor, lmao yeah right, with my 2 year old trying to help me anytime I went outside to work on this project, a 9month old little girl, some rain and oh ya and ....WORK, has now turned into weeks. These past few days ive dedicated maybe 2 hours total to the project, and the hardware store runs are really beginning to kill all my time, no such thing as a quick hardware run in the big city.

I've tested my water using the hach 5b kit, its at 15 gpg.

At any rate I want to thank everyone who has chimed in on this thread.

Now for the subject at hand, I am a bit confused after talking with a gentlemen at the "hardware" store about my install. He mentioned water heater and that I should've plumbed into the plumbing at this source, this confused the heck out of me as I thought I had it all figured out. I have posted a photo of what im working with and what my plans were.

Not sure if this would even be an option but in case anyone is wondering my water heater is located directly to the rear of my house, about 40'-50' away from the softener.

Below is the main i will tapping into for the installation. On lower left is the pipe coming off of the main, then lower right pvc is for sprinkler system.
mainwater_zps1a0339e0.jpg
okpix_zps5c78f310.jpg


This is the photo with my plumbing diagramed, elbows along the vertical main with in/out to softener. The water spout will be replaced down on the horizontal pipe with a t-coupling so it is plumbed before the soft water.

mainwater22_zpsbe786b38.jpg


Excuse my photo shop crooked lines.


Thanks again to all of you for your help, I hope to wrap this up
 

Mikey

Aspiring Old Fart, EE, computer & networking geek
Messages
3,024
Reaction score
17
Points
38
Location
Hansville, Washington
Since the experts are still in bed, I'll offer my educated opinion. The softener needs to be installed at the point where you want soft water to be available, period. In many homes, there's a utility room where the water heater sits, often at the point of entry of the water main, with electricity available, and that's a convenient spot for the softener as well. That's obviously not the case in your situation, so ignore the hardware store guy. It's nice if the softener can be located out of the weather, but not critical. These days, indoors is better to reduce the theft risk, though -- they'll steal anything that's not nailed down. Speaking of nailed down, I wonder if earthquake regulations in CA require strapping down the softener tanks like the water heater?
 

ditttohead

Water systems designer, R&D
Messages
6,088
Reaction score
455
Points
83
Location
Ontario California
The location of the softener varies regionally. In the Southern California area, outdoor intallations are very common since the risk of freezing is basically non existant. I have been unable to find any exact code wording on the subject, maybe some of the qualified experts can chime in on this idea. Bury the softener. A simple post hole digger, 20 minutes of work, and the softener basically disappears. I know of many dealers that do this to save considerable cost on copper and labor, as well as simplicity. They remove the bottom base from the tank, buy a stainless jacket, insert the jacket into the hole in the ground, slide the system down and voila! Leave the head and a few inches of the tank above the ground of course. The tank jacket allows for easy removal in the future if it is needed. Standard disclaimer, check with your local codes... Many guys even bury the brine tank. Otherwise, the brine tank can easily be located 20-40 feet away without any problem. I would recommend the 7000 since it is actually outdoor rated.

Note:, I would recommend installing a brass ball valve to the sprinklers so that if the pvc breaks, you dont have to shut down the whole house.

A fake rock cover is often installed over the head as well to hide the system.
 
Last edited:

Marcelo73

New Member
Messages
24
Reaction score
0
Points
0
Location
Los Angeles
Since the experts are still in bed, I'll offer my educated opinion. The softener needs to be installed at the point where you want soft water to be available, period. In many homes, there's a utility room where the water heater sits, often at the point of entry of the water main, with electricity available, and that's a convenient spot for the softener as well. That's obviously not the case in your situation, so ignore the hardware store guy. It's nice if the softener can be located out of the weather, but not critical. These days, indoors is better to reduce the theft risk, though -- they'll steal anything that's not nailed down. Speaking of nailed down, I wonder if earthquake regulations in CA require strapping down the softener tanks like the water heater?

Yes I was thinking about installing a motion detection theft deterrent , hahahahhahaha. Ya unfortunately I live in an older smaller home without a utility room. As for the strapping down, the tanks and pipes will be attached accordingly using the unistrut and strut clamps DITTOHEAD referred of, these little things work great and are actually inexpensive at mcmaster which is local to me.
 

Marcelo73

New Member
Messages
24
Reaction score
0
Points
0
Location
Los Angeles
The location of the softener varies regionally. In the Southern California area, outdoor intallations are very common since the risk of freezing is basically non existant. I have been unable to find any exact code wording on the subject, maybe some of the qualified experts can chime in on this idea. Bury the softener. A simple post hole digger, 20 minutes of work, and the softener basically disappears. I know of many dealers that do this to save considerable cost on copper and labor, as well as simplicity. They remove the bottom base from the tank, buy a stainless jacket, insert the jacket into the hole in the ground, slide the system down and voila! Leave the head and a few inches of the tank above the ground of course. The tank jacket allows for easy removal in the future if it is needed. Standard disclaimer, check with your local codes... Many guys even bury the brine tank. Otherwise, the brine tank can easily be located 20-40 feet away without any problem. I would recommend the 7000 since it is actually outdoor rated.

Note:, I would recommend installing a brass ball valve to the sprinklers so that if the pvc breaks, you dont have to shut down the whole house.

A fake rock cover is often installed over the head as well to hide the system.


Are you serious about burying them, hahahahhahahaha.....CALL BEFORE YOU DIG!!! alot of digging for 3 tanks, but yes it would definitely keep copper costs down.

Thanks for the recommendation on the valve, I will certainly do that, in fact every time I turn that thing off it feels like its about to snap.

Thanks fellas since there is no objections so far to my schematics I will go ahead and continue as soon as the weather permits here in Los Angeles.

Merry Christmas to everyone!!
 

Gary Slusser

That's all folks!
Messages
6,921
Reaction score
22
Points
38
Location
Wherever I park the motorhome.
Website
www.qualitywaterassociates.com
I wouldn't install it that way. The softener would be before the pressure regulator valve. That is a bad idea.

And I don't know if it matters but suspect it does, the PRV is installed upside down and I've never seen one installed that way. It allows sediment to have built up in it and that may prevent it from working correctly.
 

ditttohead

Water systems designer, R&D
Messages
6,088
Reaction score
455
Points
83
Location
Ontario California
I wouldn't install it that way. The softener would be before the pressure regulator valve. That is a bad idea.

And I don't know if it matters but suspect it does, the PRV is installed upside down and I've never seen one installed that way. It allows sediment to have built up in it and that may prevent it from working correctly.


Correct, definetly relocate the pressure regulator before the softener, and after the irrigation. I also just notice that somebody installed the ball valve handle on upside down.

Sorry for the very crude drawing, but I think this is waht you should do. I would basically completely replimb the section in front of the house as follows. I would also recommend replacing the PRV, or maybe rebuild it. I am not a fan of doing this much work and not doing it all.
Sorry for the crude drawing, but you get the idea.basic.jpg
 

Gary Slusser

That's all folks!
Messages
6,921
Reaction score
22
Points
38
Location
Wherever I park the motorhome.
Website
www.qualitywaterassociates.com
I wouldn't install the softener per your drawing either.

I'd install the softener on the right side of the plumbing after installing a new PRV valve or taking the present one apart to clean it, and getting it right side up, and then remove the pressure relief valve (PRV) and go on to my softener inlet but....

I would cut the vertical line above the main shut off valve and the irrigation TEE so as to lower the hose bib/PRV horizontal line about 2" (without interfering with the access to the irrigation line valve handle) so I could unsolder the TEE on the house line now and then install an elbow on the line into the house to connect my outlet line from the softener.

If I were going to bury anything, I would be very careful digging so I could find any underground lines without damaging them. If the irrigation is off to the right of the pics, the line probably goes along the house wall instead out away from the wall.

IOWs I would extend the present hose bib/regulator line to the right to the softener, leaving the existing hose bib valve/regular valve and irrigation lines as is. The regulator valve is on a union and the relief valve is threaded. I'd unsolder the TEE going into the house after getting the water out of the line by disconnecting that union.

I'd cut out about 2" of the vertical line from the main shut off valve and use a repair coupler to put it back together as is but with the regulator right side up and no relief valve (unless it's code) and then I'd put it on a tee and with it directing any water flow out away from the foundation of the house.

To solder the coupler you must get the water out of the line below it at least an inch but as far as possible is best. And to do that you shove a rag down inside the line using a screw driver etc. and soak the water up into it until the water is down as far as you can get it.

Fleck has the inlet come in on the right side as you face the valve. I would install a shut off valve in the inlet line. Outlet is on the left side as you face the valve. New inlet line comes in under the outlet and up into the inlet, outlet goes over the inlet line onto the line into the house.

People don't steal PVC, so instead of using copper, I would use 3/4" PVC pipe from the threaded end where the relief valve is now and to the copper going into the house. And I'd add a #4 bare copper ground wire from the copper coming up out of the ground to the copper going into the house. You could take that down into the dirt and along the house up to the copper below the main shut of valve so very little is visible... That is to maintain any main house electric panel ground using the present copper water line.

If you want a soft water hose bib, add it on a TEE in the softener's outlet line.
 

ditttohead

Water systems designer, R&D
Messages
6,088
Reaction score
455
Points
83
Location
Ontario California
The drawing is meant as a guildeline only, and it is not to scale:). Considering you are in LA, you should also install a pressure gauge after the regulator. Much of the greater Los Angeles area suffers from high pressure issues. Upwards of 250-300 PSI is not unusual in the middle of the night. A pressure bauge can be installed for less than $15 and it will allow you to monitor your water pressure. Here is an older article about the water main breaks caused by age, and mainly excessive pressure. http://www.latimes.com/news/local/la-me-watermain-break-map20-html,0,992598.htmlstory
 

Marcelo73

New Member
Messages
24
Reaction score
0
Points
0
Location
Los Angeles
I wouldn't install it that way. The softener would be before the pressure regulator valve. That is a bad idea.

And I don't know if it matters but suspect it does, the PRV is installed upside down and I've never seen one installed that way. It allows sediment to have built up in it and that may prevent it from working correctly.

Correct, definetly relocate the pressure regulator before the softener, and after the irrigation. I also just notice that somebody installed the ball valve handle on upside down.

Sorry for the very crude drawing, but I think this is waht you should do. I would basically completely replimb the section in front of the house as follows. I would also recommend replacing the PRV, or maybe rebuild it. I am not a fan of doing this much work and not doing it all.
Sorry for the crude drawing, but you get the idea.View attachment 18372

I wouldn't install the softener per your drawing either.

I'd install the softener on the right side of the plumbing after installing a new PRV valve or taking the present one apart to clean it, and getting it right side up, and then remove the pressure relief valve (PRV) and go on to my softener inlet but....

I would cut the vertical line above the main shut off valve and the irrigation TEE so as to lower the hose bib/PRV horizontal line about 2" (without interfering with the access to the irrigation line valve handle) so I could unsolder the TEE on the house line now and then install an elbow on the line into the house to connect my outlet line from the softener.

If I were going to bury anything, I would be very careful digging so I could find any underground lines without damaging them. If the irrigation is off to the right of the pics, the line probably goes along the house wall instead out away from the wall.

IOWs I would extend the present hose bib/regulator line to the right to the softener, leaving the existing hose bib valve/regular valve and irrigation lines as is. The regulator valve is on a union and the relief valve is threaded. I'd unsolder the TEE going into the house after getting the water out of the line by disconnecting that union.

I'd cut out about 2" of the vertical line from the main shut off valve and use a repair coupler to put it back together as is but with the regulator right side up and no relief valve (unless it's code) and then I'd put it on a tee and with it directing any water flow out away from the foundation of the house.

To solder the coupler you must get the water out of the line below it at least an inch but as far as possible is best. And to do that you shove a rag down inside the line using a screw driver etc. and soak the water up into it until the water is down as far as you can get it.

Fleck has the inlet come in on the right side as you face the valve. I would install a shut off valve in the inlet line. Outlet is on the left side as you face the valve. New inlet line comes in under the outlet and up into the inlet, outlet goes over the inlet line onto the line into the house.

People don't steal PVC, so instead of using copper, I would use 3/4" PVC pipe from the threaded end where the relief valve is now and to the copper going into the house. And I'd add a #4 bare copper ground wire from the copper coming up out of the ground to the copper going into the house. You could take that down into the dirt and along the house up to the copper below the main shut of valve so very little is visible... That is to maintain any main house electric panel ground using the present copper water line.

If you want a soft water hose bib, add it on a TEE in the softener's outlet line.

The drawing is meant as a guildeline only, and it is not to scale:). Considering you are in LA, you should also install a pressure gauge after the regulator. Much of the greater Los Angeles area suffers from high pressure issues. Upwards of 250-300 PSI is not unusual in the middle of the night. A pressure bauge can be installed for less than $15 and it will allow you to monitor your water pressure. Here is an older article about the water main breaks caused by age, and mainly excessive pressure. http://www.latimes.com/news/local/la-me-watermain-break-map20-html,0,992598.htmlstory


All duly noted, I wanted to avoid so much plumbing, but ive already spent all this dough thus far I don't want to mickey mouse anything. Thank you Mr Dittohead and Mr Slusser, suggestions much appreciated.
 

Marcelo73

New Member
Messages
24
Reaction score
0
Points
0
Location
Los Angeles
Im sorry Mr Slusser I got lost here.....Are these valves in place in case the softener every needs to be repaired or just stops working???

Fleck has the inlet come in on the right side as you face the valve. I would install a shut off valve in the inlet line. Outlet is on the left side as you face the valve. New inlet line comes in under the outlet and up into the inlet, outlet goes over the inlet line onto the line into the house.


Below i've sketched a rough draft of the new plumbing as suggested. Any new ideas or suggestions? The wife will take the kids for the day to allow me a day to get this done the right way, or at least try to. ;)




sketch-1.jpg
 

Gary Slusser

That's all folks!
Messages
6,921
Reaction score
22
Points
38
Location
Wherever I park the motorhome.
Website
www.qualitywaterassociates.com
Marcello, you drew what I described, the only (hand operated shut off ) valve I mentioned is on the outlet of the softener, dittohead had added like a dozen valves here'n there. I see no reason for more than my one on the outlet and even then, it isn't needed, just nice to have IF your by pass valve can't shut off water to the house while you troubleshoot a problem with the softener. And that's only needed IF the people inside the house can't follow directions to NOT USE WATER until they are told it's OK.... Fleck by pass valves don't do that as far as I know.

The only thing with your drawing is, I suggested installing the softener to the right of the existing plumbing and you drew it to the left and down while out from the wall. That's not a problem though, you can run the plumbing anywhere you need it to go. If you don't bury the softener, your inlet will go over to the left or right and then UP a couple feet, and then the outlet down and over to the left or right to the house copper.

if you've already bought the copper, then use it but any extra valves should be able to be returned with a receipt for a refund or store credit. Thinking about it, copper tubing and all fittings should be returnable as long as you didn't cut the tubing yet. PVC is much easier to work with and much less expensive. Plus it has a larger ID than the same size copper. And you could lightly sand it and paint it whatever color ya wanted to.

BTW, since dittohead's "professionals" here haven't asked yet, where are you planning to run the drain line? And what type material are you going to use?

I suggest a foot or two of 5/8" OD, 1/2" ID opaque PE tubing from the control valve to 3/4" PVC if you're going underground. It's nice to be able to see water flow or air bubbles in the drain line IF you have a problem with the softener.

I see you don't take the copper ground wire to the copper below the copper main line above or below the main brass shut off ball valve. That is where it has to/absolutely must go, not to a ground pin.
 
Last edited:

Marcelo73

New Member
Messages
24
Reaction score
0
Points
0
Location
Los Angeles
Marcello, you drew what I described, the only (hand operated shut off ) valve I mentioned is on the outlet of the softener, dittohead had added like a dozen valves here'n there. I see no reason for more than my one on the outlet and even then, it isn't needed, just nice to have IF your by pass valve can't shut off water to the house while you troubleshoot a problem with the softener. And that's only needed IF the people inside the house can't follow directions to NOT USE WATER until they are told it's OK.... Fleck by pass valves don't do that as far as I know.

Ok I see now I understand, I will certainly consider this.

The only thing with your drawing is, I suggested installing the softener to the right of the existing plumbing and you drew it to the left and down while out from the wall. That's not a problem though, you can run the plumbing anywhere you need it to go. If you don't bury the softener, your inlet will go over to the left or right and then UP a couple feet, and then the outlet down and over to the left or right to the house copper.

Mr Slusser unfortunately I can only come in off the left side where they are going to be stored and secured above ground safely there and there in/out lines soldered and ready to go.

if you've already bought the copper, then use it but any extra valves should be able to be returned with a receipt for a refund or store credit. Thinking about it, copper tubing and all fittings should be returnable as long as you didn't cut the tubing yet. PVC is much easier to work with and much less expensive. Plus it has a larger ID than the same size copper. And you could lightly sand it and paint it whatever color ya wanted to.

Yes, the copper fittings are nickels and dimes, alot of them and at 1'' for most they are adding up, and receipts are kept in safe place just in case.


BTW, since dittohead's "professionals" here haven't asked yet, where are you planning to run the drain line? And what type material are you going to use?

I suggest a foot or two of 5/8" OD, 1/2" ID opaque PE tubing from the control valve to 3/4" PVC if you're going underground. It's nice to be able to see water flow or air bubbles in the drain line IF you have a problem with the softener.

I have a drain wash out that is out of that picture frame but has very easy access to tap in with a vent, I was planning on using all pvc but the idea of viewing bubbles would be great, WAIT:rolleyes:, just so I know, hahahahah, bubbles mean problems? I guess ill deal with that when and if I get there.

I see you don't take the copper ground wire to the copper below the copper main line above or below the main brass shut off ball valve. That is where it has to/absolutely must go, not to a ground pin.

Understood I will run and attach to main vertical copper pipe.
 

Gary Slusser

That's all folks!
Messages
6,921
Reaction score
22
Points
38
Location
Wherever I park the motorhome.
Website
www.qualitywaterassociates.com
Yep, air bubbles in the drain water line, unless your brand of control valve adds them, like Clack, are not good.

They indicate that the brine line or something else is allowing air to be sucked into the resin tank (or the air is coming in with raw water) and... the only way air can get out of the resin tank is during a regeneration, specifically backwash.

Otherwise it sounds as if ya got a good plan for your installation.
 

Marcelo73

New Member
Messages
24
Reaction score
0
Points
0
Location
Los Angeles
Ok so as I mentioned to Mr Slusser in an email, after an almost complete day of work I finished up the install of my beloved softener just after midnight last night.

Excitement and deliriousness took over after install and I rushed to pour in the salt and fill brine tank with water, opppsss:rolleyes:, as instructed by Mr Slusser I went ahead and left the salt/water as is and followed his directions... since there should be air trapped in the tank, I went ahead and shut off the water ahead of the softener, Then i opneed the hose bib and relieved the pressure, turned the hose bib off, pluged in the control valve and put the control valve in the backwash position, I then turned on the main valve about a 1/4 and ran that water until all air was out of the tank (which should've taken but 5-10 seconds if that, but took a few minutes and only because I turned the water main completely on).

BUT im stuck at this point, is there a manual regeneration required or does the softener valve do the rest of the work, what do I do from here??? How do I know if it is working properly??? Aren't I supposed to program it for my family of 3 with 15 gpg? The only other thing I ve done on this valve is set the hour on timer.

Below are photos from the valve in its current state and a photo of my filled brine tank, its almost at the half way point but i need to grab probably 2 more bags to get it to half or just above it.


valve.JPG

brine.jpg


Any help or suggestions, I have just added that 1/2 cup of non scented bleach as suggested by dittohead in earlier portion of thread.


Thanks to all of you who made this project much easier for me with all your ideas and professional suggestions very much appreciated.




** UPDATE** At approximately 3:30 pm pst about 1.5hrs after this original post, I took a long warm shower. During this shower I didnt notice any difference in the water aside from almost a vinyl/rubber odor but then all of a sudden i'm getting a slight taste of salt, i taste the water and yep tasted very very salty, like sea water, a few moments later the taste is gone and water feels of slight slime/smooth, could this softener have kicked in?! The slight vinyl/rubber odor is still there ever so slight, but salt taste is gone and there is the softener feel is slightly there.
 
Last edited:

Gary Slusser

That's all folks!
Messages
6,921
Reaction score
22
Points
38
Location
Wherever I park the motorhome.
Website
www.qualitywaterassociates.com
After getting the air out did you let the control valve finish back to Service? If not it will have been regenerating while you were in the shower.

The manual you should have received with the unit or the people you bought the unit from should tell you how to program the valve.

I would not fill the salt tank with salt, 1/2 to 2/3rds is enough.
 

Marcelo73

New Member
Messages
24
Reaction score
0
Points
0
Location
Los Angeles
After getting the air out did you let the control valve finish back to Service? If not it will have been regenerating while you were in the shower.

The manual you should have received with the unit or the people you bought the unit from should tell you how to program the valve.

I would not fill the salt tank with salt, 1/2 to 2/3rds is enough.



Maybe I didn't let it finish its thing

The system was given to me by a friend, he was not a diy'r in fact he would call the service folks if there was ever a problem but I do have a pdf manual that was linked by dittohead, but i need to get the 45 or so pages printed to have in hand.

I will stop with salt now at your advice.

Thanks again.
 

Marcelo73

New Member
Messages
24
Reaction score
0
Points
0
Location
Los Angeles
Well i've programmed the valve, with hardness at 15, and capacity at 36, the brine setting is set at 12. I administered a water hardness test yesterday and results were in the area of 8 gpg, and this afternoon they are at 1 gpg.


My wife brought up an interesting question, did I service the system? I paused and said no! She asks because when she contacted the phone number on the tanks to inquire about installation they advised her that based on their records our system was due for a service. This service was somewhere in the area of 300 bucks or so. What all is included with this SERVICE they refer to. I tried to call them today but they are out of the office until Thursday. Other than this it appears the system is running as its supposed to.


Thanks again to all, and Happy New Year!!!!
 