    1976 bungalow in Victoria BC....moderate climate with relatively few days below freezing. House has one-year old Lochnivar WHN 110 boiler heating 160 linear feet of baseboards in three zones (designed with a primary loop and secondary loops) The boiler uses an outdoor reset and typically heats the house comfortably running at 20% and heating the system water to 115-118 degrees. The zone in which bathroom to be renovated operates has 76 feet of baseboards and the bathroom is question is 12X6 and is currently heated by 2 three-foot baseboards. I have good access to the bathroom from the crawlspace underneath, so piping changes are not a problem.
    I want to put in underfloor heating and replace one or both of the baseboards with a hydronic towel rack/heater. The question is given my system's operating perimeters, what combination makes the most sense?
    1) electric underfloor heat and replace one or both of the baseboards with a towel bar?
    2) replace the baseboards with pex/hydronic underfloor heating and a hydronic towel bar?
    I ask because I'm not sure how to calculate out heating requirements. My suspicion is that option 1 makes the most sense, but I would appreciate any guidance the boiler experts here could offer. I should add that Victoria is not exactly a hotbed of hydronic heating use....underfloor heating appears to becoming more popular in newer homes, by large it appears to be a town of electric baseboards or heat pumps.
    Thanks for any and all advice
    Eric
  2. Dana
    Dana In the trades
    Jan 14, 2009
    01609
    How many square feet of floor do you have available for the radiant floor- I'm assuming it's not the full 12' x 6' (or is it?) Give yourself at least a foot of clearance around the toilet, since you shouldn't be heating it, and don't count anything that is under a floor-mounted cabinet, etc., just the raw open square footage.
    And, what is the floor stackup starting with the underside of the sub-floor. Materials & thicknesses please.
    Is the existing baseboard is all ~600BTU/foot @ 180F type fin-tube? If yes, the existing 6' of fin-tube puts out about 160-170BTU/ft, or ~1000 BTU at your water temps. You can then work backward from there using the output of the radiant floor & towel rack specs.
    With the material stackup you can estimate the R value of the floor, and from there the BTU/hr per square foot you can get out of the using extruded aluminum heat spreaders at your ~115F water temp using the nomograph on p.4.
    Say your actual free floor area works out to about 50 square feet, and it's a subfloor of 3/4" plywood with thinset & ceramic tile above it. The plywood has an R value just shy of R1, and the thinset & tile add up to another ~R 0.6, call it R1.5 for the stackup. If you follow the R1.5 line on the nomograph in that other document to the 110-115F range you'll see it will deliver about 15-17 BTU/hr per square foot, so the floor will be good for 50' x 16 BTU/hr 800 BTU/hr.
    If the room is reasonably balanced with the rest of the zone at 1000 BTU/hr that means that if the floor is delivering 800BTU/hr, you can find a towel rack that puts out ~200BTU/hr @ 110F and be rid of the baseboard. The specified BTU output of radiators (including hydronic towel bars) is at a nominal 180F average water temp- the output at your water temps will be about 30% of that number. So a towel bar that's rated at about 600 BTU/hr @ 180F AWT (give or take a hundred or so) would be about right. If you preferred a bigger towel warmer, you could cut back on the amount of radiant floor, but if it's currently balancing temperature wise with the zone you want to keep it the total floor + rack to run between 900-1100 BTU/hr @ 110F AWT.
    Other heat spreader types will have different output, and the responsiveness & consistency will vary. Extruded aluminum heat spreaders are pretty good- more expensive than the stamped sheet metal, but for the amount of floor area you're talking it won't break the bank. You're looking at probably 3 joist bays 12' long with a pair of runs per bay for a total of 3 x 12' x 2= 72' of extrusion, at about $2/foot.
    Running it as a single run of 75-80' of half-inch PEX adds quite a bit of length to the zone loop, and it's advisable to set it up as a pair of equal-length loops with 2 x manifolds. The 6' of 3/4" baseboard has miniscule pumping head compared to 80' of half-inch PEX.
  4. rainy island
    Sep 3, 2013
    Victoria BC
    Dana,
    Thanks very much for your detailed reply....its exactly what I need and I'll take some time to chew through the materials you provided and make the calculations! Incidentally, I have about 33 square feet of "heatable" floor (netting out the obstructions you mentioned), and the final stack up will be 5/8 ply, 1/8 Hardiboard, thinset and then 1/4 ceramic tile.
    Thanks again for the informed response!
    Eric
  5. Dana
    Dana In the trades
    Jan 14, 2009
    01609
    At that stackup and 33' of space you're looking at about 500-550 BTU/hr out of the floor, so you'll need another 500-600 or so out of the towel rack, which would be something that puts about 1600-2000 BTU/hr @ 180F. (Runtal TW9-16 or TW9-20, or Buderus NB2432 are possiblilties.) If you err slightly to the high-side you'll have warmer towels and the bathroom might run slightly warmer if you normally keep the door closed when unoccupied, neither of which is a bad thing, and with towels hanging on it the output to the room will be reduced from it's free-air ratings. What you DON'T want do is put a rack rated at 3500BTU/hr @ 180F or higher or it could get downright sweaty in there.
  6. rainy island
    Sep 3, 2013
    Victoria BC
    Thanks Dana. I used your suggested parameters and came to the same conclusion....I would need equal btu/h output from both the floor and the towel rack if I want to replicate the current heating. After measuring the bays in the crawl, I believe I have room for about 54 linear feet of pex and transfer plates. From your perspective, would this make the most sense if installed as a pair of 27-foot loops rather than in a single run? Also, I'd be interested in your opinion as to whether you think the addition of this much pex (and its additional pumping head), combined with a towel rack (that creates more of a pumping head than the slant fin baseboards) would throw the zone significantly out of kilter or whether its impact is immaterial?
    Thanks again for your insight!
    Eric
  7. Dana
    Dana In the trades
    Jan 14, 2009
    01609
    As long as you can get 2gpm or so it won't change much. The pumping head of a towel rack is very low, the pumping head of 55' of half-inch pex is something, but might not be a deal breaker. Splitting it into two 27' parallel loops is the rough equivalent of 27' of 3/4".
    Do the math on lengths of all of the existing plumbing, including the "equivalent length" of all the ells tees, etc (you can google up tables of such), and see where it comes out relative to your pump's output curve if you add 55-60' of PEX. A primer on how to do that lives here.
    Typical residential systems are designed for delta-Ts of 10-20F @ 2-4gpm. With outdoor reset the delta is smaller when the output temp is low, but higher when you're at peak temp, peak load. It doesn't hurt to measure the delta on the zone you're modifying first. (Hockey tape on copper pipe and an infrared thermometer is good enough measuring method), but if it's over 50F outside don't be surprised if it's under 10F. If you slow the flow significantly the delta will creep up, which can affect the room-to-room balance if it goes from a 10F delta to a 30F delta. Estimate the flow from your head calculations, as long as it doesn't drop by more than 30% with the single-loop pex it won't change the balance a whole lot, if it cuts the flow by more than half, it might.
  8. rainy island
    Sep 3, 2013
    Victoria BC
    Dana,
    Thanks for the advice. you've given me a lot to think on and I'll do some more reading before I decide next steps.
    As always, I really appreciate the insight.
    Eric
  9. rainy island
    Sep 3, 2013
    Victoria BC
    Dana,
    Following your excellent suggestions, I did my best to measure the total piping, els tees ect. and have arrived at the following:
    I have ~150 feet of 3/4 inch pipe in the zone, along with ~80 feet of baseboard and ~54 els. based on the primer you provided (and assuming the baseboards are the same as 3/4 inch pipe) my totals should be (150' + 80' + (54X2.00=108')=338' EFP. Multiplied by 0.04=13.5 feet of head. I also discovered the zone in question is tied to the front of my house which means 1/3 of the piping is covered by finished ceiling…hence the estimates as opposed to exact measurements.
    My circulation pump is a Grundfos UPS 26-99-FC set on low which according to the pump curve chart pushes ~7 GPM (or can go as high as 15 GPM or 22 GPM on speed 2 or 3 respectively). Thus adding two 27’ loop of ½ pex adds ~27’ of 3/4 inch pipe or 8% to the loop and increases the head from 13.5 feet to 14.6 feet and drops the flow to 6GPM.
    I haven't measured the delta T of the zone yet because we've had unseasonably warm weather, but based on the information above, does adding two 27-foot loops for the underfloor sound reasonable?
    Thanks again
    Eric
  10. Tom Sawyer
    Tom Sawyer In the Trades
    Nov 29, 2010
    Maine
    Boy, talk about overcomplicating a pretty simple problem. LOL Look, running pex or any underfloor heating is going to be expensive and a pain in the backside as well considering the
    small space you are dealing with. Several companies make flat panel steel radiators with the heated towle bar option. Another option is a toe space heater under the vanity cabinet.
  11. Dana
    Dana In the trades
    Jan 14, 2009
    01609
    But Tom, people who want radiant floors want radiant floors- doesn't really matter if it's overly complicated for dealing with a tiny load! :)
  12. rainy island
    Sep 3, 2013
    Victoria BC
    I appreciate that I'm likely overthinking this project and I agree that the easiest solution would be to install a hydronic towel bar and leave a baseboard in place. That said, my wife wants warm tiles, so I have to choose between underfloor hydronics or an electric radiant system. Judging by the latest comments, it appears that the addition of the the small underfloor loop(s) is a viable option so I'll have to choose between that and the electric option (and the addition of a new dedicated circuit and thermostat).
    Thanks again for the feedback and insight The primers on calculating flow and load etc were really informative and have given me a much greater appreciation for the mechanics of my heating system.
    Eric
  13. Tom Sawyer
    Nov 29, 2010
    Maine
    Ok so staple up as much 1/2" pex as you can get in the bays and put a tempering valve on that loop. Just adjust the tempering valve until you get the floor temperature you want.
  14. Dana
    Dana In the trades
    Jan 14, 2009
    01609
    A tempering valve is just adding a plumbing complication, and probably isn't necessary. His problem isn't keeping the floor temp down, but rather bringing the temp UP, given his reported low boiler output temps. This is a very temperate climate, where the mid-winter weekly highs are comparable to the mid-summer weekly lows.
    He claims he's able to heat with 115-118F boiler output almost all of the time. The average mid-winter heat load in winter in Victoria (outdoor temp= +37F) isn't that different from what it is at the 99% outside design temp (+26F). He's in no danger of overheating the floor with a staple-up, and even with extruded plates it won't be super-warm to bare feet even at design condition. Unplated it probably wouldn't feel very warm at the average outdoor temps. On that rare one day out of 100,000 that it hits +4F in Victoria (the all time record low, back in 1968, before his house was built) it might feel uncomfortable, but it wont' be dangerous. The coldest recorded temp of the past 25 years is +14F. The typical low temp over a Victoria winter is about +20F (which is how we can tell we're not in Maine anymore, eh, Toto? :) ) Over the life of the system he might need 140F boiler output during below design temp cold snaps but it'll probably stay under 130F otherwise.
    At 50F outdoor temps with <115F boiler output, probably a <105 AWT, a plated sub-floor installation won't be not going to be a hot-foot- the floor won't be nearly as warm as the shower he just stepped out of. When it's 30F outside it'll feel pretty toasty but still comfortable.
    If my WAG on water temps base on his "...comfortably running at 20% and heating the system water to 115-118 degrees..." turns out to be wrong, a tempering valve can always be added if the floor gets uncomfortably warm during the colder weather.
  15. rainy island
    Sep 3, 2013
    Victoria BC
    Interesting observations on Victoria weather....though I had to do a quick refresher on my C to F conversions.....I haven't had to think about those since we went metric up here in 1977 (though I defy you to find a Canadian who can truly understand fuel economy in something other than miles-per-gallon, or who can tell you how big a hockey player is in centimeters and kilos). For the record, I do own a snow shovel, but its gets 99% of its use moving leaves in the fall.
    That said, Dana's observations on the challenge posed by my low water temperatures are, I believe, correct. My house was originally built with an electric boiler that typically ran at 160F (and consumed a breathtaking amount of electricity even at British Columbia's very low hydro-electric costs). The baseboards would get really hot for 20 minutes then shut down cold for 20 and so on, irrespective of the outside temperature. I switched to natural gas Lochnivar and the installer (from a a firm with an excellent reputation in this town) set the boiler up so that it ran 115-118 degrees (according to the digital panel....the analogue temp/pressure gauge on the primary loop usually reads 110. As a result, my baseboards are warm for long periods, but never hot and the house temperature "feels" more stable instead of the hot/cold cycling we experienced through the first 6 months in the house with the electric only. In fact, I kept my electric boiler plumbed into the system on the assumption that, with apologies to Mr. Murphy, the gas boiler will conk out on the coldest Friday evening of a long weekend. The installer suggested that If I ever needed to heat my house rapidly, I should switch on the electric boiler because it would heat the system much faster than the gas boiler was programmed to. Indeed, other than for a couple of minutes following ignition, the system invariably turns down to a 20% rate of fire.
    I asked all these questions because my neighbour (yes, up here we spell it with a "u") installed three underfloor loops into his system and is pleased with the results. He runs an electric boiler at a higher water temperature, and didn't really do any research other than to simply trust that adding a whole bunch more pex would not impact the heating efficiency and balance of his system. As it turns out, it worked, but I suspect more due to intuition and luck than design and planning. In my case, I knew that with lower average water temperatures I had other factors to consider, and wanted to get some advice from folks like you who have given a lot of thought to the intricacies of mod/con boilers combined with the wrinkle of moderate outdoor temperatures.
    Again, I greatly appreciate your feedback and insight. It has been a tremendous help in my planning process.
    Thanks again
    Eric
  16. Dana
    Dana In the trades
    Jan 14, 2009
    01609
    With an electric boiler it's the same efficiency whether it's 180F water or 90F water, so running higher temp with unplated PEX has nearly zero effect on operating cost. With much higher temps you can push a lot more heat through the floor, and can lose the plates.
    But with a condensing gas boiler it has to stay under 120F at the return (where the water enters the boiler) to stay in the mid-90s for efficiency. At 180F output, 160F return even a condensing boiler is only delivering ~86% efficiency. At your operating temps you're probably north of 95%.
    Being a science nerd in my deep dark past, and an engineer in my current profession the F/C conversion thing is something I'm stuck with often, and in an heating design context it's gotten to the point I've memorized the fives: -5C is +23F, -10C is +14F, -15C is +5F, -20C is -4F, -25C is -13F, and -30C is too damned cold- colder than I ever want to think about. ;-) Don't ask me to convert cubic meters of natural gas to BTUs or therms & back without looking it up though...
    In Victoria your 99% design temp is quite a bit warmer than Tom's (and my) mean January temp, and above his daily high for many days of the year. I heat part of my home with about R2.5 floors with ~125F water, but it takes extruded plates to get there. A staple-up wouldn't come close to making it without bumping the water temps way up. Rather than making yours a dual-temp system, plating your patch of radiant bathroom floor seems comparatively cheap & reliable.
    I'm pretty familiar with the climate in your area having spent most of my childhood in the Puget Sound region. I have relatives across the Salish Sea from you on Whidbey Island as well as further down on the Kitsap Peninsula who I visit annually. It's been over 30 years since I've been to Victoria, but it strikes me as a very nice place to call home, one of the nicest small cities ever!
  17. nukeman
    nukeman Nuclear Engineer
    Nov 20, 2009
    Nuclear Engineer
    VA
    One more easy one to put in your back pocket: -40C = -40F
    Too cold for me, though. :)
  18. rainy island
    Sep 3, 2013
    Victoria BC
    Thanks, I think your suggestion of extruded plates seems like the ticket.
    As an almost lifelong resident of Victoria, I can assure you its changed little in the past 30 years with the exception of a bunch more homes, a far better selection of Asian and Indian restaurants and a whole bunch more older, slower drivers! Despite our great climate, Victoria proper is still only 100 k and the entire region is only 350k. I had to chuckle when you mentioned the Salish Sea, because if I lean back in my chair I can see San Juan Island and Mt. Baker across Haro Strait. Its a view I've seen off and on since 1974 when I moved here as a child. Sadly, I'm too stubborn accept that most people now refer to it by its new name. My daughter, however, can (and does) tell me all about it!
  19. Dana
    Dana In the trades
    Jan 14, 2009
    01609
    The fives are always easy, if you know how to add or subtract nine. (Since 5C = 9F)
  20. rainy island
    Sep 3, 2013
    Victoria BC
    Its been a while since I started this thread, but I'm finally in a position to start my reno's. The advice I received here has been invaluable and helped focus my thinking. I did, however, have one question with respect to the best way to connect the towel rack heater into my system.
    To recap, I plan to use my recently-purchased Runtal towel rack as the primary heat source to replace two hydronic baseboard heaters in my 75 square foot bathroom. Based on the calculations I did (and considerable domestic negotiations), I went with a larger towel rack and will install a much shorter loop of staple up radiant, primary to take the chill off the tiles.
    I will be connecting to an existing series loop of baseboards, and was curious as to whether I should connect the towel rack to the loop using a pair of venturi tees and ball valves or whether I should simply connect directly to the loop and allow the entire flow to move through the radiator. I ask because I've been reading a lot about my connection options, but have not found a compelling answer suggesting one option or the other.
    Thanks
    Eric
  21. Mainer_Portland
    Mainer_Portland New Member
    Oct 25, 2014
    Maine
    Greetings Eric!
    I wanted to check in with you to see if you heard anything back from the forum regarding your last (7/11/14) post on connecting your towel heater? I wondered if perhaps you may have heard back from some members offline or under another topic here that you could point me towards? Or since this last post from you is a few months old now, perhaps you have finished your project and could provide some pointers based on your recent experience?
    For some background information for you and others who may read this, my project is finishing off a ~83 square foot daylight basement bathroom with one 28” x 38” window. Due to several restrictions in this space, 3 ft of SlantFin MultiPak 80 (high density / high output) baseboard are planned for this space – mounted on an interior wall. Another foot of this baseboard would be ideal based on rough calculations from the SlantFin website (perhaps somewhat counterbalanced by the fact that not all of one of the two exterior walls are above grade). This loop is a total length of ~85 ft of ¾” PEX and there is one 4 ft section of standard output baseboard in an adjacent room prior to the 3 ft section of Multipak 80 in the bathroom I mentioned above – there will be no other baseboard in this loop before it returns to the boiler.
    To add a little luxury and ensure there is enough heat in this bathroom, I am considering adding a 24” x 30” towel warmer manufactured here in Maine by Pensotti w/ a 1621 BTU output @176°. My wife is European and loves this idea as she had towel warmers when she lived over there, years ago. However, while the plumber I am working with has decades of experience and is a good “common sense” sort of contractor, he has never installed a towel warmer before… (The connections will come out through the wall for this short height warmer and not through the floor.)
    I have done a lot of research into towel warmers, and like you, Eric, I have not found any clear cut preferences / directions / considerations as to how properly connect a towel warmer. Due to lots of burn cautions, my thought has been to tap into the cooler “return” line of ¾” PEX that follows after the 3ft section of Multipak 80 on its way back to the boiler. Perhaps plumb this tap in either ½” PEX or ½” copper to feed and return water from the towel heater. Because of concerns about burns / other problems from an overheated towel warmer and concerns about flow restrictions in this loop by necking down the flow in to ½” lines, I did not want to run all the flow through the towel warmer.
    But this raises another concern which is ensuring there is enough flow through the warmer to actually warm towels and add some heat to the bathroom. I know that companies like Raven make monoflow tees that I could use to go from the ¾” PEX into ½” PEX or copper to supply a towel heater. While there is a lot of information on using monoflow tees to supply water to a toe kick heater or a similar application, I have yet to find anything related to the same concept for a towel heater.
    Did you find any good advice to follow when installing your towel warmer?
    Many thanks in advance for your help!
    Steve
Similar Threads: hydronic heat
Boiler Forum Downflow gravity hydronic heating - bleeding radiators Dec 26, 2016
Boiler Forum What caused this on heat exchanger on peerless hydronic boiler? Oct 6, 2016
Boiler Forum 100% hydronic heating guy Mar 6, 2016
Boiler Forum Apartment Hydronic Heating Noise Question Nov 27, 2015
Boiler Forum Help choosing a control system and manifolds for Hydronic Heating Jan 8, 2014