Generators and well pumps

Users who are viewing this thread

Arky217

New Member
Messages
43
Reaction score
0
Points
0
Location
Arkansas
I have a Honda eu2000i generator.
It is rated 2000 watts surge/1600 watts continuous or 16.6 amps surge/13.3 amps continuous.

I have started and run a number of electric motors with it; motors that would seem to be too much of a load for it.
For example:
It starts and runs a 15 amp (FLA) Milwaukee chop saw.
It starts and runs a 15 amp (FLA) circular saw.
It would not start, however, my 15 amp (FLA) piston type air compressor with pressure in the tank.

But I did an experiment with the air compressor; I installed a 3-way valve to disconnect the tanks pressure from the
compressor. So, with no load on the piston of the compressor, the Honda started the motor.
Then I switched the valve so the compressor's output went from atmosphere to the tank.
By the time the pressure reached 125psi (the cutoff point), the motor was pulling right at about 13 amps.

Now, I want to buy a 1/2 hp, 115v submersible well pump that the Honda 2000 will start.
I'm considering the Goulds brand, model, 5GS05421C. It has a FLA rating of 7.9 amps.

Now, for my question; has anybody actually started and run a 1/2hp, 115v submersible well pump with a Honda eu2000i ?

Based on my experiment with the air compressor, I tend to think that it would.
However, before investing in a $600+ submersible pump, I am trying to find out if someone has actually started a
1/2hp, 115v submersible pump with a Honda 2000.

The pump is for a new well that I will be needing water from for 6 months or more before I get hooked to the grid.
Also, for emergency use later on during power outages. The well is 115' deep with static water level at 50'.
Total run of the wiring from pump to service panel is 165'; Goulds recommends a maximum run for 12ga wire of 178', however, I plan on using 10ga wire to reduce voltage drop, making the motor a littlier easy to start.

(No, I don't want to invest in another generator just for the well pump, not even a cheap one.)

(Also, I know that the Honda will easily start the Grundfos brand pump, but for a number of reasons that I won't go into now, I would rather go with a conventional type pump instead of Grundfos's high rpm type. Besides, I haven't found any place that has that particular Grundfos model in stock.)

Another thing; I realize the the initial push of the water in the pipe is going to present somewhat of an initital start load, however, I believe that I could overcome that by installing a ball valve prior to the pressure tank.
In other words, I would start the pump with the ball valve shut, then immediately open the valve. This should be the equivalent of starting the pump under a no load situation, similar as to how I started my air compressor.

So, again I ask, has anyone actually started a 1/2hp, 115v submersible well pump with a Honda eu2000i generator ?
If so, what was the brand of the pump and it's FLA rating ?

Thanks,
Arky
 

DonL

Jack of all trades Master of one
Messages
5,205
Reaction score
72
Points
48
Location
Houston, TX
You should not use a Inverter Gen that small for that type of Motor.

You can use a Isolation Transformer to smooth out the AC of the Inverter Gen Set.

You should start the Gen before connecting power.

A bigger generator, may be a better fix.


Good Luck
 

Valveman

Cary Austin
Staff member
Messages
14,583
Reaction score
1,296
Points
113
Location
Lubbock, Texas
Website
cyclestopvalves.com
You shouldn’t have any problem starting a ½ HP sub with a 2000 generator. I have a 3500 that I have used with a 1 ½ HP test pump many times.

It is much easier to start a 3 wire motor with a capacitor start box, than it is a 2 wire motor which doesn’t use a control box.

I would use the smaller wire though. My book shows #12 wire is only good to 160’ with a 115V 1/2HP load. But I would use #12 anyway. The longest length of the smallest possible wire works like a resistor to give you a reduced voltage soft start. Then the running amps are so much lower than starting amps that there is only 5% voltage loss, which is not a problem.

I am impressed that you understand starting a pump against a closed valve is much easier on the motor than starting with a wide-open pipe. I know a lot of pump engineers who still don’t understand that one. Your idea of closing the ball valve for start up is a good idea. And you don’t have to get in a big hurry to open it. I wouldn’t leave it closed for more than a minute or so, but you don’t have to hurt yourself to get it opened.

Adjusted to the correct pressure, a Cycle Stop Valve would automatically be in the almost closed (1 GPM) position when the pump started. But then it would also fill the entire tank at only 1 GPM, which is OK if you have a small tank. But if you want to fill a large tank and shut off the generator while using the water from the tank, you ball valve method would be better. Just remember tanks don’t hold much water compared to their actual size. An 80 gallon tank only holds about 25 gallons of water.
 

Valveman

Cary Austin
Staff member
Messages
14,583
Reaction score
1,296
Points
113
Location
Lubbock, Texas
Website
cyclestopvalves.com
You should not use a Inverter Gen that small for that type of Motor.

You can use a Isolation Transformer to smooth out the AC of the Inverter Gen Set.

You should start the Gen before connecting power.

A bigger generator, may be a better fix.


Good Luck

Don would know more about that inverter gen set than I would. I didn't even know they where doing that. But I know some guys who run their test pumps from an inverter in the truck.
 

DonL

Jack of all trades Master of one
Messages
5,205
Reaction score
72
Points
48
Location
Houston, TX
Don would know more about that inverter gen set than I would. I didn't even know they where doing that. But I know some guys who run their test pumps from an inverter in the truck.


The truck battery helps a lot, and the truck motor needs to be running, so the inverter gets 13.8V.

A 4 horse motor will bog down to much, then shut down the Inverter.
 

Valveman

Cary Austin
Staff member
Messages
14,583
Reaction score
1,296
Points
113
Location
Lubbock, Texas
Website
cyclestopvalves.com
Why not use a 230 volt pump that draws less current?

I agree except that now you have to use 400’ of #14 wire to get the reduced voltage start. I am sure you could also use a short piece of #16, but I would have to do the voltage loss calculation to determine the length.

The truck battery helps a lot, and the truck motor needs to be running, so the inverter gets 13.8V.
A 4 horse motor will bog down to much, then shut down the Inverter.

Makes sense. My 3500 is old and doesn’t use an inverter. I do know that the voltage spikes from inverters are not good for motors. Thanks!
 

VAWellDriller

Active Member
Messages
539
Reaction score
111
Points
43
Location
Richmond, VA
I agree except that now you have to use 400’ of #14 wire to get the reduced voltage start. I am sure you could also use a short piece of #16, but I would have to do the voltage loss calculation to determine the length.



Makes sense. My 3500 is old and doesn’t use an inverter. I do know that the voltage spikes from inverters are not good for motors. Thanks!


The reason not to go 230 volt is his generator only makes 115 power. I think Don is thinking about battery run power inverters when not recommending them...this is an inverter generator with a gas engine and its about the cleanest power there is.....IF it will start the pump, have no fear. For what it's worth, I recently picked up a Honda EU 1000 on Craigslist and that will start and run a Grundfos 3".

I'm a big fan of the Grundfos 3"...they have proven themselves over the long haul for me (in clean wells, sandy wells, low flow wells, high flow wells), but if Arky wants to stay away; I'll respect that. I have a stack of old pumps at the shop...If we don't get snowed out, tomorrow I'll see if I can find an old 115 volt 4" and try it in the test tank with a Honda EU2000.
 

Arky217

New Member
Messages
43
Reaction score
0
Points
0
Location
Arkansas
Wow, I didn't expect so many replies so quickly; thank you all.


To DonL, "You should not use a Inverter Gen that small for that type of Motor."

IF the generator starts the pump and the running amperage doesn't exceed the generator's continuous amp rating, I guess I would have to ask, why not ?
Yes, I would definitely start the gen before powering the pump; also, I would make sure the gen economy mode is off.
As to a bigger gen, I just don't want to invest in another gen just for the pump, especially if the Honda will do the job.


To Valveman, "It is much easier to start a 3 wire motor with a capacitor start box, than it is a 2 wire motor which doesn’t use a control box."

Even though the 3 wire would 'kick' the motor harder, would it cause an increased instantaneous surge current that the generator would have to overcome ?
I think I understand what you said about using the smaller gauge wire, but again, how would that affect the instantaneous start current; would it increase or decrease ?


To Craigpump, "Why not use a 230 volt pump that draws less current?"

The Honda doesn't have a 240v output, only 120v; and I just don't want to invest in a 240v gen just for the pump, not even a cheapie.


To VAWellDriller,

Actually, I was all set to purchase the Grundfos (mod# 5SQ05-180-115v), but the place I was going to buy from (Aqua Science) is out of stock and said they would not be getting another for about a month, and I just could not seem to find another supplier that had that model in stock. Also, I got to wondering about the lifespan of the pump running at 10,700rpm, besides being about $100 more than the Goulds.
But having said that, I would probably still buy the Grundfos if I could find one without waiting another month.

"I'll see if I can find an old 115 volt 4" and try it in the test tank with a Honda EU2000."

Wow, if you could do that, I thank you very much; it would make me feel a lot more easier about ordering the Goulds.

Again, thanks to all for the quick replies,
Arky
 

Valveman

Cary Austin
Staff member
Messages
14,583
Reaction score
1,296
Points
113
Location
Lubbock, Texas
Website
cyclestopvalves.com
Even though the 3 wire would 'kick' the motor harder, would it cause an increased instantaneous surge current that the generator would have to overcome ?

I think I understand what you said about using the smaller gauge wire, but again, how would that affect the instantaneous start current; would it increase or decrease ?
Arky

It is the capacitor in the control box that “kicks” the motor harder, so the gen set doesn’t have to do it, which keeps the starting amps lower.

The smaller wire limits how much current you can send to the motor, so is decreases the starting amperage.

With a capacitor start, small wire, and starting against a closed valve, the starting amps may not be much more than the running amps.
 

VAWellDriller

Active Member
Messages
539
Reaction score
111
Points
43
Location
Richmond, VA
4" of snow and 13 degrees here, so I'm spending the day in the shop. To make a long story short, much to my surprise, my Honda EU2000 generator started and ran a Goulds 1/2 HP 115 volt, 10LS05 pump. At first it killed the generator, but it is about 33 degrees in the shop, so I let the generator warm up for about 10 minutes, then turned off eco-throttle and it started right up...in the worst possible conditions I might add....I had a 10', 12 gauge power cord on it and I had a 1" hose with no restriction on discharge...wide open pumping 16 gpm. After running it for about 5 minutes, I then tried to do it starting with the eco throttle ON and the generator at a bare idle. From this point it also started the pump. I've been wanted to know for a while since so many people have this generator, and I'm glad I found out.
 

DonL

Jack of all trades Master of one
Messages
5,205
Reaction score
72
Points
48
Location
Houston, TX
4" of snow and 13 degrees here, so I'm spending the day in the shop. To make a long story short, much to my surprise, my Honda EU2000 generator started and ran a Goulds 1/2 HP 115 volt, 10LS05 pump. At first it killed the generator, but it is about 33 degrees in the shop, so I let the generator warm up for about 10 minutes, then turned off eco-throttle and it started right up...in the worst possible conditions I might add....I had a 10', 12 gauge power cord on it and I had a 1" hose with no restriction on discharge...wide open pumping 16 gpm. After running it for about 5 minutes, I then tried to do it starting with the eco throttle ON and the generator at a bare idle. From this point it also started the pump. I've been wanted to know for a while since so many people have this generator, and I'm glad I found out.


Great that you ran that test.

Most of the Inverter gen sets rely on a Capacitor so that it can handle the Peak Surge currents. And they have Aluminum flywheels.

Old school generators rely on The Flywheel weight to maintain Peak Starting loads, That is why they use Big Heavy Cast Iron flywheels.

It sound like the OP has a bad Air Compressor Unloader Valve. They get dirty and do not relief the head pressure like they should.


Have fun.
 

Arky217

New Member
Messages
43
Reaction score
0
Points
0
Location
Arkansas
4" of snow and 13 degrees here, so I'm spending the day in the shop. To make a long story short, much to my surprise, my Honda EU2000 generator started and ran a Goulds 1/2 HP 115 volt, 10LS05 pump. At first it killed the generator, but it is about 33 degrees in the shop, so I let the generator warm up for about 10 minutes, then turned off eco-throttle and it started right up...in the worst possible conditions I might add....I had a 10', 12 gauge power cord on it and I had a 1" hose with no restriction on discharge...wide open pumping 16 gpm. After running it for about 5 minutes, I then tried to do it starting with the eco throttle ON and the generator at a bare idle. From this point it also started the pump. I've been wanted to know for a while since so many people have this generator, and I'm glad I found out.


VAWellDriller, thank you very much.

On the pump that you tested, was it a 2 wire or 3 wire pump ?

Also, did you happen to have an ampmeter on it; if so, what was the approximate surge current and running current ?

Again, thank you very much,
Arky
 

DonL

Jack of all trades Master of one
Messages
5,205
Reaction score
72
Points
48
Location
Houston, TX
Unless your amp meter has a Peak Hold, You can not detect or read the Real peak current.


Have fun.
 

VAWellDriller

Active Member
Messages
539
Reaction score
111
Points
43
Location
Richmond, VA
It was 2 wire, and I didn't catch the starting amps, but it was running at 9.8 ... I started it multiple times with no problem. You should; as I think you mentioned before, turn the eco throttle off... I tried it once just to see, and though it worked, it didn't like it much. With a warm gen and eco turned off, it doesn't sound like much of a strain on the gen at all, I would easily rely on this for water.
 

DonL

Jack of all trades Master of one
Messages
5,205
Reaction score
72
Points
48
Location
Houston, TX
It was 2 wire, and I didn't catch the starting amps, but it was running at 9.8 ... I started it multiple times with no problem. You should; as I think you mentioned before, turn the eco throttle off... I tried it once just to see, and though it worked, it didn't like it much. With a warm gen and eco turned off, it doesn't sound like much of a strain on the gen at all, I would easily rely on this for water.


With that reading, That motor has about a 50% loss of power, or more.

Harmonics off of a inverter, can throw off the reading of a amp meter.


Can you close the outlet of the pump and get a reading, Just for Fun ?


I want to play. lol
 

Arky217

New Member
Messages
43
Reaction score
0
Points
0
Location
Arkansas
It is the capacitor in the control box that “kicks†the motor harder, so the gen set doesn’t have to do it, which keeps the starting amps lower.

The smaller wire limits how much current you can send to the motor, so is decreases the starting amperage.

With a capacitor start, small wire, and starting against a closed valve, the starting amps may not be much more than the running amps.


Thanks VAWellDriller for the quick reply !

To Valveman,

On your quote above, what you said seems logical, but could you explain how that ties in to the data on the following 2 pumps ?

Pump #1, Goulds 2 wire, model# 5GS05421C, 1/2 hp, 115v.
The electrical data shows full load amps 7.9, Service Factor amps 9.8, Locked Rotor amps 28

Pump #2, Goulds 3 wire, model# 5GS05411CL, 1/2 hp, 115v.
The electrical data shows full load amps 'Y=8.8', 'B=8.8', 'R=0', service factor amps 'Y=10.9', 'B=10.9', 'R=0',
Locked Rotor amps 44

On the 3 wire under the general description, it just shows amps as 11.0, but on the electrical data chart it gets into
these Y, B, R figures. I don't know what that means.
I got the above data off of the Goulds electrical data for these two pumps.


Could you explain in a little more detail how the 3 wire setup results in a lesser start current.
( I'm just curious, since the data shows such a diffenence in the locked rotor current between the 2 wire and 3 wire (28 vs 44).

Thanks,
Arky
 

VAWellDriller

Active Member
Messages
539
Reaction score
111
Points
43
Location
Richmond, VA
With that reading, That motor has about a 50% loss of power, or more.

Harmonics off of a inverter, can throw off the reading of a amp meter.


Can you close the outlet of the pump and get a reading, Just for Fun ?


I want to play. lol

Really bored today and I guess you sparked my interest; so I re-tested with pressure gauge and 1" water meter.
I'm not at all following you with the statement about 50% power loss or more??? And also not at all following you on the inverter throwing off the amp readings.

Here's what I got:

9.8 amp, wide open, 16 gpm
9.2 amp, 60 psi on pump, 10 gpm
6.6 amp, 103 psi deadhead pressure.

Repeated this test with shop power and got results within +/- 0.1 amps.

As I see it, the motor was right on for the manufacturers nameplate amp draw, and the wet end was pretty close on the pump curve (actually high on the deadhead) and a little low on flow at 60 psi. This pump is about 5 years old and was pulled out to install higher flow pump for the customer.
 

Arky217

New Member
Messages
43
Reaction score
0
Points
0
Location
Arkansas
With that reading, That motor has about a 50% loss of power, or more.

Harmonics off of a inverter, can throw off the reading of a amp meter.


Can you close the outlet of the pump and get a reading, Just for Fun ?


I want to play. lol


DonL, Are you saying that the motor is not developing the full 1/2 hp at the 9.8 amps ?

From the Goulds Electrical Data, the FLA of that motor is 7.9

Does that mean that running the pump from the generator will be detrimental to the motor ?

Also, about overload protection for the motor on submersible pumps; is it built into the motor somehow, like a thermal switch, or should overload protection be added to the circuit ?

Thanks,
Arky
 

Texas Wellman

In the Trades
Messages
1,035
Reaction score
59
Points
48
Location
SE Texas-Coastal
This thread has been very informative. I always wanted to know if the EU2000i would run the 1/2 HP 115V motors.

FWIW I am told that the Franklin 2-wire and the Centri-pro 2-wire are not similar. Supposedly the Centi-pro has a start-cap built into the motor whereas the Franklin has the biac-switch. The franklin manual clearly states that the 2-wire uses 2x the power to start via a generator.

PM sent on where to get a grundfos for a great price.
 