Clack Retention Tank Problem

Discussion in 'Water Softener Forum, problems, installation and r' started by asmart82, May 29, 2012.

  1. asmart82

    asmart82 New Member

    Joined:
    Jan 26, 2011
    Location:
    East Orlando FL
    The inlet port on my retention tank is causing my plastic c-clip to come off when I screw in the pipe connection, thus allowing water to spray back out. Anyone ever have the issue and/or know what might cause it? The pipe connection screws in fine on the outlet side.
     
  2. Tom Sawyer

    Tom Sawyer In the Trades

    Joined:
    Nov 29, 2010
    Location:
    Maine
    Does your tank have the by-pass valves or plain adapters? At any rate you may want to try screwing the pipe into the adapter and then install the adapter and c clip. If that don't work then something is f'd up (technical term) and you probably need to replace the inlet adapter assembly. And remember, it's plastic so don't gorilla the fittings in
     