Getting burst of air in all my plumbing fixtures.

New tank and check valve but when I turn the water on it spits and sputters.
What's happening?
 

bqz

New Member
Messages
14
Reaction score
0
Points
0
Submersible pump,tank is bladder type (20 gal.I think)and check valve is between the two.(after pump and before tank)
 

Valveman

Cary Austin
Staff member
Messages
14,643
Reaction score
1,305
Points
113
Location
Lubbock, Texas
Website
cyclestopvalves.com
Remove the check valve. If this does not solve the problem, it will help you pin point where the problem is. When the pump builds pressure and shuts off, if the pressure drops while no water is being used, you most likely have a hole in the pipe down in the well.
 

bqz

New Member
Messages
14
Reaction score
0
Points
0
Remove the check valve. If this does not solve the problem, it will help you pin point where the problem is. When the pump builds pressure and shuts off, if the pressure drops while no water is being used, you most likely have a hole in the pipe down in the well.

Question: won't the pressure tank push the water back out of the pump or does the pump have a built- in check valve so to speak??
 

Valveman

Cary Austin
Staff member
Messages
14,643
Reaction score
1,305
Points
113
Location
Lubbock, Texas
Website
cyclestopvalves.com
That is how you can tell if the pump has a check valve on it or there is a hole in the drop pipe. Either one of those things has to be fixed, and adding another check valve up top is not the fix.
 

bqz

New Member
Messages
14
Reaction score
0
Points
0
I'm follwing you now ,I'll check it out,thanks for the help.
 

Cacher_Chick

Test, Don't Guess!
Messages
5,458
Reaction score
213
Points
63
Location
Land of Cheese
Any chance that you replaced a non-bladder tank with a bladder tank?

If so you might have bleeders in the drop pipe that need to be removed.
 

Valveman

Cary Austin
Staff member
Messages
14,643
Reaction score
1,305
Points
113
Location
Lubbock, Texas
Website
cyclestopvalves.com
I was thinking the same thing. If you remove the above ground check valve, a bleeder orifice should stay closed so you shouldn't need to pull the pipe and plug it. However, if water is going back down hole, it needs to be fixed no matter if it is a bleeder orifice, hole in the pipe, or a bad check on the pump.
 

bqz

New Member
Messages
14
Reaction score
0
Points
0
I believe I found problem.
Opened lid on well looked in and when the well kicks on water is spraying out the side of the pipe going down to pump ,leak is near the top I can see it shotting out the side of a pipe (maybe 2ft down)
If water leak in pipe won't this cause air in lines??
 

Valveman

Cary Austin
Staff member
Messages
14,643
Reaction score
1,305
Points
113
Location
Lubbock, Texas
Website
cyclestopvalves.com
Sounds like the o-ring in your pitless adapter is leaking. Maybe just pull it up and replace the o-ring to fix it. Yes the leak will cause air in the line but, only if you have a check valve after the leak. Removing the check valve will let the water leak oout and the pump cycle on and off but, there would not be any air in the line. The leak has got to be fixed either way.
 