240 Circuit

Users who are viewing this thread

Paul Spindy

New Member
Messages
19
Reaction score
1
Points
3
Location
Pennsylvania
I thought my well went and replaced the motor and it did not work. Late found stove lights up but no heat. Same with dryer, drum turns but no heat. If I take a volt meter I get 120 from hot to ground on both sides. If I touch both hots I don't get any voltage. I get voltage to the well pump hot to ground, but no reading on both hots. Same on all 240 lines. Any ideas and thanks in advanced.

Paul
 

Jadziedzic

Active Member
Messages
310
Reaction score
60
Points
28
Location
New Hampshire
It's highly likely you lost one hot leg of the incoming 3-wire supply. Try cycling the main breaker and repeat your measurements; if you're still missing 240V between the two hots I'd suggest you call your local utility company so they can check the incoming supply lines at the meter.
 

Paul Spindy

New Member
Messages
19
Reaction score
1
Points
3
Location
Pennsylvania
Power company came and was on thier end. The lineperson said they do not see this often. Something should have tripped the transformer but did not. Something was welded together and othe neighbors was fine, we were the only ones to have the problem.
 