15A outlets/switches on 20A circuit

Discussion in 'Electrical Forum discussion & Blog' started by maurice53, May 29, 2011.

  1. maurice53

    maurice53 New Member

    Joined:
    May 15, 2011
    Location:
    Tucson, AZ
    I have outlets on a number of 20A circuits (12/2 wire)- dining area, kitchen counter, den, garage- that appear to be rated 15A. Is this okay? Do wall switches need to be rated according to the circuit amps?
     
  2. jwelectric

    jwelectric Electrical Contractor/Instructor

    Joined:
    Jun 14, 2007
    Occupation:
    Instructor
    Location:
    North Carolina
    This is code compliant

    If it was a single receptacle on a 20 amp circuit then it would be required to be rated at 20 amps but a duplex receptacle on a 20 amp circuit can be rated at 15 amps
     
  3. Sponsor

    Sponsor Paid Advertisement

     
  4. DonL

    DonL Jack of all trades Master of one

    Joined:
    Mar 30, 2011
    Occupation:
    Rocket Scientist
    Location:
    Houston, TX
    The wall switch needs to be rated above the load that they are switching, Not the Max circuit amps that the breaker can provide.

    Have a great day.

    DonL
     
  5. jadnashua

    jadnashua Retired Defense Industry Engineer xxx

    Joined:
    Sep 2, 2004
    Occupation:
    Retired Systems engineer for defense industry.
    Location:
    New England
    IOW, if the switch can turn the entire circuit off, it needs to be 20A, otherwise, as long as it is sized for the max load it can have, it is fine. Typically, that switch would turn a lamp on/off, and only if that load was the full value of the circuit or was dedicated to that single load, would it need to be a 20A switch.
     
Similar Threads: outlets/switches circuit
Forum Title Date
Electrical Forum discussion & Blog Can I install outlets/switches before drywall? Jun 11, 2010
Electrical Forum discussion & Blog Electrical Circuit Larger Than Needed Today at 11:55 AM
Electrical Forum discussion & Blog Under-performing circuit panel with two 240V appliances Dec 15, 2014
Electrical Forum discussion & Blog New circuit for gas water heater Dec 7, 2014
Electrical Forum discussion & Blog AFCI breaker (in Wisconsin) needed for dedicated light circuit? Jul 30, 2014

Share This Page