    I wired my bedrooms with 12 gauge wire and have already orded my switches that are 15AMP:eek:. Can I install these switches or is this a code violation?
    The other question is: Can you install a 20AMP switch on a 15AMP circuit?
    It seems like common sense tells me 20AMP switch for 20AMP circuit and vice versa. But, is this really the case?
  2. cacher_chick
    Jan 5, 2008
    Test, Don't Guess!
    As long as the load does not exceed the rating of the switch it does not matter. If the switch controls an outlet, you should then use a 15A outlet.
  4. leejosepho
    leejosepho DIY scratch-pad engineer
    Nov 23, 2006
    disabled-retired industrial fabricator
    The wire must be sufficient to carry whatever the circuit breaker will let through, but you can have either 15- or 20-amp devices connected by either 14- or 12-gauge wire as long as the circuit is protected by a 15-amp breaker. But if you use a 20-amp breaker, then the wire must be at least 12-gauge even though 15-amp switches and receptacles can still be acceptable unless the circuit is a dedicated circuit such as for an AC unit requiring 20 amps.
  5. Cybermonkey
    Mar 16, 2008
    Vermont
    So, basically if the switch is just supplying the light I should be just fine?
    Thanks for the help!
  6. leejosepho
    Nov 23, 2006
    Yes, as long as the load on the switch is less than the switch's rating.
  7. Johnny C
    Johnny C Electrician
    Oct 19, 2008
    Elect Teacher, Consultant, Seminar Presenter, Elec
    Mass. & now Virginia Beach, VA
    Section 404.14 requires snap switches to be used within their ratings as marked. See Section 404.14(A) through (D). The ampere rating of the switch is based on the type of switch, the load current that it is intended to interrupt, and the type of load, such as inductive, motor, or tungsten loads.
    Assuming the loads you intend to control are lights and small utilization equipment such as radio and tv, switches rated 15 amperes at 125 volts are permited on a 15 or 20 ampere circuit wired with No. 12 awg, Cu.
  8. Cybermonkey
    Mar 16, 2008
    Vermont
    Thanks for the reply.
  9. leejosepho
    Nov 23, 2006
    Yes, 15 amps are within a 20-amp rating.
  10. Johnny C
    Oct 19, 2008
    15 amp sw
    Yes you can install a 20 ampere switch on a 15 ampere circuit.
  11. hj
    switch
    The only time you could not use that 15 amp switch is if you were doing it the easy way and backstabbing the wires. In that case the openings, by code, will not accept the 12 gauge wire.
Similar Threads: switches
Electrical Forum discussion & Blog Three Way Switches Light Dimmer Installation May 1, 2016
Electrical Forum discussion & Blog Dual switches not working correctly after light modification Jul 19, 2015
Electrical Forum discussion & Blog 3-way switches with dimmers for lighting? May 2, 2014
Electrical Forum discussion & Blog 1 circuit/2 gang 3 way switches- Does this look right? Apr 17, 2014
Electrical Forum discussion & Blog Ignorant question, business replacing receptacles and switches. Oct 28, 2013